[EnergyPlus_Support] Re: Fan and Pump Efficiency
Is Delta Pressure the static or total pressure rise?
Normally static is measured, but it is not explicitly stated.
Regards,
Jean Marais
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "JV Dirkes II" <jvd2pe@...> wrote:
>
>
> Dear Mr / Ms Herrmann,
>
> Fans can have separately assigned efficiencies for the fan and motor, as
> shown in the sample object below.
>
> FAN:SIMPLE:VARIABLEVOLUME, Fan Name RFan_AH1, Available Schedule
> SchCpct_FanOpern, Fan Total Efficiency 0.6, Delta Pressure 1, Max
> Flow Rate Autosize, Min Flow Rate 0, Motor Efficiency .91, Motor In
> Airstream Fraction 1, FanCoefficient 1 .0013, FanCoefficient 2 .147,
> FanCoefficient 3 .9506, FanCoefficient 4 -.0998, FanCoefficient 5 0,
> Fan_Inlet_Node NodeOut_EA_AH1, Fan_Outlet_Node NodeIn_OA_AH1; End-Use
> Subcategory
>
> Pumps, however, combine the efficiencies of motor and pump into a single
> value which is somewhat poorly identified as "Motor Efficiency". Since
> the combined value is static, this is not a big concern. It does,
> however, force a separate calculation to combine the motor and pump
> efficincies into a single value for pumps.
>
> PUMP:VARIABLE SPEED, Pump Name HtgWtr Pump_1, Inlet_Node Node_HtgWtr
> SupplyInlet_In, Outlet_Node Node_HtgWtr Pump1_Out, Rated Volumetric
> Flow Rate 0.0076, Rated Pump Head 179165, Rated Power Consumption
> 2350, Motor Efficiency 0.895, Fraction of Motor Inefficiencies to
> Fluid Stream 0, Coefficient1 of the Part Load Performance Curve
> 0.203671, Coefficient2 of the Part Load Performance Curve -0.827077,
> Coefficient3 of the Part Load Performance Curve 1.181191, Coefficient4
> of the Part Load Performance Curve 0.442055, Min Flow Rate while
> operating in variable flow capacity 0.0023, Pump Control Type
> CONTINUOUS, Pump Flow Rate Schedule Name SchCpct_AlwaysOn;
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, L Herrmann <l.herrmann@>
> wrote:
> >
> > Hello,
> >
> > I was wondering about how to adjust pump and fan efficiencies in EP.
> For example, to change the efficiency of the pump motor, would one need
> to create an entirely new pump with a higher efficiency which meets the
> flow rate and head of the system?
> >
> > Thanks
> >
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/