[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: ASHRAE qurey on water cooled chillers
Hi Vignesh,
Take note that in ASHRAE 90.1-2007 Section G3.1.3.7 it mentions that
"... The baseline building design's chiller plant shall be modeled with chillers having the number and type as indicated in Table G3.1.3.7 as a function of building peak load."
Table G3.1.3.7 only specifies WATER COOLED CHILLERS.
If you'd like the exact clause, I think the clause "... having the number and type..." will be enough to answer your question.
Regards
Reniel Barroso
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, vignesh kumar <vigneshkumar1986@...> wrote:
>
> Hi
>
> I have a qurey in ASHRAE 90.1 ,like is there any where mentioned like
> we should use only water cooled chillers in in Base case Model , if the
> conditioned area of the building is greater than 150000 sqft , it has
> mentioned only about using chilled water plant , nothing about the condenser
> part , any advice would be helpful
>
> Regards
> --
> vigneshkumar
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/