|
Mario, yes, i have seen that algorithm. it is based on ISO 15099, and it applies to a narrow, sealed non ventilated cavity. My model has natural ventilation and has a considerable gap in between panes. My objective is to see how E+ behaves using a especific algorithm formulated for double skin facades with natural ventilation. Pedro. To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: mneves32@xxxxxxxxx Date: Tue, 6 Jul 2010 10:58:20 +0000 Subject: [EnergyPlus_Support] Re: Surface Convection Algorithms
Pedro,
Have you sean the TombWall coeficients? --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Pedro Peixeiro <pedro_peixeiro@...> wrote: > > > Mario, > > It wouldnt. I'm doing a research work on natural ventilated double skin facades, and the inside convective coefficients depends on a handfull of paramenters that need to be calculated for each time step. I must apply a not so simple algorithm, rather than using constant values, or even any of the available algorithms in E+. > > Pedro > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > From: mneves32@... > Date: Tue, 6 Jul 2010 09:08:25 +0000 > Subject: [EnergyPlus_Support] Re: Surface Convection Algorithms > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Hello Pedro, > > > > How about using this object: > > > > IDF,SurfaceProperty:ConvectionCoefficients:MultipleSurface,AllExteriorWalls,Outside,Value,25*,,Inside,Simple,7.69*,; > > > > Won´t it get the job done? > > > > *- values acording to the ITE-50 [W/m2.K] > > > > MN > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Pedro Peixeiro <pedro_peixeiro@> wrote: > > > > > > > > > Mario, > > > > > > I have. But the issue here is that i want to apply different coefficients, other than the ones available in E+. As far as i know, DB will not provide me such thing. I've read through the EMS, and it specifically says that it is possible to define and apply custom made algorithms for the convective coefficients, wich is exactly what i need. > > > > > > Pedro. > > > > > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > > > From: mneves32@ > > > Date: Mon, 5 Jul 2010 22:24:54 +0000 > > > Subject: [EnergyPlus_Support] Re: Surface Convection Algorithms > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Hello Pedro, > > > > > > > > > > > > Have you sean how Designbuilder coupes with this problem? > > > > > > If you export the IDF you will see that each surface hase it´s own "pair" of superficial coeficients. > > > > > > > > > > > > MN > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Pedro Peixeiro <pedro_peixeiro@> wrote: > > > > > > > > > > > > > > > > > > > > > I would have to say that is good news. Could I get any hint on where to start looking for information on what exactly is this EMS feature, what aditional tools (if any) i need to have and how to start learning how to use it? I'm rather in the blank about this, could use some guidance on where to look, thank you for your help!! > > > > > > > > > > > > > > Pedro > > > > > > > > > > > > > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > > > > > > > From: brent.griffith@ > > > > > > > Date: Fri, 2 Jul 2010 14:10:20 -0600 > > > > > > > Subject: RE: [EnergyPlus_Support] Re: Surface Convection Algorithms > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Work is underway to overhaul the > > > > > > > convection coefficient algorithms and there will be many more options available > > > > > > > in the next version. > > > > > > > > > > > > > > > > > > > > > > > > > > > > Currently, the EMS > > > > > > > feature includes actuators for surface convection coefficients. It is a bit of > > > > > > > an advanced feature, and could get pretty cumbersome for large models, but it is > > > > > > > possible to implement any algorithm you want using EnergyPlus Runtime Language. > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > From: > > > > > > > EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Pedro Peixeiro > > > > > > > > > > > > > > Sent: Friday, July 02, 2010 10:05 > > > > > > > AM > > > > > > > > > > > > > > To: > > > > > > > energyplus_support@xxxxxxxxxxxxxxx > > > > > > > > > > > > > > Subject: RE: [EnergyPlus_Support] > > > > > > > Re: Surface Convection Algorithms > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > yes. for the SurfaceConvectionAlgorithm:Inside > > > > > > > and SurfaceConvectionAlgorithm:Outside objects. > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > To: EnergyPlus_Support@xxxxxxxxxxxxxxx > > > > > > > > > > > > > > From: mneves32@ > > > > > > > > > > > > > > Date: Fri, 2 Jul 2010 15:54:36 +0000 > > > > > > > > > > > > > > Subject: [EnergyPlus_Support] Re: Surface Convection Algorithms > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > sUPERFICIAIS? > > > > > > > > > > > > > > > > > > > > > > > > > > > > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, > > > > > > > "pedro_peixeiro" <pedro_peixeiro@> wrote: > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Hello everyone. > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Is there any way to include in a simulation other algorithms for the > > > > > > > convective heat transfer coeffients? thanks. > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > Pedro > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > The New Busy is not the too busy. Combine all your e-mail accounts with > > > > > > > Hotmail. Get busy. > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > __________________________________________________________ > > > > > > > The New Busy is not the too busy. Combine all your e-mail accounts with Hotmail. > > > > > > > http://www.windowslive.com/campaign/thenewbusy?tile=multiaccount&ocid=PID28326::T:WLMTAGL:ON:WL:en-US:WM_HMP:042010_4 > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > > __________________________________________________________ > > > Hotmail is redefining busy with tools for the New Busy. Get more from your inbox. > > > http://www.windowslive.com/campaign/thenewbusy?ocid=PID28326::T:WLMTAGL:ON:WL:en-US:WM_HMP:042010_2 > > > > > > > > > > > > > > > > > > > > > > __________________________________________________________ > The New Busy is not the too busy. Combine all your e-mail accounts with Hotmail. > http://www.windowslive.com/campaign/thenewbusy?tile=multiaccount&ocid=PID28326::T:WLMTAGL:ON:WL:en-US:WM_HMP:042010_4 > Hotmail is redefining busy with tools for the New Busy. Get more from your inbox. See how. __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |