The fan power depends on the flow rate, pressure rise, and efficiency of
the fan. To give you a ballpark start, I measured the fan power on my
3-ton AC system at home. At 1450 cfm, the fan power was 190W at 0.6 inwc
external static pressure. Adding in an estimated 0.5 inwc for the coil
pressure drop and an estimated 0.1 inwc losses at the entrance/exit of
the unit gives a pressure rise of 1.2 inwc for this fan. Hope this helps.
Hu,Jia wrote:--> Hello, all:
> I use Gainesville (in FL) weather file to simulate a small office with
> 3m(width)*5m(length)*3m(height). The window faces south and is located
> in the wall that is 3m * 3m. I autosize PTAC (The design day is from
> the weather file). And I calculate its electric power (watt) as you
> can see from excel file at URL:
> http://groups.yahoo.com/group/EnergyPlus_Support/files/_Problem_Submittals/watt.xls
> <http://groups.yahoo.com/group/EnergyPlus_Support/files/_Problem_Submittals/watt.xls>
>
> You can download the excel file to see the values of PTAC energy
> consumption (in watts).
> *my question is that whether the values of energy consumption of PTAC
> (in watts), indicated in the excel file, are realistic ? *
> Thank you in advance.
> Jia Hu
>
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/