Hi Vignesh,
 
You will not be able to find such clause other than the one mentioned in ASHRAE 90.1-2004 Section G3.1.3.11 where it mentions
 
"G3.1.3.11 Heat Rejection (Systems 7 & 8). The heat rejection device shall be an axial fan cooling tower with two speed fans..." 
 
which translates to water-cooled chiller system.
 
Hope I helped you in this way.
 
 
Reniel



--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, vignesh kumar <vigneshkumar1986@...> wrote:
>
> Thanks Reniel ,
> 
> i had a look in to the ASHRAE- 90.1 -  2007 , in the table itself it is
> mentioned as Water cooled chillers only , but the problem is in ASHRAE 90.1-
>  2004, it is mentioned nowhere in ASHRAE-2004 , is there any addenda or
> errata is there which explains
> 
> 
> 
> Thanks and Regards
> 
> vignesh
> 
> 
> On Mon, Jun 21, 2010 at 6:58 PM, renielbarroso <renielbarroso@...>wrote:
> 
> >
> >
> >
> > Hi Vignesh,
> >
> > Take note that in ASHRAE 90.1-2007 Section G3.1.3.7 it mentions that
> >
> > "... The baseline building design's chiller plant shall be modeled with
> > chillers having the number and type as indicated in Table G3.1.3.7 as a
> > function of building peak load."
> >
> > Table G3.1.3.7 only specifies WATER COOLED CHILLERS.
> >
> > If you'd like the exact clause, I think the clause "... having the number
> > and type..." will be enough to answer your question.
> >
> > Regards
> >
> > Reniel Barroso
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx<EnergyPlus_Support%40yahoogroups.com>,
> > vignesh kumar <vigneshkumar1986@> wrote:
> > >
> > > Hi
> > >
> > > I have a qurey in ASHRAE 90.1 ,like is there any where mentioned like
> > > we should use only water cooled chillers in in Base case Model , if the
> > > conditioned area of the building is greater than 150000 sqft , it has
> > > mentioned only about using chilled water plant , nothing about the
> > condenser
> > > part , any advice would be helpful
> > >
> > > Regards
> > > --
> > > vigneshkumar
> > >
> >
> >  
> >
> 
> 
> 
> -- 
> vigneshkumar
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/