Dear Vinay, Standard 90.1 says you must model a heating and cooling system,
but does not say that it must be operating continuously. Obviously, most
cooling systems are OFF during cold weather; this is normal and expected.
I suspect that cooling IS available via an economizer control. If, for some reason, you actually need to operate your DX system
in the middle of the winter as sometimes is the case, I’m not sure what
to do. I think, though, that you can adjust the coil curves to reflect the
actual equipment’s operation without causing a problem in E+. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Vinay
Devanathan Mr. Dirkes, On Thu, Jul 8, 2010 at 8:45 PM,
James V Dirkes II, PE <jvd2pe@xxxxxxx>
wrote: Dear
Vinay, · A simple way to fix this is to assign an
availability schedule to the cooling coil which is ON only during warmer
months. For the coil below, I’ve used an “AlwaysOn” schedule,
but you can create any schedule that you like, perhaps similar to the one I
show at the bottom. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Vinay Devanathan Hello All, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.