[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Re: how to reassign EMS:Sensor value



Hi, Linda
Thank you for your reply!
Maybe the example I posted is not clear!
What I want to do is to simulate the sensor fault, just like bias or others. It means if the real room temp is 26[C], the controller get the singal from the sensor is "26+1=27"[C], assumed the bias is +1[C].
Using EMS, I think, there should be an EMS:Sensor Troom, and in the EMS:Program, there should be an sentence "set Troom = Troom +1".
Is that right?
Or there is another way?

--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Linda Lawrie <linda@...> wrote:
>
> With the update release (V5.0.0.035) we added the weather variables 
> as EMS sensors.  However we did not add documentation with the update.
> 
> (All internals to EnergyPlus are handled in SI units -- so your 
> example of Fahrenheit temperature -- not sure what you are saying).
> 
> Outdoor Dry Bulb [C]
> Outdoor Dew Point [C]
> Outdoor Relative Humidity [%]
> Diffuse Solar [W/m2]
> Direct Solar [W/m2]
> Wind Speed [m/s]
> Wind Direction [deg]
> 
> were added.
> 
> At 06:04 AM 7/14/2010, Hu wrote:
> >Hi, all.
> >Can I reassign EMS:Sensor value?
> >That means, if there is a EMS:Sensor T1, does "set T1 = T1 + 1" work 
> >in the EMS:Pragram?
> >For example, the outdoor air temp is in the degrees Fahrenheit, and 
> >I want to reset it in the Celsius.
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/