[EnergyPlus_Support] Re: can't figure out how to fix errors
Hello
Some questions:
- Does your zone have a sizing object?
- Does your plant have s sizing object?
- Does your zone have internal gains ?
MN
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "greg.morss" <gmorss@...> wrote:
>
> Hello,
> I am trying to simulate a 100% Outside air with Heat Recovery system for a project that I am working on, and have fixed all the connection errors that have come up, but now I am getting a large number of warning which are causing the simulation to fail and I cant figure out how to correct them or where to look. The first one is:
> ** Warning ** Calculated design cooling load for zone=CORNER 1 is zero.
> ** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs
>
> and when I check where it recommends, everything looks correct.
>
> The next one is :
> ** Warning ** PlantFlowResolver: Branch flow rates out of bounds, for Plant Loop=HW LOOP, Branch=HW INTERIOR REHEAT COIL BRANCH
> ** ~~~ ** Conditions should be: 0.631 <= 0.132 <= 0.568 Occurrence info=NORMAL, 01/01 00:00 - 00:15
>
> Any ideas where i should start?
>
>
> Thanks
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/