Look at the expanded input file (*.expidf) and see what type of 
thermostat is used. the HVACTemplate:Thermostat object should give you a 
dual set point. You can also use this file (by changing the name to 
something.idf) after the first run to make other custom changes that are 
not available in the HVACTemplate objects.

ZoneControl:Thermostat,
Zone 2 Thermostat, !- Name
EAST ZONE, !- Zone Name
Zone Control Type Sched, !- Control Type Schedule Name
ThermostatSetpoint:DualSetpoint, !- Control 1 Object Type
Dual Setpoint with DB; !- Control 1 Name

Schedule:Compact,
Zone Control Type Sched, !- Name
Control Type, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00,4; !- Field 3

ThermostatSetpoint:DualSetpoint,
Dual Setpoint with DB, !- Name
Heating Setpoints, !- Heating Setpoint Temperature Schedule Name
Cooling Setpoints; !- Cooling Setpoint Temperature Schedule Name

Also check the control type schedule to make sure it uses "4" as the 
control type (1=heating, 2=cooling, 3 = single heating and cooling, 4 = 
dual set point). Note the control type schedule below uses a dual set 
point all year long.

Schedule:Compact,
Zone Control Type Sched, !- Name
Control Type, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: AllDays, !- Field 2
Until: 24:00,4; !- Field 3

asparke2 wrote:
>
> Hi Everyone,
>
> I've modeled a 1 zone house's HVAC system with a HVACTemplate: 
> System:Unitary, a HVACTemplate: Zone:Unitary, and a HVACTemplate: 
> Thermostat. The year-round temperature setpoints are 71 for heating 
> and 76 for cooling. During the winter, the heating system (gas) is 
> pushing the temperature up to 76 (instead of stopping at 71), then the 
> cooling coil is kicking in to push it back down. During the summer, 
> the system is working as expected, only bringing the temperature down 
> to 76. Any idea why this is happening? Everything is set to autosize, 
> and there is no economizer or humdifier. According to the standards 
> I'm following, the heating and cooling must be available year-round, 
> so manually defining a schedule is not an option. All feedback is 
> appreciated.
>
> Thanks,
>
> Andrew
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/