RE: [EnergyPlus_Support] AFN Node Pressure Distribution & Air Density
My answers are under your questions.
1a) Where is the Zone_Node situated Floor/ceiling/center?
A: Center.
1b) Is there a link to the room-air-model (temperature at a specific height
- if not mixed air)?
A: No.
1c) could you please give the formuala for the zone 'AirflowNetwork Node
Total Pressure'? Especially how is the zone static pressure calculated?
A: The model uses the total pressure, The static pressure is not calculated
alone. The section of AirflowNetwork model in the Engineering Reference
provides detailed information.
2) For the calculation of the air density i used following formula, which
wasn't found in the eng.reference - but it gives slightly different results:
ρ=(P_atm (1+W_air))/(461,518(T_air+273,15)(W_air+0,62198)) [kg/m3]
ρ = Air density [kg/m3]
Patm = Outdoor barometric pressure at ground level [Pa]
Wair = Air humidity ratio [kgWater/kgAir]
Tair = Air Temperature [°C]
A: the following equation is used to calculate air density
rhoair = pb/(287.d0*(tdb+KelvinConv)*(1.d0+1.6077687d0*w))
Lixing
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a
high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
Documentation link and press the "search" button.
Yahoo! Groups Links
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/