[EnergyPlus_Support] Simulation of an adiabatic room with cooling ceiling



Hi,

I've started  working on an project where I want to have an adiabatic room with a cooling ceiling (LowTempRadiant:Variableflow). Cooling load is created by lights (100% convective). 
When I set the thermal absorptance in material to 0,9 (which is needed) the simulation takes 15 minutes and I get about 30,000 warnings concerning convergence problems (and I have to restart EP-Launch). When I set to 0,1 e+ has finished in a minute and I get no warnings. 
What's this about?

The file is attached. Please, can anyone tell me whether I made a mistake in the construction of the room or the setup of the Loop?

Thanks!

!-Generator IDFEditor 1.37c
!-Option SortedOrder UseSpecialFormat

!-NOTE: All comments with '!-' are ignored by the IDFEditor and are generated automatically.
!-      Use '!' comments if they need to be retained when using the IDFEditor.


!-   ===========  ALL OBJECTS IN CLASS: VERSION ===========

Version,5.0;

!-   ===========  ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========


SimulationControl,
    No,                      !- Do Zone Sizing Calculation
    No,                      !- Do System Sizing Calculation
    No,                      !- Do Plant Sizing Calculation
    No,                      !- Run Simulation for Sizing Periods
    Yes;                     !- Run Simulation for Weather File Run Periods


!-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========

Building,
    Klimaversuchsraum,       !- Name
    0,                       !- North Axis {deg}
    City,                    !- Terrain
    0.5,                     !- Loads Convergence Tolerance Value
    0.4,                     !- Temperature Convergence Tolerance Value {deltaC}
    FullExterior,            !- Solar Distribution
    25;                      !- Maximum Number of Warmup Days


!-   ===========  ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:INSIDE ===========

SurfaceConvectionAlgorithm:Inside,Detailed;

!-   ===========  ALL OBJECTS IN CLASS: SURFACECONVECTIONALGORITHM:OUTSIDE ===========

SurfaceConvectionAlgorithm:Outside,Detailed;

!-   ===========  ALL OBJECTS IN CLASS: HEATBALANCEALGORITHM ===========

HeatBalanceAlgorithm,ConductionFiniteDifference,300;

!-   ===========  ALL OBJECTS IN CLASS: TIMESTEP ===========

Timestep,60;

!-   ===========  ALL OBJECTS IN CLASS: RUNPERIOD ===========


RunPeriod,
    ,                        !- Name
    1,                       !- Begin Month
    1,                       !- Begin Day of Month
    1,                       !- End Month
    31,                      !- End Day of Month
    UseWeatherFile,          !- Day of Week for Start Day
    Yes,                     !- Use Weather File Holidays and Special Days
    No,                      !- Use Weather File Daylight Saving Period
    No,                      !- Apply Weekend Holiday Rule
    No,                      !- Use Weather File Rain Indicators
    No,                      !- Use Weather File Snow Indicators
    1;                       !- Number of Times Runperiod to be Repeated


!-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========

ScheduleTypeLimits,
    Teilweise,               !- Name
    0,                       !- Lower Limit Value
    1,                       !- Upper Limit Value
    Continuous;              !- Numeric Type

ScheduleTypeLimits,
    An/Aus,                  !- Name
    0,                       !- Lower Limit Value
    1,                       !- Upper Limit Value
    Discrete;                !- Numeric Type

ScheduleTypeLimits,
    Temperatur,              !- Name
    -60,                     !- Lower Limit Value
    200,                     !- Upper Limit Value
    Continuous;              !- Numeric Type

ScheduleTypeLimits,
    Thermostat,              !- Name
    0,                       !- Lower Limit Value
    4,                       !- Upper Limit Value
    Discrete;                !- Numeric Type


!-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========

Schedule:Compact,
    Zonenregelungsplan,      !- Name
    Thermostat,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: Alldays,            !- Field 2
    Until: 24:00, 2;         !- Field 4

Schedule:Compact,
    Kühldecke Setpoint,      !- Name
    Temperatur,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: Alldays,            !- Field 2
    Until: 24:00, 16;        !- Field 4

