Thanks for the help. I have tried using the
ZoneControl:Thermostatic:OperativeTemperature but with no real visible
success. Any suggestions on where to check if it is impacting the comfort
properly? Also what Humidity Ratio is referenced in the thermal comfort
calculations? If its from the Sizing:System is it Preheat or
Central? Or is it outside the sizing object? Thanks
again
Greg
Morss From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Griffith, Brent Sent: Thursday, July 22, 2010 10:33 AM To: EnergyPlus_Support@xxxxxxxxxxxxxxx Subject: [EnergyPlus_Support] RE: Thermal Comfort Issues
It is reporting right.
The basic issue is radiant temperatures cause discomfort and it is a real
phenomenon. Modelers and others usually focus on ensuring that drybulb air
temperature setpoints are being met (or at least not being missed more than 300
hours a year) and these Standard 55 comfort results are often ignored.
Obviously if you are trying to design for comfort then pay attention to
comfort results. Tightening up the thermostat deadband can help decrease
Standard 55 hours, but it depends on the thermal envelope. There are also ways
to model control of HVAC based directly on comfort -- see for example
ZoneControl: From:
Hello, I have been trying to
find out how much I should worry about "Time Not Comfortable Based on Simple ASHRAE
55-2004". I ran a simulation and came back with
different numbers of hours, so I looked at the example files and most I have
looked at come back with Hours in this category. So is this an
issue? Is it really not comfortable or is this not reporting right?
Or should I just ignore it? Please let me know, thanks. Greg
Morss __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.