Re: [EnergyPlus_Support] system sizing data transfer





Why don't you run the system sizing and the annual simulation in the same run -- then the results of the sizing will be used for the annual simulation?

To answer your direct question, there is some work ongoing to be able to produce output/input slices for saving the sizing results, but it has not yet been completed.

At 03:09 AM 8/6/2010, diorthotis wrote:
Hello,

I run a system sizing and yearly simulation for two similar models (the only difference between them is that the one has some extra energy saving measures such as Daylighting Controls). The system sizing gives of course different results.

Is there a way to simulate the second system with the same sizing results as the first one? I know I can transfer the sizing data manually (but there is quite a lot of work). Is there a way to do it automatically?


__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___