Re: [EnergyPlus_Support] Series Counterflow Chiller Arrangement



Try setting the branch control to SeriesActive for each chiller and see 
if that helps.

Branch,
Central Chiller Branch, !- Name
0, !- Maximum Flow Rate {m3/s}
, !- Pressure Drop Curve Name
Chiller:Electric, !- Component 1 Object Type
Central Chiller, !- Component 1 Name
Central Chiller Inlet Node, !- Component 1 Inlet Node Name
Central Chiller Outlet Node, !- Component 1 Outlet Node Name
SeriesActive; !- Component 1 Branch Control Type


elmaria024 wrote:
>
> I'm trying to model a series counterflow (water-cooled) chiller 
> arrangement where two chillers are in series. I can get the SVG file 
> to accurately represent the arrangement, but I can't seem to control 
> the chillers properly. When only one chiller is on (the other not on 
> the plant equipment list), the chilled water loop maintains set point, 
> but when I add the second chiller to the equipment list neither 
> chiller turns on during the year. I've tried uncontrolled, cooling 
> load, and component set point operation controls to no avail.
>
> Can series counterflow chillers or just series chillers be modeled? I 
> don't see any example files. If they can, what am I missing?
>
> Thanks in advance!
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/