Schedule:Compact,
    Belastungsplan,          !- Name
    An/Aus,                  !- Schedule Type Limits Name
    Through: 1/1,            !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 0,         !- Field 4
    Through: 1/2,            !- Field 5
    For: AllDays,            !- Field 6
    Until 24:00,             !- Field 7
     1,                      !- Field 8
    Through: 1/10,           !- Field 9
    For: AllDays,            !- Field 10
    Until: 24:00, 0,         !- Field 12
    Through: 1/31,           !- Field 13
    For: AllDays,            !- Field 14
    Until: 24:00, 1,         !- Field 16
    Through: 12/31,          !- Field 17
    For: AllDays,            !- Field 18
    Until: 24:00, 0;         !- Field 20

Schedule:Compact,
    Raumtemperatur Setpoint, !- Name
    Temperatur,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: Alldays,            !- Field 2
    Until: 24:00, 16;        !- Field 4

Schedule:Compact,
    Kühlung,                 !- Name
    Temperatur,              !- Schedule Type Limits Name
    Through: 12/31,          !- Field 1
    For: Alldays,            !- Field 2
    Until: 24:00, 17;        !- Field 4

Schedule:Compact,
    Kühlkreislauf,           !- Name
    An/Aus,                  !- Schedule Type Limits Name
    Through: 1/1,            !- Field 1
    For: AllDays,            !- Field 2
    Until: 24:00, 1,         !- Field 4
    Through: 1/2,            !- Field 5
    For: AllDays,            !- Field 6
    Until 24:00,             !- Field 7
     1,                      !- Field 8
    Through: 1/10,           !- Field 9
    For: AllDays,            !- Field 10
    Until: 24:00, 1,         !- Field 12
    Through: 1/31,           !- Field 13
    For: AllDays,            !- Field 14
    Until: 24:00, 0,         !- Field 16
    Through: 12/31,          !- Field 17
    For:AllDays,             !- Field 18
    Until: 24:00, 0;         !- Field 20


!-   ===========  ALL OBJECTS IN CLASS: MATERIAL ===========

Material,
    Außenwandmaterial,       !- Name
    MediumRough,             !- Roughness
    0.3,                     !- Thickness {m}
    0.047,                   !- Conductivity {W/m-K}
    75,                      !- Density {kg/m3}
    840,                     !- Specific Heat {J/kg-K}
    0.9;                     !- Thermal Absorptance

Material,
    Stahlbleche,             !- Name
    VerySmooth,              !- Roughness
    0.001,                   !- Thickness {m}
    40,                      !- Conductivity {W/m-K}
    7850,                    !- Density {kg/m3}
    470,                     !- Specific Heat {J/kg-K}
    0.9;                     !- Thermal Absorptance

Material,
    PCM SGL,                 !- Name
    MediumSmooth,            !- Roughness
    0.1,                     !- Thickness {m}
    1.12,                    !- Conductivity {W/m-K}
    1060,                    !- Density {kg/m3}
    2500,                    !- Specific Heat {J/kg-K}
    0.0001;                  !- Thermal Absorptance

Material,
    Graphitpressling,        !- Name
    MediumSmooth,            !- Roughness
    0.01,                    !- Thickness {m}
    5,                       !- Conductivity {W/m-K}
    2250,                    !- Density {kg/m3}
    709,                     !- Specific Heat {J/kg-K}
    0.9;                     !- Thermal Absorptance


!-   ===========  ALL OBJECTS IN CLASS: MATERIALPROPERTY:PHASECHANGE ===========

MaterialProperty:PhaseChange,
    PCM SGL,                 !- Name
    0,                       !- Temperature Coefficient for Thermal Conductivity {W/m-K2}
    15,                      !- Temperature 1 {C}
    0,                       !- Enthalpy 1 {J/kg}
    18,                      !- Temperature 2 {C}
    171000,                  !- Enthalpy 2 {J/kg}
    20,                      !- Temperature 3 {C}
    3000;                    !- Enthalpy 3 {J/kg}


!-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========

Construction,
    Außenwand,               !- Name
    Außenwandmaterial;       !- Outside Layer


!-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION:INTERNALSOURCE ===========

Construction:InternalSource,
    Kühldeckensystem,        !- Name
    1,                       !- Source Present After Layer Number
    1,                       !- Temperature Calculation Requested After Layer Number
    2,                       !- Dimensions for the CTF Calculation
    0.05,                    !- Tube Spacing {m}
    Graphitpressling,        !- Outside Layer
    Stahlbleche;             !- Layer 2


