On 6/13/2010 12:19 PM, jlcvrosa wrote:
> Hello,
>
> I need to size a chiller but i´m having some problems with the sizing period and the schedules to use.
> In the SizingPeriod:Design Day, what is the difference between choosing SummerDesign Day or for example Wednesday? I think that if i choose Wedneday the program will assume the values in the schedules for ocupation, ilumination and equipment as a normal weekday. I´m i right?
>
Yes. The purpose of SummerDesign is to allow you to specify special
schedules that are used only in the sizing calulation. For instance,
I use the normal week day schedules for occupancy, lights, equip etc but
I use flat (no set back or set up) schedules for the zone
thermostats.
> Also in the SizingPeriod:Design Day if i choose SummerDesignDay, i need to put this type of day in my sechedule, like "Through: 31 Dec For: Weekdays SummerDesignDay...."? In the schedules if i have "For:AllOtherDays" this will also include de design days, SummerDesignDay and WinterDesignDay?
>
Yes.
> One last question. It is possible when calculating the design loads to account for a heat recovery system?
>
The design loads can't model this..
> Thanks for your help.
>
> Joao
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/