RE: [EnergyPlus_Support] How to debug/identify these errors






apart from that..i have a question..how to activate the quick panel dialog for each simulation that i do..in my case it only comes for the first simulation..after that doesnt...Plz help.


From: YuanLu Li <yli006@xxxxxxxxxxx>
Subject: RE: [EnergyPlus_Support] How to debug/identify these errors
To: "Linda" <energyplus_support@xxxxxxxxxxxxxxx>
Date: Thursday, 22 July, 2010, 5:03 AM

 
Hi, Rahul
 
This second tutorial file is quite different from the first one.  You are now using the HVAC templates which is not the same as your previous tutorial file.  There may be some more errors, not just one.  I have not tried your IDF yet.
 
Is there any reason why you need the 3m concrete walls?
 
Linda has already answered the part on the 3 meter thick concrete, in another group mail. 
============ ========= ===
I noticed that you are not using the correct schedule types, etc.  You are using annual simulation, instead of design day simulation.  This may generate repeated warnings, which you do not want to see.
 
My advice is to do the DesignDay simulation first.  When there is no error, then do the annual weather file run.


 Dr. Li  



 

To: EnergyPlus_Support@ yahoogroups. com
CC: yli006@hotmail. com
From: rahulopg@yahoo. co.in
Date: Thu, 22 Jul 2010 03:38:37 +0530
Subject: [EnergyPlus_ Support] How to debug/identify these errors

 

thnk you prof. Li for your kind help....well a tried a new simulation almost like the previous one with some changes and with my best efforts able to keep my errors=1 warnings=1,warning is OK to me but im not able to make out the error...

                                                        Your help will be obliged.I am attaching my IDF file and .err file for your needful.

                                                                                             Thnk you
                                                                                          RAHUL GUPTA
--- On Wed, 21/7/10, YuanLu Li <yli006@hotmail. com> wrote:

From: YuanLu Li <yli006@hotmail. com>
Subject: RE: [EnergyPlus_ Support] How to debug/identify these errors
To: "Linda" <energyplus_support@ yahoogroups. com>
Date: Wednesday, 21 July, 2010, 10:41 PM

 

Hi, Rahul
 
I usually only respond to questions with IDF posted, and posted with real name.
 
I had a look at your attachments.
 
The BMP file is the DOS screen.  If you right click your mouse on the screen, and select "select all" on the pop up, the file is saved in the windows clip-board, and you can "paste" it to a notepad or wordpad to see the whole file.
 
This file would show you where the simulation has stopped, but will not show you the IDF errors.
============ =======
Your first error file indicated 11 severe errors.  These are mainly input name errors.
 
Material:   to many spaces between "8     mm" This made it invisible to the construction objects, and the building surfaces.
 
The floor has a z-axis entry = 2.7.  Should be all zero (flat)
 
Design day object has incomplete fields after the wetbulb field.  These are optional.
 
DesignDay humidity indicator for Winter should have the same value as the maximum dry-bulb. (Warning only)
 
For the walls, "external environment" requires another field, or not valid field.  Use "outdoors" instead.
 
It appears to me that you have changed the IDF from an earlier version of Ex1.  Purchase Air, etc. are now changed to the new names.
 
Always 4, I have changed it to "control type".  "Any number" would work, but then there will be no type checking.
 
Always 20 is temperature, but can be any number.
 
Output variables has duplicated "hourly" , hourly;
There are extra spaces in the name as well. 
 
In the schedule "All days" should be "AllDays", no space.
 
The run control object:   No, No, No, Yes, No. One Yes is the minimum.   You have left the   Yes   field blank.
============ ========= =
If you read the error file careful, these are all listed or pointed to, but not explained with suggestion for corrections, except those have option field names.
 
The corrected  IDF is attached.
 
Please do not hesitate to contact me again, if you have more questions.  I am a retired EE Professor in Canada.

 

 Dr. Li  

 

To: EnergyPlus_Support@ yahoogroups. com
From: rahulopg@yahoo. co.in
Date: Wed, 21 Jul 2010 07:02:14 +0530
Subject: [EnergyPlus_ Support] How to debug/identify these errors

 
I am a beginner to Energy Plus.The first program that I tried to simulate gave me this error in Command prompt while simulating and Energy plus terminates.I have attached the error showing screen and my .idf file.


                                                 Will be helpful if anyone can reply with sum suggestions.

                                                                                                         thnxx




Look 'em in the eye: FREE Messenger video chat Chat Now!



Turn down-time into play-time with Messenger games Play Now!



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___