!-   ===========  ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========

GlobalGeometryRules,
    ULC,                     !- Starting Vertex Position
    Clockwise,               !- Vertex Entry Direction
    Relative;                !- Coordinate System


!-   ===========  ALL OBJECTS IN CLASS: ZONE ===========

Zone,
    ZN,                      !- Name
    0,                       !- Direction of Relative North {deg}
    0, 0, 0,                            !- X,Y,Z  {m}
    1,                       !- Type
    1,                       !- Multiplier
    2.6,                     !- Ceiling Height {m}
    Autocalculate,           !- Volume {m3}
    Detailed,                !- Zone Inside Convection Algorithm
    Detailed;                !- Zone Outside Convection Algorithm


!-   ===========  ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED ===========

BuildingSurface:Detailed,
    AW W,                    !- Name
    Wall,                    !- Surface Type
    Außenwand,               !- Construction Name
    ZN,                      !- Zone Name
    Surface,                 !- Outside Boundary Condition
    AW W,                    !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Vertices
    0, 0, 3,                            !- X,Y,Z  1 {m}
    0, 0, 0,                            !- X,Y,Z  2 {m}
    0, 4, 0,                            !- X,Y,Z  3 {m}
    0, 4, 3;                            !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    AW S,                    !- Name
    Wall,                    !- Surface Type
    Außenwand,               !- Construction Name
    ZN,                      !- Zone Name
    Surface,                 !- Outside Boundary Condition
    AW S,                    !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Vertices
    4, 0, 3,                            !- X,Y,Z  1 {m}
    4, 0, 0,                            !- X,Y,Z  2 {m}
    0, 0, 0,                            !- X,Y,Z  3 {m}
    0, 0, 3;                            !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    AW O,                    !- Name
    Wall,                    !- Surface Type
    Außenwand,               !- Construction Name
    ZN,                      !- Zone Name
    Surface,                 !- Outside Boundary Condition
    AW O,                    !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Vertices
    4, 4, 3,                            !- X,Y,Z  1 {m}
    4, 4, 0,                            !- X,Y,Z  2 {m}
    4, 0, 0,                            !- X,Y,Z  3 {m}
    4, 0, 3;                            !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    AW N,                    !- Name
    Wall,                    !- Surface Type
    Außenwand,               !- Construction Name
    ZN,                      !- Zone Name
    Surface,                 !- Outside Boundary Condition
    AW N,                    !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    0,                       !- View Factor to Ground
    4,                       !- Number of Vertices
    0, 4, 3,                            !- X,Y,Z  1 {m}
    0, 4, 0,                            !- X,Y,Z  2 {m}
    4, 4, 0,                            !- X,Y,Z  3 {m}
    4, 4, 3;                            !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    FBoden,                  !- Name
    Floor,                   !- Surface Type
    Außenwand,               !- Construction Name
    ZN,                      !- Zone Name
    Surface,                 !- Outside Boundary Condition
    FBoden,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    autocalculate,           !- View Factor to Ground
    4,                       !- Number of Vertices
    0, 4, 0,                            !- X,Y,Z  1 {m}
    0, 0, 0,                            !- X,Y,Z  2 {m}
    4, 0, 0,                            !- X,Y,Z  3 {m}
    4, 4, 0;                            !- X,Y,Z  4 {m}

BuildingSurface:Detailed,
    DDecke,                  !- Name
    Ceiling,                 !- Surface Type
    Außenwand,               !- Construction Name
    ZN,                      !- Zone Name
    Surface,                 !- Outside Boundary Condition
    DDecke,                  !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    1,                       !- View Factor to Ground
    4,                       !- Number of Vertices
    0, 4, 3,                            !- X,Y,Z  1 {m}
    4, 4, 3,                            !- X,Y,Z  2 {m}
    4, 0, 3,                            !- X,Y,Z  3 {m}
    0, 0, 3;                            !- X,Y,Z  4 {m}


!-   ===========  ALL OBJECTS IN CLASS: ROOFCEILING:DETAILED ===========

RoofCeiling:Detailed,
    Platte 1,                !- Name
    Kühldeckensystem,        !- Construction Name
    ZN,                      !- Zone Name
    Surface,                 !- Outside Boundary Condition
    ,                        !- Outside Boundary Condition Object
    NoSun,                   !- Sun Exposure
    NoWind,                  !- Wind Exposure
    1,                       !- View Factor to Ground
    4,                       !- Number of Vertices
    0, 4, 2.6,                          !- X,Y,Z  1 {m}
    4, 4, 2.6,                          !- X,Y,Z  2 {m}
    4, 0, 2.6,                          !- X,Y,Z  3 {m}
    0, 0, 2.6;                          !- X,Y,Z  4 {m}


