[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: Modelling Displacement Ventilation





I didn't have a chance to look at your model yet. I will do that when I go back to work on Monday, but let me give you an idea about energy savings with displacement ventilation and how to get them:

-Because supply air temperature is high (19 degree c) there will be more chances to use more free cooling if the outdoor conditions are suitable (cooling only savings). Note: to do that you should have an economizer.
-Because of the higher ventilation effectiveness of displacement ventilation, when the outdoor conditions are very hot, less outdoor flow could be used with DV which leads to energy savings as well (cooling and heating). Note: you need to define that in the object (controller:outdoor air).

However .. these savings could be easily canceled, and even more energy use could happen because of:
1-  The higher fan power due to higher flow rates with DV. This is because smaller d(t) between supply air and room set point requires higher flow to handle cooling loads. Note that the effect of increasing flow rate on energy use is cubical. 
2- If there is a need for humidity control, the air will need to be cooled anyway for de-humidification which will cancel savings due to free cooling even if the outdoor temperature is suitable, unless another way of de-humidification other than cooling is used.
3- In the case of heating with 100% outdoor air, all heating inputs from the lighting are canceled. However, this is an advantage in the case of cooling with 100% outdoor air.

In conclusion if you want energy savings with DV you should :

-Have outdoor conditions suitable for free cooling (dry and below 19 degree c) 
-Or/and separate between thermal control and ventilation. e.g., use DV for ventilation only and use chilled ceiling for cooling.
-Or/and have a conditioned space that requires a very high ventilation rate due to high occupancy levels, e.g. class rooms
 
I hope that was useful

Cheers

Alaa Kandil
Calgary, Canada



From: "Lombe, Chilufya" <Chilufya.Lombe@xxxxxxxxxxxxxx>
To: alaak1974@xxxxxxxxx
Sent: Thu, July 1, 2010 7:00:34 AM
Subject: Re: Modelling Displacement Ventilation

Hi , thanks for replying to my post. I was expecting to get lower energy usage for the displacement system. I have attached my idf files , I followed the example files quite closely and went through the input/output reference as well but I was expecting some kind of reduced energy usage from the DV. To my knowledge , users donâ??t have control over the air velocity into the room (except for PMV calcs) so the settings I change was only the supply air temp (apart from adding the room air models).

 

10b.

Re: Modelling Displacement Ventilation

Posted by: "alaa kandil" alaak1974@xxxxxxxxx   alaak1974

Thu Jul 1, 2010 12:20 am (PDT)



I have some experience with modeling displacement ventilation with energy plus and I think I can help .. what kind of results did u get ? why do u think results are strange ? what were you expecting?

Alaa Kandil
Calgary, Canada

________________________________
From: chilu32 <chilufya.lombe@xxxxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Thu, July 1, 2010 12:07:59 AM
Subject: [EnergyPlus_Support] Modelling Displacement Ventilation

Hi , I am trying to do a simple comparison between a displacement ventilation system and a normal mixed zone system. The energy consumption numbers I get back don't make sense and I am trying to troubleshoot my inputs. Anyone have similar experience?? I added the room air models and changed supply air temp to 18C for the DV model.

 

 



_______________________________________________________________________________________
Chilufya Lombe
Electro-Mechanical Engineer

WSP Consulting Engineers SA Pty Ltd | P.O. Box 2613 | CAPE TOWN | 8000 | South Africa
Tel: +27 (0)21 481-8649 | Fax: +27 (0)21 481-8799 | Cell: +27 (0)82 403-2024
e-Mail: chilufya.lombe@xxxxxxxxxxxxxx

www.wspgroup.co.za
_______________________________________________________________________________________
This email and all contents are subject to the following disclaimer.
http://www1.wspgroup.co.za/disclaimer.htm

P Help save paper - do you really need to print this email?

 




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___