When you tell the program that the interior wall is an adiabatic wall, then it uses the properties (storage included) in the calculation for the zone the wall is in, but assumes that the zone adjacent to that zone is of the same conditions/temperature so does not calculate the heat transfer through the wall to affect the adjacent zone.

At 11:00 PM 7/16/2010, sara wrote:
When I assume that an interior wall is an adiabatic wall, is the storage in the wall included in the process of calculation?