Look at the Location Design days spreadsheet in the MacroDataSets folder -- leads to a IMF file for design day conditions by location/WMO region.

##ifdef CHN_HARBIN
 Site:Location,
   Harbin CHN WMO=509530,     !- Location Name
      45.75,     !- Latitude {N+ S-}
     126.77,     !- Longitude {W- E+}
       8.00,     !- Time Zone Relative to GMT {GMT+/-}
     143.00;     !- Elevation {m}
 
 !  WMO=509530 Time Zone=CHN        (GMT+08:00) Beijing, Chongqing, Hong Kong, Urumqi
 !  Data Source=ASHRAE 2009 Annual Design Conditions
 
 ! Using Design Conditions from "Climate Design Data 2009 ASHRAE Handbook"
 ! Harbin CHN Extreme Annual Wind Speeds, 1%=9.1m/s, 2.5%=7.5m/s, 5%=6.6m/s
 ! Harbin CHN Extreme Annual Temperatures, Max Drybulb=-30.9°C Min Drybulb=33.5°C
 
 ! Harbin CHN Annual Heating Design Conditions Wind Speed=1.2m/s Wind Dir=200
 ! Coldest Month=January
 ! Harbin CHN Annual Heating 99.6%, MaxDB=-28.4°C
 SizingPeriod:DesignDay,
  Harbin Ann Htg 99.6% Condns DB,     !- Name
      -28.4,      !- Max Dry-Bulb {C}
        0.0,      !- Daily Temp Range {C}
      -28.4,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        1.2,      !- Wind Speed {m/s} design conditions vs. traditional 6.71 m/s (15 mph)
        200,      !- Wind Direction {Degrees; N=0, S=180}
       0.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          1,      !- Month
  WinterDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Heating 99%, MaxDB=-25.9°C
 SizingPeriod:DesignDay,
  Harbin Ann Htg 99% Condns DB,     !- Name
      -25.9,      !- Max Dry-Bulb {C}
        0.0,      !- Daily Temp Range {C}
      -25.9,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        1.2,      !- Wind Speed {m/s} design conditions vs. traditional 6.71 m/s (15 mph)
        200,      !- Wind Direction {Degrees; N=0, S=180}
       0.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          1,      !- Month
  WinterDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Humidification 99.6% Design Conditions DP=>MCDB, DP=-31.8°C
 SizingPeriod:DesignDay,
  Harbin Ann Hum_n 99.6% Condns DP=>MCDB,     !- Name
      -27.7,      !- Max Dry-Bulb {C}
        0.0,      !- Daily Temp Range {C}
      -31.8,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        1.2,      !- Wind Speed {m/s} design conditions vs. traditional 6.71 m/s (15 mph)
        200,      !- Wind Direction {Degrees; N=0, S=180}
       0.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          1,      !- Month
  WinterDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Dewpoint;     !- Humidity Indicating Type
 
 ! Harbin CHN Annual Humidification 99% Design Conditions DP=>MCDB, DP=-29.4°C
 SizingPeriod:DesignDay,
  Harbin Ann Hum_n 99% Condns DP=>MCDB,     !- Name
      -24.6,      !- Max Dry-Bulb {C}
        0.0,      !- Daily Temp Range {C}
      -29.4,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        1.2,      !- Wind Speed {m/s} design conditions vs. traditional 6.71 m/s (15 mph)
        200,      !- Wind Direction {Degrees; N=0, S=180}
       0.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          1,      !- Month
  WinterDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Dewpoint;     !- Humidity Indicating Type
 
