[EnergyPlus_Support] RE: import air of specific conditions (T, RH) in a zone



Yes, this is possible by a number of different ways.  One way fairly simple way  is with EMS --  see  Example #7 in the EMS application guide and the example file called EMSConstantVolumePurchAir.idf.  
Another way is set up an entire air handler with all the coils and controls and such to process the air as directed by scheduled supply deck conditions.  A third way is a set up a dummy zone that is controlled to the conditions you want and then move air from it to your zone using ZoneMixing.  

________________________________________
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Georgios KOKOGIANNAKIS [georgios.kokogiannakis@xxxxxxxxxxxxxxxxx]
Sent: Thursday, July 29, 2010 9:50 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] import air of specific conditions (T, RH) in a zone

Hi there,

I would like to import air of specific conditions (T, RH) in a zone. Is there a way of doing this in EnergyPlus (e.g. by importing the air flow and its condition from a csv file)?

Thanks,
Georgios*******************************************************************************************************************************
This email has been scanned by the Altman Email Security System.
For more information please visit www.altman.co.uk/emailsystems

*******************************************************************************************************************************




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/