|
Dear Jeannie and Vinay, ·
I have not followed this thread of conversation from the beginning,
and cannot give you too much time to look it up… but I’ll try. ·
Assuming that you are involved with a LEED project, your baseline
HVAC is PZ-AC only if the building o has 3
floors or less o is
also less than 25,000 sq.ft. o and
the proposed system is fossil-fueled or purchased heat ·
That means your baseline system should be defined with a DX
cooling coil and fossil-fueled heating coil. I think that I would use a
gas coil for the baseline; it’s simpler to create (no water loop). ·
I use component efficiencies appropriate for the modeled system
(the entire air or water loop, not individual zones). Baseline systems
require autosizing per ASHRAE 90.1, so you will have to get the model running,
then check the reports to see what capacity E+ has determined, then adjust your
input efficiencies as needed to match the 90.1 requirements. ·
The proposed system will be exactly as designed by
you (or whomever is the designer), including components and efficiencies. The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef Mr. Dirkes, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |