Hi
, I got the model working more realistically. I added the economiser and
noticed a decrease in chiller power consumption and an increase in fan energy
as predicted below. Atleast now I know the model is working correctly and can adjust
setpoint temperatures etc to optimise the system. Thanks for the info you
provided .
Chilu
Cape
Town , South Africa
From: alaa kandil [mailto:alaak1974@xxxxxxxxx]
Sent: 02 July 2010 08:55 AM
To: Lombe, Chilufya
Cc: energyplus_support@xxxxxxxxxxxxxxx
Subject: Re: Modelling Displacement Ventilation
I didn't have a chance to
look at your model yet. I will do that when I go back to work on Monday, but
let me give you an idea about energy savings with displacement ventilation and
how to get them:
-Because supply air temperature is high (19 degree c) there will be more
chances to use more free cooling if the outdoor conditions are suitable
(cooling only savings). Note: to do that you should have an economizer.
-Because of the higher ventilation effectiveness of displacement ventilation,
when the outdoor conditions are very hot, less outdoor flow could be used with
DV which leads to energy savings as well (cooling and heating). Note: you
need to define that in the object (controller:outdoor air).
However .. these savings could be easily canceled, and even more energy
use could happen because of:
1- The higher fan power due to higher flow rates with DV. This is because
smaller d(t) between supply air and room set point requires higher flow to
handle cooling loads. Note that the effect of increasing flow rate on energy
use is cubical.
2- If there is a need for humidity control, the air will need to be cooled
anyway for de-humidification which will cancel savings due to free cooling even
if the outdoor temperature is suitable, unless another way of de-humidification
other than cooling is used.
3- In the case of heating with 100% outdoor air, all heating inputs from the
lighting are canceled. However, this is an advantage in the case of cooling
with 100% outdoor air.
In conclusion if you want energy savings with DV you should :
-Have outdoor conditions suitable for free cooling (dry and below 19 degree
c)
-Or/and separate between thermal control and ventilation. e.g., use DV for
ventilation only and use chilled ceiling for cooling.
-Or/and have a conditioned space that requires a very high ventilation rate due
to high occupancy levels, e.g. class rooms
I hope that was useful
Cheers
Alaa Kandil
Calgary, Canada
From: "Lombe, Chilufya"
<Chilufya.Lombe@xxxxxxxxxxxxxx>
To: alaak1974@xxxxxxxxx
Sent: Thu, July 1, 2010 7:00:34 AM
Subject: Re: Modelling Displacement Ventilation
Hi , thanks for replying to my post. I was expecting to get
lower energy usage for the displacement system. I have attached my idf files ,
I followed the example files quite closely and went through the input/output
reference as well but I was expecting some kind of reduced energy usage from
the DV. To my knowledge , users don’t have control over the air velocity into
the room (except for PMV calcs) so the settings I change was only the supply
air temp (apart from adding the room air models).
10b.
Thu
Jul 1, 2010 12:20 am (PDT)
I have some experience with modeling displacement ventilation with energy plus
and I think I can help .. what kind of results did u get ? why do u think
results are strange ? what were you expecting?
Alaa Kandil
Calgary, Canada
________________________________
From: chilu32 <chilufya.lombe@xxxxxxxxxxxxxx>
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Sent: Thu, July 1, 2010 12:07:59 AM
Subject: [EnergyPlus_Support] Modelling Displacement Ventilation
Hi , I am trying to do a simple comparison between a displacement ventilation
system and a normal mixed zone system. The energy consumption numbers I get
back don't make sense and I am trying to troubleshoot my inputs. Anyone have
similar experience?? I added the room air models and changed supply air temp to
18C for the DV model.
_______________________________________________________________________________________
Chilufya Lombe
Electro-Mechanical Engineer
WSP Consulting Engineers SA Pty Ltd | P.O. Box 2613 | CAPE TOWN | 8000 | South
Africa
Tel: +27 (0)21 481-8649 | Fax: +27 (0)21 481-8799 | Cell: +27 (0)82 403-2024
e-Mail: chilufya.lombe@xxxxxxxxxxxxxx
www.wspgroup.co.za
_______________________________________________________________________________________
This email and all contents
are subject to the following disclaimer.
http://www1.wspgroup.co.za/disclaimer.htm
P Help save paper - do you really need to
print this email?
__._,_.___
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|