Re: [EnergyPlus_Support] Re: An error when applied the UCSD Displacement Ventilation Module





You need to send your input file to the helpdesk and state the problem there.

At 12:48 AM 6/11/2010, chilu32 wrote:
Hi , was there ever a solution to the problem stated below? I have the same problem when using E+ v5.0 .

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Zhen Tian <tianzhen9@...> wrote:
>
> Thanks, Mike.
>
> If I delete all the Room Air Mode for the zones with the UCDS DV, then these errors are gone,even I have the RoomAir Mode inputs for the UCDS UFAD. It seems this error is in the DV mode itself.
>
> I checked the zone inputs for the internal loads. These inputs are based on design data and all seems normal.
>
> Thanks.
>
> Regards,
>
> David
>
> "Michael J. Witte" <mjwitte@...> wrote:                               This type of error will trip on the first zone that goes past the limit, so it
>  is not surprising that fixing one zone will lead to failure in another similar
>  zone.  If you delete all of the room air models, does the simulation run
>  normally?
> 
>  Mike
> 
>  On 4 Feb 2008 at 12:40, Zhen Tian wrote:
> 
>  > Thanks, Mike.
>  >
>  > Actually this error only appears when I add the UCSD DV module into the zones.
>  > There is no problem when I use the UCSD UFAD module or use conventional mixing
>  > module.
>  >
>  > I tried to delete the RoomAir Model for the zone with errors. Then, another zone
>  > appears the same error and causes the simulation to crash.
>  >
>  > Thanks.
>  >
>  > Regards,
>  >
>  > David
>  >
>  >
>  >
>  > "Michael J. Witte" <mjwitte@...> wrote:                               It is
>  > difficult to say without more information.  My guess is that there is
>  >  something wrong with the ventilation inputs and the zone is overheating from
>  >  solar or internal gains.  Did the simulation progress far enough to report any
>  >  output?  Perhaps you can report zone air and surface temperatures and determine
>  >  more about the problem.
>  >
>  >  Mike
>  >
>  >  On 29 Jan 2008 at 13:12, Zhen Tian wrote:
>  >
>  >  > Dear all,
>  >  >
>  >  > I modeled one floor of a building with displacement ventilation builidng. I
>  >  used > the UCSD Displacement ventilation module in my simulaiton model. Then I
>  >  got the > following warnings and error. > > "Warning ** Calculated Relative
>  >  Humidity out of range (PsyRhFnTdbWPb) >    **   ~~~   **  Occurrence
>  >  info=CALGARY INT'L AB CAN WYEC2-B-25110 >    WMO#=718770, 01/02 05:00 - 05:10
>  >  **   ~~~   **  Dry-Bulb= -333.04 Humidity >    Ratio= 1.000E-005 Calculated
>  >  Relative Humidity (fraction)= 844.67 **   ~~~  >    ** Relative Humidity being
>  >  reset to 1.0 > ... > > Severe  ** Temperature out of bounds (219.18) for
>  >  surface=SUBOBJ:0468 >    **   ~~~   ** in Zone=Z106 >    **   ~~~   **
>  >  Occurrence info=CALGARY INT'L AB CAN WYEC2-B-25110 >    WMO#=718770, 01/02
>  >  05:05 - 05:06 **   ~~~   ** A temperature out of bounds >    problem can be
>  >  caused by several things.  The user **   ~~~   ** should check >    the weather
>  >  environment, the level of internal gains with respect **   ~~~  >    ** to the
>  >  zone, and the thermal properties of their materials among other >    things. **
>  >    ~~~   ** A common cause is a building with no thermal mass -- >    all
>  >  materials with **   ~~~   ** Regular-R definitions." > > But I did not use
>  >  reguar-r for building materials and construciton. In addition, > the model
>  >  without the UCSD DV module has not problem. > > Does someone has the same
>  >  experiences before and can tell me how to resolve this > issue? > > Thanks a
>  >  lot in advance. > > Regards, > > David > > > >
>  >  --------------------------------- > Looking for last minute shopping deals?
>  >  Find them fast with Yahoo! Search. > > [Non-text portions of this message have
>  >  been removed] > > > > The primary EnergyPlus web site is found at: >
>  >  http://www.energyplus.gov > > The group web site is: >
>  >  http://groups.yahoo.com/group/EnergyPlus_Support/ > > Attachments are not
>  >  allowed -- please post any files to the appropriate folder > in the Files area
>  >  of the Support Web Site. > > EnergyPlus Documentation is searchable.  Open
>  >  EPlusMainMenu.pdf under the > Documentation link and press the "search" button.
>  >  > > Yahoo! Groups Links > > > > >
>  >
>  >  ========================================================
>  >  Michael J. Witte, GARD Analytics, Inc.
>  >  EnergyPlus Testing and Support     
>  >  EnergyPlus-Support@...
>  >
>  >
>  >
>  >
>  >
>  >
>  > ---------------------------------
>  > Never miss a thing.   Make Yahoo your homepage.
>  >
>  > [Non-text portions of this message have been removed]
>  >
>  >
>  >
>  > The primary EnergyPlus web site is found at:
>  > http://www.energyplus.gov
>  >
>  > The group web site is:
>  > http://groups.yahoo.com/group/EnergyPlus_Support/
>  >
>  > Attachments are not allowed -- please post any files to the appropriate folder
>  > in the Files area of the Support Web Site.
>  >
>  > EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the
>  > Documentation link and press the "search" button.
>  >
>  > Yahoo! Groups Links
>  >
>  >
>  >
>  >
>  >
> 
>  ========================================================
>  Michael J. Witte, GARD Analytics, Inc.
>  EnergyPlus Testing and Support     
>  EnergyPlus-Support@...
> 
> 
>     
>                               
>
>       
> ---------------------------------
> Be a better friend, newshound, and know-it-all with Yahoo! Mobile.  Try it now.
>
> [Non-text portions of this message have been removed]
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___