Dear Marcel and Liam, If the home is of older construction or constructed by someone
not familiar with low infiltration construction practice … it would not
be unusual to have 1.0 -2.0 air changes per hour infiltration. I recall
some ASHRAE data from years back which confirmed this. On another note, infiltration does not occur at a constant
rate. It is affected by the pressure difference between outdoors and
indoors. Although I’ve used a constant average rate in the past
(similar to your approach, Marcel), it has only been for a rough evaluation. I have not studied the impact of different approaches with E+,
but I think the air change per hour approach with coefficients that allow
variation with wind speed is a good one. It allows selection of a “base”
rate, which is then modified according to wind speed. The coefficients
below were taken from the E+ I/O Reference manual and originally came from BLAST
(I think). Another advantage of this approach is that, for many climates,
the wind speed (and therefore infiltration) is lower in the summer months, higher
in winter months … which causes the infiltration to vary something like
reality. “Flow/Exterior Area” is theoretically perhaps
the best method, but past experience suggests that it’s almost impossible
to predict. Most of my past experience is with industrial buildings,
where average heating season infiltration rate varied between 0.1 and 0.5 air
changes per hour, so I tend to stay in that range. Finally, the fact that the room remains warmer than setpoint
probably has little to do with the infiltration. Rather, your cooling
system air flow rate or coil capacity is probably too low. I always report
outdoor air flow rate, mixed air temperature, coil leaving temperature, fan
leaving temperature and leaving temperature setpoint for each air handler to
see what is happening at each timestep. This lets me know whether each
component is performing properly. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Liam O'Brien Hi Marcel, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.