Re: [EnergyPlus_Support] CollingCoil:DX inputs



Enter the flow rate that was used for the Rated Cooling Capacity. For 
example, for a 10-ton air conditioner (the Rated Cooling Capacity), the 
air flow rate would be around 4000 cfm (400 cfm/ton).

Vinay Devanathan wrote:
>
> Hello All,
>
> While I auto-size a run period and obtain values from that simulation 
> and plug it into the simulation next time, I come across a situation 
> which I would like to clarify.
> I auto-size and obtain the values of Rated Cooling Capacity. And the 
> problem I am facing is in inputting the Rated Air Flow Rate. What 
> value should go in this field? Is it the max. air flow rate or the air 
> flow rate that satisfies the cooling load? When I use the air flow 
> rate that satisfies cooling load, I see that the Rate Vol Flow rate 
> (m3/s) per Watt of the Rated Cooling Capacity is less than the minimum 
> specified in the I/O reference (0.000040).
>
> Any help would be great.
>
> Thank you.
>
> Regards,
> Vinay
>
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/