!-   ===========  ALL OBJECTS IN CLASS: LIGHTS ===========

Lights,
    Dummies,                 !- Name
    ZN,                      !- Zone Name
    Belastungsplan,          !- Schedule Name
    LightingLevel,           !- Design Level Calculation Method
    780,                     !- Lighting Level {W}
    ,                        !- Watts per Zone Floor Area {W/m2}
    ,                        !- Watts per Person {W/person}
    0,                       !- Return Air Fraction
    0,                       !- Fraction Radiant
    0,                       !- Fraction Visible
    0,                       !- Fraction Replaceable
    General,                 !- End-Use Subcategory
    No;                      !- Return Air Fraction Calculated from Plenum Temperature


!-   ===========  ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT ===========

ZoneControl:Thermostat,
    Thermostat,              !- Name
    ZN,                      !- Zone Name
    Zonenregelungsplan,      !- Control Type Schedule Name
    ThermostatSetpoint:SingleCooling,  !- Control 1 Object Type
    Thermostat Kühlung;      !- Control 1 Name


!-   ===========  ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:SINGLECOOLING ===========

ThermostatSetpoint:SingleCooling,
    Thermostat Kühlung,      !- Name
    Kühlung;                 !- Setpoint Temperature Schedule Name


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:LOWTEMPERATURERADIANT:VARIABLEFLOW ===========

ZoneHVAC:LowTemperatureRadiant:VariableFlow,
    Kühlregister,            !- Name
    Kühlkreislauf,           !- Availability Schedule Name
    ZN,                      !- Zone Name
    Platte 1,                !- Surface Name or Radiant Surface Group Name
    0.006,                   !- Hydronic Tubing Inside Diameter {m}
    340,                     !- Hydronic Tubing Length {m}
    MeanAirTemperature,      !- Temperature Control Type
    ,                        !- Maximum Hot Water Flow {m3/s}
    ,                        !- Heating Water Inlet Node Name
    ,                        !- Heating Water Outlet Node Name
    ,                        !- Heating Control Throttling Range {deltaC}
    ,                        !- Heating Control Temperature Schedule Name
    0.00015,                 !- Maximum Cold Water Flow {m3/s}
    Kühlregister Inlet,      !- Cooling Water Inlet Node Name
    Kühlregister Outlet,     !- Cooling Water Outlet Node Name
    2,                       !- Cooling Control Throttling Range {deltaC}
    Raumtemperatur Setpoint; !- Cooling Control Temperature Schedule Name


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========

ZoneHVAC:EquipmentList,
    Equipment Liste,         !- Name
    ZoneHVAC:LowTemperatureRadiant:VariableFlow,  !- Zone Equipment 1 Object Type
    Kühlregister,            !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS ===========

ZoneHVAC:EquipmentConnections,
    ZN,                      !- Zone Name
    Equipment Liste,         !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Raumluft,                !- Zone Air Node Name
    Banane;                  !- Zone Return Air Node Name


!-   ===========  ALL OBJECTS IN CLASS: BRANCH ===========

Branch,
    Plant Demand Inlet Branch,  !- Name
    ,                        !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pipe:Adiabatic,          !- Component 1 Object Type
    Plant Demand Inlet Pipe, !- Component 1 Name
    Plant Demand Inlet,      !- Component 1 Inlet Node Name
    Plant Demand Inlet Outlet,  !- Component 1 Outlet Node Name
    Passive;                 !- Component 1 Branch Control Type

Branch,
    Kühlregister Branch,     !- Name
    ,                        !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    ZoneHVAC:LowTemperatureRadiant:VariableFlow,  !- Component 1 Object Type
    Kühlregister,            !- Component 1 Name
    Kühlregister Inlet,      !- Component 1 Inlet Node Name
    Kühlregister Outlet,     !- Component 1 Outlet Node Name
    Active;                  !- Component 1 Branch Control Type

