[EnergyPlus_Support] VAV HeatandCool no reheat - Minimum OA flowrates





Hi all,

 

I’ m simulating a 100% outdoor air loop. The air loop provides fresh air and heating or cooling to 3 rooms with the same occupancy, electric equipment and lighting profile.

 

 People is allowed to smoke inside the building so the outside air flow rates are  huge ( 5 ach).

 

The building will not be always 100% occupied. To reduce energy consumption in partial occupancy scenario,  the air handling unit will have 4 levels of air supply.

 

To approach this on energyplus,  I’ve created a VAV air loop with terminal unit VAV: HeatandCool: NoReheat. The lower occupancy fraction predicted is 0.50, so I’ve set the zone miminum air flow fraction of 0.50.

 

The  leaving coil air temperatures modulated between 19 and 25 ºC with Set-point managers single zone heating and cooling placed in one of the rooms.

 

 

On the  Controller: OutdoorAir I’ve set:

 

Controller:OutdoorAir,

    AHU5-6 OA Controller,   !- Name

    AHU 5-6 Relief Air Outlet,  !- Relief Air Outlet Node Name

    AHU 5-6 Air Loop Inlet,  !- Return Air Node Name

    AHU 5-6 Mixed Air Outlet,!- Mixed Air Node Name

    AHU 5-6 Outside Air Inlet,  !- Actuator Node Name

    16.250,                  !- Minimum Outdoor Air Flow Rate {m3/s}

    16.250,                  !- Maximum Outdoor Air Flow Rate {m3/s}

    NoEconomizer,            !- Economizer Control Type

    ModulateFlow,            !- Economizer Control Action Type

    ,                        !- Economizer Maximum Limit Dry-Bulb Temperature {C}

    ,                        !- Economizer Maximum Limit Enthalpy {J/kg}

    ,                        !- Economizer Maximum Limit Dewpoint Temperature {C}

    ,                        !- Electronic Enthalpy Limit Curve Name

    19,                      !- Economizer Minimum Limit Dry-Bulb Temperature {C}

    NoLockout,               !- Lockout Type

    FixedMinimum,            !- Minimum Limit Type

    OccupProfile,             !- Minimum Outdoor Air Schedule Name

    on,                      !- Minimum Fraction of Outdoor Air Schedule Name

    on;                      !- Maximum Fraction of Outdoor Air Schedule Name

 

The OccupProfile schedule was defined with the 4 fan operating levels based on the predicted occupancy profile.

 

Because I’ve defined FixedMinimum limit on the outdoor air controller, in partial occupancy scenario I was expecting the unit to supply at least the minimum air flow rate defined by the Minimum Outdoor Air Schedule Name.

 

In the winter, the calculated supply air  temperature is  19 ºC ( the lower temperature defined on the set-point manager) but the supply air flow rate is lower than the defined by the !- Minimum Outdoor Air Schedule Name.

 

I’ve read input output reference on this topic, and for my understanding,  VAV flowrate should be restricted to the minimum outdoor air defined. 

 

My question is:

 

In the simulation, VAV only considers the minimum air flow rate defined in the VAV: HeatandCool: NoReheat or It is meant to consider also the outside air controller action?

 

Thanks in advance for your help,

 

Best regards

 

Filipe Madureira



__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___