Re: [EnergyPlus_Support] Re: Series Counterflow Chiller Arrangement



When you say a "series counterflow" arrangement, do you mean that the 
chiller evaporators are in series (chiller 1 then chiller 2), and then 
the condensers are also in series with flow in the opposite direction 
(chiller 2 then chiller 1)? If so, the condenser side of the chiller 
pair can not be in series. If one chiller is off, the condenser side of 
that chiller is off, and then the other chiller will not run (since 
there is 0 condenser flow for that chiller). Try running the condenser 
side in parallel and see if that works.

elmaria024 wrote:
>
> Thanks for the advice. I have tried changing the control types to 
> SeriesActive, but it didn't seem to help. Any more ideas?
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx 
> <mailto:EnergyPlus_Support%40yahoogroups.com>, Richard Raustad 
> <RRaustad@...> wrote:
> >
> > Try setting the branch control to SeriesActive for each chiller and see
> > if that helps.
> >
> > Branch,
> > Central Chiller Branch, !- Name
> > 0, !- Maximum Flow Rate {m3/s}
> > , !- Pressure Drop Curve Name
> > Chiller:Electric, !- Component 1 Object Type
> > Central Chiller, !- Component 1 Name
> > Central Chiller Inlet Node, !- Component 1 Inlet Node Name
> > Central Chiller Outlet Node, !- Component 1 Outlet Node Name
> > SeriesActive; !- Component 1 Branch Control Type
> >
> >
> > elmaria024 wrote:
> > >
> > > I'm trying to model a series counterflow (water-cooled) chiller
> > > arrangement where two chillers are in series. I can get the SVG file
> > > to accurately represent the arrangement, but I can't seem to control
> > > the chillers properly. When only one chiller is on (the other not on
> > > the plant equipment list), the chilled water loop maintains set 
> point,
> > > but when I add the second chiller to the equipment list neither
> > > chiller turns on during the year. I've tried uncontrolled, cooling
> > > load, and component set point operation controls to no avail.
> > >
> > > Can series counterflow chillers or just series chillers be modeled? I
> > > don't see any example files. If they can, what am I missing?
> > >
> > > Thanks in advance!
> > >
> > >
> >
> > --
> > Richard A. Raustad
> > Senior Research Engineer
> > Florida Solar Energy Center
> > University of Central Florida
> > 1679 Clearlake Road
> > Cocoa, FL 32922-5703
> > Phone: (321) 638-1454
> > Fax: (321) 638-1439 or 1010
> > Visit our web site at: http://www.fsec.ucf.edu <http://www.fsec.ucf.edu>
> >
> > UCF - From Promise to Prominence: Celebrating 40 Years
> >
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/