Funny that you mentioned that the building is at the South pole. The heters may be out of control. If the outside air is processed and fed into the air loop with a splitter to all zones, I think many unexpected conditions may happen. I cannot figure out yet how the re-heat coils are controlled when connected to only one fan in the air one loop, and whether the centrol large area is one of the zones. Dr. Li To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: wfbuhl@xxxxxxx Date: Tue, 13 Apr 2010 10:51:29 -0700 Subject: Re: [EnergyPlus_Support] Re: can't figure out how to fix errors
It's pretty unusual to not not have any design cooling loads. The warning message is coming from
the zone sizing calculation. This calculation does not know or care anything about the system or plant level input. It is strictly a zone level calculation. Thus the problem must be coming from the zone level inputs. Check your design days and zone level schedules. Make sure the schedules are active for SummerDesignDay. Anything you are not mentioning - like the building is at the South Pole? Did you check the Sizing:Zone inputs and make sure the specified "Zone Cooling Design Supply Air Temperature" is less than your expected zone temperature? Fred Buhl On 4/13/2010 9:09 AM, Morss, Greg wrote:
Live connected. Get Hotmail & Messenger for mobile. __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |