Hi, Linda
Thank you for your reply!
Maybe the example I posted is not clear!
What I want to do is to simulate the sensor fault, just like bias or others. It means if the real room temp is 26[C], the controller get the singal from the sensor is "26+1=27"[C], assumed the bias is +1[C].
Using EMS, I think, there should be an EMS:Sensor Troom, and in the EMS:Program, there should be an sentence "set Troom = Troom +1".
Is that right?
Or there is another way?
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> wrote:
>
> With the update release (V5.0.0.035) we added the weather variables
> as EMS sensors. However we did not add documentation with the update.
>
> (All internals to EnergyPlus are handled in SI units -- so your
> example of Fahrenheit temperature -- not sure what you are saying).
>
> Outdoor Dry Bulb [C]
> Outdoor Dew Point [C]
> Outdoor Relative Humidity [%]
> Diffuse Solar [W/m2]
> Direct Solar [W/m2]
> Wind Speed [m/s]
> Wind Direction [deg]
>
> were added.
>
> At 06:04 AM 7/14/2010, Hu wrote:
> >Hi, all.
> >Can I reassign EMS:Sensor value?
> >That means, if there is a EMS:Sensor T1, does "set T1 = T1 + 1" work
> >in the EMS:Pragram?
> >For example, the outdoor air temp is in the degrees Fahrenheit, and
> >I want to reset it in the Celsius.
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/