Branch,
    Kühldecke Bypass Branch, !- Name
    ,                        !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pipe:Adiabatic,          !- Component 1 Object Type
    Kühldecke Bypass,        !- Component 1 Name
    Kühldecke Bypass Inlet,  !- Component 1 Inlet Node Name
    Kühldecke Bypass Outlet, !- Component 1 Outlet Node Name
    Bypass;                  !- Component 1 Branch Control Type

Branch,
    Plant Supply Outlet Branch,  !- Name
    ,                        !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pipe:Adiabatic,          !- Component 1 Object Type
    Plant Supply Outlet Pipe,!- Component 1 Name
    Plant Supply Outlet Inlet,  !- Component 1 Inlet Node Name
    Plant Supply Outlet,     !- Component 1 Outlet Node Name
    Passive;                 !- Component 1 Branch Control Type

Branch,
    Plant Demand Outlet Branch,  !- Name
    ,                        !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pipe:Adiabatic,          !- Component 1 Object Type
    Plant Demand Outlet Pipe,!- Component 1 Name
    Plant Demand Outlet Inlet,  !- Component 1 Inlet Node Name
    Plant Demand Outlet,     !- Component 1 Outlet Node Name
    Passive;                 !- Component 1 Branch Control Type

Branch,
    Fernkühlung Branch,      !- Name
    ,                        !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    DistrictCooling,         !- Component 1 Object Type
    FK,                      !- Component 1 Name
    FK Inlet,                !- Component 1 Inlet Node Name
    FK Outlet,               !- Component 1 Outlet Node Name
    Active;                  !- Component 1 Branch Control Type

Branch,
    Pumpe Branch,            !- Name
    ,                        !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pump:VariableSpeed,      !- Component 1 Object Type
    Pumpe,                   !- Component 1 Name
    Pumpe Inlet,             !- Component 1 Inlet Node Name
    Pumpe Outlet,            !- Component 1 Outlet Node Name
    Passive;                 !- Component 1 Branch Control Type

Branch,
    FK Bypass Branch,        !- Name
    ,                        !- Maximum Flow Rate {m3/s}
    ,                        !- Pressure Drop Curve Name
    Pipe:Adiabatic,          !- Component 1 Object Type
    FK Bypass,               !- Component 1 Name
    FK Bypass Inlet,         !- Component 1 Inlet Node Name
    FK Bypass Outlet,        !- Component 1 Outlet Node Name
    Bypass;                  !- Component 1 Branch Control Type


!-   ===========  ALL OBJECTS IN CLASS: BRANCHLIST ===========

BranchList,
    Plant Demand Branch Liste,  !- Name
    Plant Demand Inlet Branch,  !- Branch 1 Name
    Kühlregister Branch,     !- Branch 2 Name
    Kühldecke Bypass Branch, !- Branch 3 Name
    Plant Demand Outlet Branch;  !- Branch 4 Name

BranchList,
    Plant Supply Branch Liste,  !- Name
    Pumpe Branch,            !- Branch 1 Name
    Fernkühlung Branch,      !- Branch 2 Name
    FK Bypass Branch,        !- Branch 3 Name
    Plant Supply Outlet Branch;  !- Branch 4 Name


!-   ===========  ALL OBJECTS IN CLASS: CONNECTOR:SPLITTER ===========

Connector:Splitter,
    Plant Demand Splitter,   !- Name
    Plant Demand Inlet Branch,  !- Inlet Branch Name
    Kühlregister Branch,     !- Outlet Branch 1 Name
    Kühldecke Bypass Branch; !- Outlet Branch 2 Name

Connector:Splitter,
    Plant Supply Splitter,   !- Name
    Pumpe Branch,            !- Inlet Branch Name
    Fernkühlung Branch,      !- Outlet Branch 1 Name
    FK Bypass Branch;        !- Outlet Branch 2 Name


!-   ===========  ALL OBJECTS IN CLASS: CONNECTOR:MIXER ===========

Connector:Mixer,
    Plant Demand Mixer,      !- Name
    Plant Demand Outlet Branch,  !- Outlet Branch Name
    Kühlregister Branch,     !- Inlet Branch 1 Name
    Kühldecke Bypass Branch; !- Inlet Branch 2 Name

