Dear Vinay, While .6 fan efficiency is within normal range, the goal is to
define a combination of fan efficiency and pressure rise which results in the
acceptable fan power. You start with known air flow, make a reasonable estimate
of fan efficiency and then derive the pressure rise. For a “Proposed” system, the derivation is not
needed; you use the actual fan and motor efficiencies, actual airflow and
actual pressure rise. For your information (just in case it’s helpful), the
derivation of fan power is shown below in IP units. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Vinay
Devanathan Mr. Dirkes, Thanks for your reply. So, is 0.6
Fan Efficiency (including motor efficiency) acceptable? or does it depend on
any other variable? I am assuming there are no set specifics for Fan Efficiency
value. So, with this procedure, we can calculate Fan Power from Appendix G
formula and adjust Pressure difference. Am I right on this?
Regards, Vinay On Wed, Jul 7, 2010 at 9:25 PM,
James V Dirkes II, PE <jvd2pe@xxxxxxx>
wrote: Dear
Vinay, ASHRAE
90.1-2007 specifies Baseline system fan power in Table G3.1.2.9. For VAV
systems, also use Table G3.1.3.15 for part load performance. A sample
object for the VAV fan is shown below. For
all baseline fans, I made a spreadsheet which, based on anticipated motor and
fan efficiency, calculates the pressure rise which will result in the correct
ASHRAE 90.1 fan power. Remember that E+, when asking for “fan
efficiency”, really wants (Fan mechanical efficiency x Motor efficiency).
For example, if the fan mechanical efficiency = .60 and motor efficiency
= .90, the E+ “fan efficiency” = .54.
The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Vinay Devanathan Subject:
Re: [EnergyPlus_Support] ASHRAE Compliant Fans and Pumps Alan, On Tue, Jun 29, 2010 at 11:33 AM, Jackson,
Alan <ajackson@xxxxxxxxxxxxxxxxx>
wrote: You're going to want to adjust
your Static Pressure DeltaP. Once you
------------------------------------
Yahoo! Groups Links __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |