[EnergyPlus_Support] Re: ASHRAE 90.1-2007 9.4.1.1 & 9.4.1.2




According to the version 5.0 Input Output Reference for the "Lights" statement:

Field: Schedule Name
The name of the schedule that modifies the lighting power design level (see next field). The schedule values can be any positive number. The electrical input for lighting in a particular
timestep is the product of the design level and the value of this schedule in that timestep. If the design level is the maximum lighting power input the schedule should contain values between 0.0 and 1.0.

So, fractional schedule values are possible (allowed) for Lights.

But, from what you describe, sounds like you need to use a lighting schedule that is "similar" to your occupancy schedule... but with values that are 1.0 during occupied periods and then drop to 0.0 thirty minutes after there are no people remaining in the zone.  You just need to create a separate schedule for this (e.g., using Schedule:Compact or other Schedule* objects)


--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "jeannieboef" <jeannieboef@...> wrote:
>
> No replies...Any thoughts on this?
> 
> I've thought of modeling the occupant sensors by triggering the lights with the occupation schedule, but the occupation schedule is fractional and I don't know if that is allowed...i.e. that the program will make a 1 out of a fraction and a 0 when occupation is zero.
> 
> Secondly, how to manage the lights going out 30 min after occupation ends?
>




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/