|
It won’t work to connect multiple loops
using some tricky configuration. In general, nodes and connectors need to
be unique across different plant loops; you are not allowed to use
splitter/mixers to cross-wire loops. Certain types of component models do
“connect” separate loops but it is usually pretty clear from the
node input fields that they are intended for that purpose. You can use a single condenser loop to serve
multiple chillers and multiple towers. The splitter/mixer for the towers
will mix cooled condenser water before returning to the chillers. From: Is is possible to put the same connectors (connector
list) on multiple loops? __._,_.___ The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |