[EnergyPlus_Support] HVACTemplate:System:PackagedVAV
I am trying to model a Packaged VAV system, and I am using the HVACTemplate:System:PackagedVAV object to do so. I am getting the following warning when the object is expanded:
** Warning ** Output:PreprocessorMessage="ExpandObjects" has the following Warning conditions:
** ~~~ ** Warning: In HVACTemplate:System:PackagedVAV "RTU Packaged VAV" the Heating
** ~~~ ** Coil Design Setpoint is greater than the Cooling Coil Design Setpoint. This
** ~~~ ** may cause the heating coil and cooling coil to operate simultaneously.
** ~~~ ** Check results carefully and adjust controls if needed.
The warning is telling me that I should have my cooling-coil temperature (currently 55*F) warmer that the heating-coil temperature (currently 75*F) so that they don't fight each other. This would be fine if I had a a main heating coil & and reheat coil, but in this case the main heating coil needs to provide all of the heating.
Has anyone run into this issue before? Or, has anyone successfully modeled a packaged VAV system without reheat coils? If so, how do you keep the heating coil and cooling coil from fighting each other?
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/