Hello. About the IDF not opening the file: AirLoopHVAC:ZoneSplitter and AirLoopHVAC:ZoneMixer have too many objects. only 50 outlet names are permited per each. Opening the idf in a text editor such as notepad, and deleting the outlet names so that you end up having 50 per AirLoopHVAC will enable you to open the IDF in the Editor. You probably will have to create a new object of each AirLoop and insert the outlets that you had to previously delete (i'm not very sure about this last part, i dont have much experience dealing with these objects). As for the errors: 1. you're using window and/or door multipliers while having FullExterior Solar distribution. If you want to correctly model Solar Distribution using FullExterior, you shouldnt use window multipliers unless you are sure that doing so wont make much of a difference on the final results, considering the geometry of your model. 2. many of the zones where you have a thermostat dont require cooling or heating. 3. DB is probably trying to get all the output:variables possible in E+, when your modelation doesnt have them all available (it depends on the inputs). There are some other errors about SizePlant and SizePump flow rates being zero (considering that you have so many zones without loads, it might be related). Other than this, only the FullExterior issue might compromise your results, the rest are just warnings that you should be aware of. Hope someone else with more experience takes a look at this and give you some more detailed help. Pedro. To: energyplus_support@xxxxxxxxxxxxxxx From: kulandhai_psna@xxxxxxxxx Date: Tue, 23 Mar 2010 23:25:52 -0700 Subject: [EnergyPlus_Support] problem with idf file
Hotmail: Trusted email with powerful SPAM protection. Sign up now. __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |