[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: AFN Node Pressure Distribution & Air Density
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: AFN Node Pressure Distribution & Air Density
- From: "tobiasschulzeoooitu" <tobias.schulze@xxxxxxxxxxxxxx>
- Date: Mon, 03 May 2010 11:48:52 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Mon, 03 May 2010 05:53:27 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1272887606; bh=5n/5bFNRLYUyeXG97GXq3qvPbUpYLSQFe+8FhnAmoDU=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=bXVcLT993Za6Y79CBFH34LiRfmFbOKC5PaL1K11fklXZAhraKRWRBXISAx9HtUTLaZbXeKHzn+6nINs//wKVtkLdek1NdZ7MeBHs7YFXxrkgpaQXBtFJYXPKyb2GD3w+
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=tb0L9lb2w5WT4UD4w2egrV52gLBJgDzcud5lcH58+D2UqTgqiEJb6sGJ1oXz7BaIbR/9pD4ITiKw7jOkZ4MVq7v1MvAdndzB7tZcucGf1red8gOpyL9OSdwLiomQr92G;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <003a01cae235$32d0f6e0$9872e4a0$@ucf.edu>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Dear Lixing,
Thank you for your prompt answer. I have one more question about vertical airflow in the AFN which for I first should describe my model a little.
I try to connect several floors of a high rise building to a common used thermal chimney. So this stack has openings on different heights to different zones. I simulated the case 1) with one chimney zone 2) multi chimney zones (one per floor) connected by horizontal openings (90deg Cd=1). With the one zone chimney i had a faster decrease of flow rates from bottom to higher floors than with the multi zone model.
Anyway, my question is, if it is a meaningful way to connect more than 2 zones vertically by horizontal openings? What are the restictions here? There is one example file available, where only two zones are stacked (AirflowNetwor_Multizone_HorizontalOpening.idf). Would the model work, if more zones are stacked, for example in stairways, elevator stack, atrium or double skin facade? I wonder if the AFN Restriction In-Out-Ref also counts for horizontal openings connections or if it was written before the introduction of horiz.open. in E+.
"Air circulation and/or air temperature stratification within thermal zone. For example, you should not try to divide a high space, such as an atrium, into subzones separated by artificial horizontal surfaces that have cracks or openings with the expectation that AirflowNetwork will give you a realistic temperature in each subzone and/or a realistic air flow between subzones."
If you would know a reference dealing with a similar problem, that would be also helpful for me.
Best regards,
Tobias
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>
> My answers are under your questions.
>
> 1a) Where is the Zone_Node situated Floor/ceiling/center?
>
> A: Center.
>
> 1b) Is there a link to the room-air-model (temperature at a specific height
> - if not mixed air)?
>
> A: No.
>
> 1c) could you please give the formuala for the zone 'AirflowNetwork Node
> Total Pressure'? Especially how is the zone static pressure calculated?
>
> A: The model uses the total pressure, The static pressure is not calculated
> alone. The section of AirflowNetwork model in the Engineering Reference
> provides detailed information.
>
> 2) For the calculation of the air density i used following formula, which
> wasn't found in the eng.reference - but it gives slightly different results:
>
> ρ=(P_atm (1+W_air))/(461,518(T_air+273,15)(W_air+0,62198)) [kg/m3]
> ρ = Air density [kg/m3]
> Patm = Outdoor barometric pressure at ground level [Pa]
> Wair = Air humidity ratio [kgWater/kgAir]
> Tair = Air Temperature [°C]
>
> A: the following equation is used to calculate air density
> rhoair = pb/(287.d0*(tdb+KelvinConv)*(1.d0+1.6077687d0*w))
>
> Lixing
>
> ------------------------------------
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a
> high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> Yahoo! Groups Links
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/