[EnergyPlus_Support] Re: FindRootSimpleController: Controller error
The following are other setpoint managers
SetpointManager:OutdoorAirReset,
Chiller1 ChW Temp Manager, !- Name
Temperature, !- Control Variable
12.2, !- Setpoint at Outdoor Low Temperature {C}
15.6, !- Outdoor Low Temperature {C}
6.7, !- Setpoint at Outdoor High Temperature {C}
26.7, !- Outdoor High Temperature {C}
Chiller1 ChW Supply Outlet; !- Setpoint Node or NodeList Name
SetpointManager:OutdoorAirReset,
HWLForFanCoils HW Temp Manager, !- Name
Temperature, !- Control Variable
82.2, !- Setpoint at Outdoor Low Temperature {C}
-6.7, !- Outdoor Low Temperature {C}
65.6, !- Setpoint at Outdoor High Temperature {C}
10, !- Outdoor High Temperature {C}
HWLForFanCoils HW Supply Outlet; !- Setpoint Node or NodeList Name
Thanks
-Ven
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Fred Buhl <wfbuhl@...> wrote:
>
> From the warning message, it appears that the setpoint temperature is
> 11.89, not 24 as
> you wish. And the chilled water entering the coil is at 24.81 C, too
> warm to do any cooling.
> Probably the chiller is off. Is there some other SetpointManager setting
> the setpoint?
>
> Fred Buhl
>
> On 5/7/2010 8:36 AM, eplusven wrote:
> > Hi all,
> >
> > Could you please help how do i resolve this. Actually i wanted to model AHU air supply always 24C, becasue my Fancoil units will further does cooling or heating. For this reason I set the controller as
> >
> > SetpointManager:OutdoorAirReset,
> > Supply Air Temp Manager 1, !- Name
> > Temperature, !- Control Variable
> > 24, !- Setpoint at Outdoor Low Temperature {C}
> > -9, !- Outdoor Low Temperature {C}
> > 24, !- Setpoint at Outdoor High Temperature {C}
> > 35, !- Outdoor High Temperature {C}
> > Supply Air Temp Nodes 1; !- Setpoint Node or NodeList Name
> > This si giving problem only for one month i.e May. But rest of teh months the simulation going well with lot of warnings
> >
> >
> > ** Severe ** FindRootSimpleController: Controller error for controller = CENTRAL COOLING COIL CONTROLLER 1
> > ** ~~~ ** Occurrence info=MonSIM, 05/02 06:15 - 06:30
> > ** ~~~ ** Controller function is inconsistent with user specified controller action = Reverse action
> > ** ~~~ ** Actuator will be set to maximum action
> > ** ~~~ ** Controller control type=Temperature
> > ** ~~~ ** Controller temperature set point = 11.89 [C]
> > ** ~~~ ** Controller sensed temperature = 23.56 [C]
> > ** ~~~ ** Controller actuator mass flow rate set to 116.44 [kg/s]
> > ** ~~~ ** Controller actuator temperature = 24.81 [C]
> > ** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled
> > ** ~~~ ** water temperature (controller actuator temperature) should be below the setpoint temperature
> >
> >
> >
> > Thanks
> > -Ven
> >
> >
> >
> > ------------------------------------
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >
>
------------------------------------
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/