The message is telling you that the flow rate through the HX has fallen
to 49.4% of the nominal flow rate (see documentation for this HX). The
is below the threshold where the simulation can accurately predict HX
performance. Have you tried increasing the minimum OA flow rate
(Controller:OutdoorAir)?
O. Tugrul Karaguzel wrote:
>
> Hi all,
> I'm repeatedly having the following warning for my Energy Plus model
> in which i tried to simulate a heat recovery system
(using
> HeatExchanger:AirToAir:SensibleAndLatent).
>
> ** Warning ** HeatExchanger:AirToAir:SensibleAndLatent "OA HEAT
> RECOVERY 3"
> ** ~~~ ** Average air volume flow rate is <50% or >130% of the nominal
> HX supply air volume flow rate.
> ** ~~~ ** Air volume flow rate ratio = 0.494. Occurrence info=
> HEADMASTER'S RESIDENCE, 01/01 08:00 - 08:15
>
> Does anyone have experience with such a warning? I tried to overcome
> it by changing input parameters in objects of Controller:OutdoorAir or
> Fan:VariableVolume or Sizing:System but unfortunately I cannot manage
> to solve it.
> Many Thanks.
>
> Omer T. Karaguzel
> Center for Building Performance & Diagnostics
> Carnegie Mellon University
> 5000 Forbes Ave. Pittsburgh, 15213 PA
>
>
>
>
--
Richard A. Raustad
Senior Research
Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at:
http://www.fsec.ucf.eduUCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to
energyplus-support@xxxxxxxxThe primary EnergyPlus web site is found at:
http://www.energyplus.govThe group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join (Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/