Hi,

I believe the minimum requirements are the five objects listed in the example below.  In addition, you'll need a surface to mount the PV, a zone to specify where inverter losses occur (optional; blank=outdoors), and an availability schedule (which I have listed as always on).  

Liam

----------------

Generator:Photovoltaic,
    PV generator,            !- Name
    ROOF_S   ,               !- Surface Name
    PhotovoltaicPerformance:Simple,  !- Photovoltaic Performance Object Type
    PV Simple,               !- Module Performance Name
    IntegratedSurfaceOutsideFace,  !- Heat Transfer Integration Mode
    1,                       !- Number of Modules in Parallel {dimensionless}
    1;                       !- Number of Modules in Series {dimensionless}

PhotovoltaicPerformance:Simple,
    PV Simple,               !- Name
    0.80,                     !- Fraction of Surface Area with Active Solar Cells {dimensionless}
    Fixed,                   !- Conversion Efficiency Input Mode
    0.10;                     !- Value for Cell Efficiency if Fixed

ElectricLoadCenter:Generators,
    PV Array,                !- Name
    PV generator,            !- Generator 1 Name
    Generator:Photovoltaic,  !- Generator 1 Object Type
    100000,                  !- Generator 1 Rated Electric Power Output
    ALWAYS ON,               !- Generator 1 Availability Schedule Name
    ;                        !- Generator 1 Rated Thermal to Electrical Power Ratio

ElectricLoadCenter:Inverter:Simple,
    Inverter Simple,         !- Name
    ALWAYS ON,               !- Availability Schedule Name
    BASE,                    !- Zone Name
    0.5,                     !- Radiative Fraction
    0.90;                     !- Inverter Efficiency

ElectricLoadCenter:Distribution,
    Distribution,            !- Name
    PV Array,                !- Generator List Name
    Baseload,                !- Generator Operation Scheme Type
    ,                        !- Demand Limit Scheme Purchased Electric Demand Limit {W}
    ,                        !- Track Schedule Name Scheme Schedule Name
    ,                        !- Track Meter Scheme Meter Name
    DirectCurrentWithInverter,  !- Electrical Buss Type
    Inverter Simple;         !- Inverter Object Name

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, êáôéá êáôïõ <roulagan@...> wrote:
>
> Hi...
>  
> Can anyone tell me which fields of E+ 4 i have to complete in order to put PV on the roof of a building...????
>  
>  
>  
> Thank you in advance!!
> 
> 
>       
> ___________________________________________________________ 
> ×ñçóéìïðïéåßôå Yahoo!; 
> ÂáñåèÞêáôå ôá åíï÷ëçôéêÜ ìçíýìáôá (spam); Ôï Yahoo! Mail 
> äéáèÝôåé ôçí êáëýôåñç äõíáôÞ ðñïóôáóßá êáôÜ ôùí åíï÷ëçôéêþí 
> ìçíõìÜôùí http://login.yahoo.com/config/mail?.intl=gr
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/