Connector:Mixer,
    Plant Supply Mixer,      !- Name
    Plant Supply Outlet Branch,  !- Outlet Branch Name
    Fernkühlung Branch,      !- Inlet Branch 1 Name
    FK Bypass Branch;        !- Inlet Branch 2 Name


!-   ===========  ALL OBJECTS IN CLASS: CONNECTORLIST ===========

ConnectorList,
    Connector Demand Liste,  !- Name
    Connector:Splitter,      !- Connector 1 Object Type
    Plant Demand Splitter,   !- Connector 1 Name
    Connector:Mixer,         !- Connector 2 Object Type
    Plant Demand Mixer;      !- Connector 2 Name

ConnectorList,
    Connector Supply Liste,  !- Name
    Connector:Splitter,      !- Connector 1 Object Type
    Plant Supply Splitter,   !- Connector 1 Name
    Connector:Mixer,         !- Connector 2 Object Type
    Plant Supply Mixer;      !- Connector 2 Name


!-   ===========  ALL OBJECTS IN CLASS: OUTDOORAIR:NODE ===========

OutdoorAir:Node,
    Aussenluft,              !- Name
    -1;                      !- Height Above Ground {m}


!-   ===========  ALL OBJECTS IN CLASS: PIPE:ADIABATIC ===========

Pipe:Adiabatic,
    Plant Demand Inlet Pipe, !- Name
    Plant Demand Inlet,      !- Inlet Node Name
    Plant Demand Inlet Outlet;  !- Outlet Node Name

Pipe:Adiabatic,
    Kühldecke Bypass,        !- Name
    Kühldecke Bypass Inlet,  !- Inlet Node Name
    Kühldecke Bypass Outlet; !- Outlet Node Name

Pipe:Adiabatic,
    Plant Demand Outlet Pipe,!- Name
    Plant Demand Outlet Inlet,  !- Inlet Node Name
    Plant Demand Outlet;     !- Outlet Node Name

Pipe:Adiabatic,
    Plant Supply Outlet Pipe,!- Name
    Plant Supply Outlet Inlet,  !- Inlet Node Name
    Plant Supply Outlet;     !- Outlet Node Name

Pipe:Adiabatic,
    FK Bypass,               !- Name
    FK Bypass Inlet,         !- Inlet Node Name
    FK Bypass Outlet;        !- Outlet Node Name


!-   ===========  ALL OBJECTS IN CLASS: PUMP:VARIABLESPEED ===========

Pump:VariableSpeed,
    Pumpe,                   !- Name
    Pumpe Inlet,             !- Inlet Node Name
    Pumpe Outlet,            !- Outlet Node Name
    0.00015,                 !- Rated Flow Rate {m3/s}
    179352,                  !- Rated Pump Head {Pa}
    50,                      !- Rated Power Consumption {W}
    0.9,                     !- Motor Efficiency
    0,                       !- Fraction of Motor Inefficiencies to Fluid Stream
    ,                        !- Coefficient 1 of the Part Load Performance Curve
    1,                       !- Coefficient 2 of the Part Load Performance Curve
    ,                        !- Coefficient 3 of the Part Load Performance Curve
    ,                        !- Coefficient 4 of the Part Load Performance Curve
    ,                        !- Minimum Flow Rate {m3/s}
    Continuous;              !- Pump Control Type


!-   ===========  ALL OBJECTS IN CLASS: DISTRICTCOOLING ===========

DistrictCooling,
    FK,                      !- Name
    FK Inlet,                !- Chilled Water Inlet Node Name
    FK Outlet,               !- Chilled Water Outlet Node Name
    1400;                    !- Nominal Capacity {W}


!-   ===========  ALL OBJECTS IN CLASS: PLANTLOOP ===========

PlantLoop,
    KW Loop,                 !- Name
    Water,                   !- Fluid Type
    KW Loop OPS,             !- Plant Equipment Operation Scheme Name
    Plant Supply Outlet,     !- Loop Temperature Setpoint Node Name
    98,                      !- Maximum Loop Temperature {C}
    4,                       !- Minimum Loop Temperature {C}
    0.00015,                 !- Maximum Loop Flow Rate {m3/s}
    0,                       !- Minimum Loop Flow Rate {m3/s}
    autocalculate,           !- Plant Loop Volume {m3}
    Pumpe Inlet,             !- Plant Side Inlet Node Name
    Plant Supply Outlet,     !- Plant Side Outlet Node Name
    Plant Supply Branch Liste,  !- Plant Side Branch List Name
    Connector Supply Liste,  !- Plant Side Connector List Name
    Plant Demand Inlet,      !- Demand Side Inlet Node Name
    Plant Demand Outlet,     !- Demand Side Outlet Node Name
    Plant Demand Branch Liste,  !- Demand Side Branch List Name
    Connector Demand Liste,  !- Demand Side Connector List Name
    Optimal;                 !- Load Distribution Scheme


