Re: [EnergyPlus_Support] Question about multi-equipment system.



What supply air temperature would you like? 10C? How much outside air do 
you need? You would pick these values according to your design. Same for 
the other inputs.

The Sizing:Zone object applies to all equipment in the zone. I would use 
the higher of the 2 air flow rates. But if you want to size these 
systems more like they would actually be, then make multiple runs using 
different sizing object inputs, and then use these inputs to "manually" 
size each system.

??? wrote:
> Dear e+ Users.
> When I want to describe multi-equipments in one zone(ex. VAV with FCU),
> what vaules should I insert into
> 1. Zone Cooling Design Supply Air Temperature & Zone Heating Design 
> Supply Air Temperature
> 2. Outdoor Air Flow Rate
> 3. Cooling Design Air Flow Rate & Heating Design Air Flow Rate
> in SIzing:Zone object?
> For example, if the cooling design air flow rate of VAV is 0.1 m3/s 
> and of FCU is 0.05 m3/s, should I insert 0.15 m3/s into the Cooling 
> Design Air Flow Rate of Sizing:Zone object?
> Kosan Roh.
> 

-- 
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL  32922-5703
Phone:   (321) 638-1454
Fax:     (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu

UCF - From Promise to Prominence: Celebrating 40 Years



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/