Re: [EnergyPlus_Support] Re: Fan Power Pressures and Efficiencies - Are the calculations based on Pstat or Pt
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: Re: [EnergyPlus_Support] Re: Fan Power Pressures and Efficiencies - Are the calculations based on Pstat or Pt
- From: Richard Raustad <RRaustad@xxxxxxxxxxxx>
- Date: Fri, 22 Jan 2010 08:49:01 -0500
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Fri, 22 Jan 2010 06:50:58 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1264168257; bh=mDfOh6U4/GKmtSeVC9a0xi0WXdMSaq5yUYEFjJjk5Z8=; h=Received:Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:In-reply-to:To:Message-id:Organization:User-Agent:References:X-Originating-IP:X-eGroups-Msg-Info:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=qxE2f847iHYyGqDo2qFptDM/TRSPoYCXvy/iMY8/cBg8wktCHjhtjHuNnEHVR4W0M2O3+yNTIBsDhXFswEgDT79RF3ESkPo91gE+aoQEUP+kjJ6Cx2NezX+E7+tlbkoe
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=M55MKDhQLBmxZyN8sfhDRreN9HdPqwxq1YVO0a83vEQiuttwpHseGSlNoSNULr13o5R9TWV+JSbwM9g4Xs8l46OVgapJfSbAVyVyOZdFR0+MpnnBPPEqPqTFKmOSTle4;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <hjc9vh+3n5g@eGroups.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Organization: Florida Solar Energy Center
- References: <hjc9vh+3n5g@eGroups.com>
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: Thunderbird 2.0.0.23 (Windows/20090812)
Why don't you enter a pressure and see if you get the power you expect?
jeannieboef wrote:
>
> That is a very circular answere that does not at all answere the
> question. I've looked the documentation and it is not clear which is
> the input, static pressure rise "across the fan" or dynamic pressure rise.
>
> The definition of "Supply Fan Delta Pressure" is not clear!
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> <RRaustad@...> wrote:
> >
> > The value you enter in the fan object is used by E+ in the
> calculations:
> > the equations are described in the Engineering Reference. The detlaP
> > used in those equations are the value you enter in the fan object (in
> > this case 600 Pa)
> >
> > Fan:OnOff,
> > Supply Fan 1, !- Name
> > FanAndCoilAvailSched, !- Availability Schedule Name
> > 0.7, !- Fan Efficiency
> > 600.0, !- Pressure Rise {Pa}
> >
> >
> > jeannieboef wrote:
> > >
> > > Correct, however still not clear which is used as user input and
> which
> > > is calculated by e+.
> > >
> > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx
> <mailto:EnergyPlus_Support%40yahoogroups.com>
> > > <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad
> > > <RRaustad@> wrote:
> > > >
> > > > Total pressure.
> > > >
> > > > Ptotal = Pstatic + Pdynamic
> > > > Ptotal = Pstatic + 1/2 * rhoV^2
> > > >
> > > >
> > > > jeannieboef wrote:
> > > > >
> > > > > Are the calculations based on total pressure or static
> pressure rise?
> > > > >
> > > > > Field: Supply Fan Total Efficiency
> > > > > Enter the total efficiency of the supply fan. This is the
> ratio of
> > > the
> > > > > power delivered to the air to
> > > > > the electrical input power at maximum flow. This is also the
> product
> > > > > of the fan motor
> > > > > efficiency and fan (impeller) efficiency. The motor efficiency
> is the
> > > > > power delivered to the
> > > > > shaft divided by the electrical power input to the motor. The fan
> > > > > efficiency is the power
> > > > > delivered to the air divided by the shaft power. The power
> delivered
> > > > > to the fluid is the mass
> > > > > flow rate of the air multiplied by the pressure rise divided
> by the
> > > > > air density. Must be greater
> > > > > than 0 and less than or equal to 1. The default is 0.7.
> > > > >
> > > > > Field: Supply Fan Delta Pressure
> > > > > Enter the pressure rise in Pa at full flow and standard
> conditions.
> > > > > Standard conditions are
> > > > > considered 20o C at sea level, 101325 Pa. The default is 1000 Pa.
> > > > >
> > > > >
> > > >
> > > > --
> > > > Richard A. Raustad
> > > > Senior Research Engineer
> > > > Florida Solar Energy Center
> > > > University of Central Florida
> > > > 1679 Clearlake Road
> > > > Cocoa, FL 32922-5703
> > > > Phone: (321) 638-1454
> > > > Fax: (321) 638-1439 or 1010
> > > > Visit our web site at: http://www.fsec.ucf.edu
> <http://www.fsec.ucf.edu> <http://www.fsec.ucf.edu
> <http://www.fsec.ucf.edu>>
> > > >
> > > > UCF - From Promise to Prominence: Celebrating 40 Years
> > > >
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/