Hi all, I’ m simulating a 100% outdoor air loop. The air loop provides
fresh air and heating or cooling to 3 rooms with the same occupancy, electric
equipment and lighting profile. People is allowed to smoke inside the building so the outside air
flow rates are huge ( 5 ach). The building will not be always 100% occupied. To reduce energy consumption
in partial occupancy scenario, the air handling unit will have 4 levels of air
supply. To approach this on energyplus, I’ve created a VAV air loop with
terminal unit VAV: HeatandCool: NoReheat. The lower occupancy fraction predicted
is 0.50, so I’ve set the zone miminum air flow fraction of 0.50. The leaving coil air temperatures modulated between 19 and 25
ºC with Set-point managers single zone heating and cooling placed in one of the
rooms. On the Controller: OutdoorAir I’ve set: Controller:OutdoorAir, AHU5-6 OA Controller, !- Name AHU 5-6 Relief Air Outlet, !- Relief Air Outlet Node Name AHU 5-6 Air Loop Inlet, !- Return Air Node Name AHU 5-6 Mixed Air Outlet,!- Mixed Air Node Name AHU 5-6 Outside Air Inlet, !- Actuator Node Name 16.250, !- Minimum Outdoor Air Flow Rate
{m3/s} 16.250, !- Maximum Outdoor Air Flow Rate
{m3/s} NoEconomizer, !- Economizer Control Type ModulateFlow, !- Economizer Control Action Type , !- Economizer Maximum Limit
Dry-Bulb Temperature {C} , !- Economizer Maximum Limit
Enthalpy {J/kg} , !- Economizer Maximum Limit
Dewpoint Temperature {C} , !- Electronic Enthalpy Limit Curve
Name 19, !- Economizer Minimum Limit
Dry-Bulb Temperature {C} NoLockout, !- Lockout Type FixedMinimum, !- Minimum Limit Type OccupProfile, !- Minimum Outdoor Air Schedule
Name on, !- Minimum Fraction of Outdoor Air
Schedule Name on; !- Maximum Fraction of Outdoor Air
Schedule Name The OccupProfile schedule was defined with the 4 fan operating
levels based on the predicted occupancy profile. Because I’ve defined FixedMinimum limit on the outdoor air
controller, in partial occupancy scenario I was expecting the unit to supply at
least the minimum air flow rate defined by the Minimum Outdoor Air Schedule
Name. In the winter, the calculated supply air temperature is 19 ºC
( the lower temperature defined on the set-point manager) but the supply air
flow rate is lower than the defined by the !- Minimum Outdoor Air Schedule Name. I’ve read input output reference on this topic, and for my
understanding, VAV flowrate should be restricted to the minimum outdoor air
defined. My question is: In the simulation, VAV only considers the minimum air flow rate
defined in the VAV: HeatandCool: NoReheat or It is meant to consider also the
outside air controller action? Thanks in advance for your help, Best regards Filipe Madureira __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.