!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTLIST ===========

PlantEquipmentList,
    FK Liste,                !- Name
    DistrictCooling,         !- Equipment 1 Object Type
    FK;                      !- Equipment 1 Name


!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATION:UNCONTROLLED ===========

PlantEquipmentOperation:Uncontrolled,
    KW Loop Control,         !- Name
    FK Liste;                !- Equipment List Name


!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATION:COOLINGLOAD ===========

PlantEquipmentOperation:CoolingLoad,
    KW Loop Control,         !- Name
    0,                       !- Load Range 1 Lower Limit {W}
    7000,                    !- Load Range 1 Upper Limit {W}
    FK Liste;                !- Priority Control 1 Equipment List Name


!-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATIONSCHEMES ===========

PlantEquipmentOperationSchemes,
    KW Loop OPS,             !- Name
    PlantEquipmentOperation:Uncontrolled,  !- Control Scheme 1 Object Type
    KW Loop Control,         !- Control Scheme 1 Name
    Kühlkreislauf;           !- Control Scheme 1 Schedule Name


!-   ===========  ALL OBJECTS IN CLASS: SETPOINTMANAGER:SCHEDULED ===========

SetpointManager:Scheduled,
    KW Loop Setpoint Manager,!- Name
    Temperature,             !- Control Variable
    Kühldecke Setpoint,      !- Schedule Name
    Plant Supply Outlet;     !- Setpoint Node or NodeList Name


!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY ===========

Output:VariableDictionary,Regular;

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========

Output:Variable,*,Zone Mean Air Temperature,Detailed;
Output:Variable,*,Zone Total Internal Convective Heat Gain ,Hourly;
Output:Variable,*,Outdoor Dry Bulb,Hourly;
Output:Variable,*,System Node Temp,Hourly;
Output:Variable,*,Hydronic Low Temp Radiant Cooling Rate,Hourly;
Output:Variable,*,Plant Loop Cooling Demand ,Hourly;
Output:Variable,*,System Node MassFlowRate ,Hourly;
Output:Variable,*,Zone/Sys Thermostat Cooling Setpoint ,Hourly;
Output:Variable,*,Plant Loop Cooling Demand ,Hourly;
Output:Variable,*,Zone/Sys Thermostat Cooling Setpoint ,Hourly;
Output:Variable,*,Zone/Sys Sensible Load Predicted ,Hourly;
Output:Variable,*,Zone/Sys Sensible Load to Cooling Setpoint Predicted ,Hourly;
Output:Variable,*,District Cooling Outlet Temp ,Hourly;
Output:Variable,*,District Cooling Rate ,Hourly;
Output:Variable,*,Source Location Temperature ,Hourly;
Output:Variable,*,Zone Total Internal Total Heat Gain ,Hourly;
Output:Variable,*,CondFD Nodal Temperature ,Hourly;
Output:Variable,*,Zone/Sys Sensible Cooling Rate ,Hourly;
Output:Variable,*,Hydronic Low Temp Radiant Cooling Energy ,Hourly;
Output:Variable,*,Zone Air Balance Internal Convective Gains Rate ,Hourly;
Output:Variable,*,Zone Air Balance Surface Convection Rate ,Hourly;
Output:Variable,*,Zone Air Balance Air Energy Storage Rate ,Hourly;
Output:Variable,*,Zone Lights Total Heat Gain ,Hourly;
Output:Variable,*,Pump Heat To Fluid,Hourly;
Output:Variable,*,Time Cooling Setpoint Not Met,Hourly;
Output:Variable,*,CondFD Outside Surface Heat Flux,Hourly;
Output:Variable,*,CondFD Inside Surface Heat Flux,Hourly;

!-   ===========  ALL OBJECTS IN CLASS: OUTPUT:SQLITE ===========


Output:SQLite,
    SimpleAndTabular;        !- Option Type





------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/