You could correct these inputs and then use
SetPointManger:SingleZone:Coolling and SetPointManger:SingleZone:Heating
to control each coil individually (or even scheduled SP managers if you
like). You may have to manually size the heating coil if autosizing is used.
eddiecorwin wrote:
>
> I am trying to model a Packaged VAV system, and I am using the
> HVACTemplate:System:PackagedVAV object to do so. I am getting the
> following warning when the object is expanded:
>
> ** Warning ** Output:PreprocessorMessage="ExpandObjects" has the
> following Warning conditions:
> ** ~~~ ** Warning: In HVACTemplate:System:PackagedVAV "RTU Packaged
> VAV" the Heating
> ** ~~~ ** Coil Design Setpoint is greater than the Cooling Coil Design
> Setpoint. This
> ** ~~~ ** may cause the heating coil and cooling coil to operate
> simultaneously.
> ** ~~~ ** Check results carefully and adjust controls if needed.
>
> The warning is telling me that I should have my cooling-coil
> temperature (currently 55*F) warmer that the heating-coil temperature
> (currently 75*F) so that they don't fight each other. This would be
> fine if I had a a main heating coil & and reheat coil, but in this
> case the main heating coil needs to provide all of the heating.
>
> Has anyone run into this issue before? Or, has anyone successfully
> modeled a packaged VAV system without reheat coils? If so, how do you
> keep the heating coil and cooling coil from fighting each other?
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/