That surface defines the position and
geometry for all the PV models, but the net area of that surface is only used with
the Simple model. Net area is the gross area minus the area of any sub-surfaces
–see I/O Ref entry for the field called “Fraction of Surface Area with
Active Solar Cells. The more advanced PV models use the area of the PV module entered
in the respective PhotovoltaicPerformance input objects and don’t use the
surface’s area at all. From: Hi everybody, I have a question
about photovoltaic model on EnergyPlus. I want to simulate a
building with PV panels located in the building façade. In the object
"Generator:Photovol If there
are windows on these walls, I don't know if the program will
automatically desconsider the area of the windows, to locate the PV panels, or
I have to create another surface on the opaque surfaces in order to locate the
panels? Thank you very much, Paulo Ara. Veja quais são os assuntos do momento no Yahoo! + Buscados: Top
10 - Celebridades
- Música
- Esportes __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.