 ! Harbin CHN Annual Heating Wind 99.6% Design Conditions WS=>MCDB, WS=8.3m/s
 SizingPeriod:DesignDay,
  Harbin Ann Htg Wind 99.6% Condns WS=>MCDB,     !- Name
      -11.6,      !- Max Dry-Bulb {C}
        0.0,      !- Daily Temp Range {C}
      -11.6,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        8.3,      !- Wind Speed {m/s} design conditions vs. traditional 6.71 m/s (15 mph)
        200,      !- Wind Direction {Degrees; N=0, S=180}
       0.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          1,      !- Month
  WinterDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Heating Wind 99% Design Conditions WS=>MCDB, WS=7.4m/s
 SizingPeriod:DesignDay,
  Harbin Ann Htg Wind 99% Condns WS=>MCDB,     !- Name
        -12,      !- Max Dry-Bulb {C}
        0.0,      !- Daily Temp Range {C}
        -12,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        7.4,      !- Wind Speed {m/s} design conditions vs. traditional 6.71 m/s (15 mph)
        200,      !- Wind Direction {Degrees; N=0, S=180}
       0.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          1,      !- Month
  WinterDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin Annual Cooling Design Conditions Wind Speed=4.1m/s Wind Dir=220
 ! Hottest Month=July
 ! Harbin CHN Annual Cooling (DB=>MWB) .4%, MaxDB=31.1°C MWB=20.8°C
 SizingPeriod:DesignDay,
  Harbin Ann Clg .4% Condns DB=>MWB,     !- Name
       31.1,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       20.8,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (DB=>MWB) 1%, MaxDB=29.6°C MWB=20.6°C
 SizingPeriod:DesignDay,
  Harbin Ann Clg 1% Condns DB=>MWB,     !- Name
       29.6,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       20.6,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (DB=>MWB) 2%, MaxDB=28.2°C MWB=20.4°C
 SizingPeriod:DesignDay,
  Harbin Ann Clg 2% Condns DB=>MWB,     !- Name
       28.2,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       20.4,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (WB=>MDB) .4%, MDB=28°C WB=24.1°C
 SizingPeriod:DesignDay,
  Harbin Ann Clg .4% Condns WB=>MDB,     !- Name
         28,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       24.1,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (WB=>MDB) 1%, MDB=26.8°C WB=23.2°C
 SizingPeriod:DesignDay,
  Harbin Ann Clg 1% Condns WB=>MDB,     !- Name
       26.8,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       23.2,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (WB=>MDB) 2%, MDB=25.9°C WB=22.4°C
 SizingPeriod:DesignDay,
  Harbin Ann Clg 2% Condns WB=>MDB,     !- Name
       25.9,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       22.4,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Wetbulb;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (DP=>MDB) .4%, MDB=26.5°C DP=23°C HR=0.0180
 SizingPeriod:DesignDay,
  Harbin Ann Clg .4% Condns DP=>MDB,     !- Name
       26.5,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
         23,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Dewpoint;     !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (DP=>MDB) 1%, MDB=25.7°C DP=22.1°C HR=0.0170
 SizingPeriod:DesignDay,
  Harbin Ann Clg 1% Condns DP=>MDB,     !- Name
       25.7,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       22.1,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Dewpoint;     !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (DP=>MDB) 2%, MDB=24.8°C DP=21.1°C HR=0.0161
 SizingPeriod:DesignDay,
  Harbin Ann Clg 2% Condns DP=>MDB,     !- Name
       24.8,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       21.1,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Dewpoint;     !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (Enthalpy=>MDB) .4%, MDB=28°C Enthalpy=73.8kJ/kg
 SizingPeriod:DesignDay,
  Harbin Ann Clg .4% Condns Enth=>MDB,     !- Name
         28,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       73.8,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Enthalpy;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (Enthalpy=>MDB) 1%, MDB=26.9°C Enthalpy=70.3kJ/kg
 SizingPeriod:DesignDay,
  Harbin Ann Clg 1% Condns Enth=>MDB,     !- Name
       26.9,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       70.3,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Enthalpy;      !- Humidity Indicating Type
 
 ! Harbin CHN Annual Cooling (Enthalpy=>MDB) 2%, MDB=26°C Enthalpy=66.9kJ/kg
 SizingPeriod:DesignDay,
  Harbin Ann Clg 2% Condns Enth=>MDB,     !- Name
         26,      !- Max Dry-Bulb {C}
        8.1,      !- Daily Temp Range {C}
       66.9,      !- Humidity Indicating Condition at Max Dry-Bulb
     99619.,      !- Barometric Pressure {Pa}
        4.1,      !- Wind Speed {m/s} design conditions vs. traditional 3.35 m/s (7mph)
        220,      !- Wind Direction {Degrees; N=0, S=180}
       1.00,      !- Clearness {0.0 to 1.1}
          0,      !- Rain {0-no,1-yes}
          0,      !- Snow on ground {0-no,1-yes}
         21,      !- Day of Month
          7,      !- Month
  SummerDesignDay,!- Day Type
          0,      !- Daylight Savings Time Indicator
   Enthalpy;      !- Humidity Indicating Type
 
##endif

At 03:25 PM 5/13/2010, L Herrmann wrote:


Hi EP Group,

Does anyone know where I can find design days for Harbin, China?  I'm looking for the following:

Ann Htg 99.6% Condns DB
Ann Clg .4% Condns DB=>MWB
Ann Clg .4% Condns WB=>MDB

I currently have degree days that do not specify the conditions (i.e. 99.6%, 92%...).  Are there significant differences between different types of desing days? 

Thanks,
Lesley





__._,_.___


The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___