[EnergyPlus_Support] Re: ASHRAE qurey on water cooled chillers



Hi Vignesh,

Take note that in ASHRAE 90.1-2007 Section G3.1.3.7 it mentions that 

"... The baseline building design's chiller plant shall be modeled with chillers having the number and type as indicated in Table G3.1.3.7 as a function of building peak load."

Table G3.1.3.7 only specifies WATER COOLED CHILLERS.

If you'd like the exact clause, I think the clause "... having the number and type..." will be enough to answer your question.


Regards


Reniel Barroso



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, vignesh kumar <vigneshkumar1986@...> wrote:
>
> Hi
> 
> I  have a qurey in ASHRAE 90.1 ,like  is there any where mentioned like
> we should use only water cooled chillers in  in Base case Model , if the
> conditioned area of the building is greater than 150000 sqft , it has
> mentioned only about using chilled water plant , nothing about the condenser
> part , any advice would be helpful
> 
> Regards
> -- 
> vigneshkumar
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/