Thank you for your prompt answer. I have one more question about vertical airflow in the AFN which for I first should describe my model a little.
I try to connect several floors of a high rise building to a common used thermal chimney. So this stack has openings on different heights to different zones. I simulated the case 1) with one chimney zone 2) multi chimney zones (one per floor) connected by horizontal openings (90deg Cd=1). With the one zone chimney i had a faster decrease of flow rates from bottom to higher floors than with the multi zone model.
Anyway, my question is, if it is a meaningful way to connect more than 2 zones vertically by horizontal openings? What are the restictions here? There is one example file available, where only two zones are stacked (AirflowNetwor_Multizone_HorizontalOpening.idf). Would the model work, if more zones are stacked, for example in stairways, elevator stack, atrium or double skin facade? I wonder if the AFN Restriction In-Out-Ref also counts for horizontal openings connections or if it was written before the introduction of horiz.open. in E+.

"Air circulation and/or air temperature stratification within thermal zone. For example, you should not try to divide a high space, such as an atrium, into subzones separated by artificial horizontal surfaces that have cracks or openings with the expectation that AirflowNetwork will give you a realistic temperature in each subzone and/or a realistic air flow between subzones."

If you would know a reference dealing with a similar problem, that would be also helpful for me.
Best regards,
Tobias



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Lixing Gu <gu@...> wrote:
>
> My answers are under your questions.
> 
> 1a) Where is the Zone_Node situated Floor/ceiling/center?
> 
> A: Center.
> 
> 1b) Is there a link to the room-air-model (temperature at a specific height
> - if not mixed air)?
> 
> A: No.
> 
> 1c) could you please give the formuala for the zone 'AirflowNetwork Node
> Total Pressure'? Especially how is the zone static pressure calculated?
> 
> A: The model uses the total pressure, The static pressure is not calculated
> alone. The section of AirflowNetwork model in the Engineering Reference
> provides detailed information.
>  
> 2) For the calculation of the air density i used following formula, which
> wasn't found in the eng.reference - but it gives slightly different results:
> 
> &#961;=(P_atm (1+W_air))/(461,518(T_air+273,15)(W_air+0,62198))     [kg/m3]
> &#961; = Air density [kg/m3]
> Patm = Outdoor barometric pressure at ground level [Pa]
> Wair = Air humidity ratio [kgWater/kgAir]
> Tair = Air Temperature [°C]
> 
> A: the following equation is used to calculate air density
>       rhoair = pb/(287.d0*(tdb+KelvinConv)*(1.d0+1.6077687d0*w))
> 
> Lixing
> 
> ------------------------------------
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are currently allowed but be mindful that not everyone has a
> high speed connection.  Limit attachments to small files.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
> Documentation link and press the "search" button.
> Yahoo! Groups Links
>




------------------------------------

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/