Re: [EnergyPlus_Support] WeatherProperty:SkyTemperatu re, error with "name" field



If you are running with V5.0.0.035, I believe we removed the requirement
to have the name in that object.

Hopefully, by V6 release, we will fully utilize that name field for
selecting different run periods, but for now, you should be able to leave
it blank (again, if you have V5.0.0.035) -- which is an update released in
early July.

I think you can simply change your IDD to not require it if you don't want
to download the update, but I'm not sure.

On Tue, 31 Aug 2010 00:37:38 -0000, "gun_arrr" <adam.scherba@xxxxxxxxx>
wrote:
> Hello,
> I am attempting to run a simulation using the
> "weatherproperty:skytemperature" object to input a sky temperature
> schedule. I would like to apply this schedule to the entire run period.
> Just to test things out, I created a Schedule:compact that sets the sky
> temp to 150 deg. When I run the simulation, I get the following errors
(see
> below). I have tried running this both with and without a named run
period.
> It seems that when a name is used, Eplus assumes it references a Design
> Day, but when no name is used, an error is also triggered. The I/O
> reference seems to imply that a blank name field will apply the modified
> sky temp to all run periods.
> 
> Any tips on how to avoid these errors?
> Thanks,
> Adam
> (my IDF file is included at the end of this post for reference)
> 
> 
> Cut and paste from I/O Reference:
> "Field: Name. This name references an existing design period (i.e.,
> SizingPeriod:DesignDay,SizingPeriod:WeatherFileDays, or
> SizingPeriod:WeatherFileConditionType) or run period (by
> name or blank for all run periods)."
> 
> Here are the two errors I get:
> 
> --------Case 1: RunPeriod name=JulyDay--------------------------
> ** Severe  **
> GetWeatherProperties:WeatherProperty:SkyTemperature="JULYDAY", invalid
> SizingPeriod:DesignDay referenced.
>    ** Severe  **
>    GetWeatherProperties:WeatherProperty:SkyTemperature="JULYDAY",
invalid
>    Schedule Name.
>    **  Fatal  ** GetWeatherInput: Above errors cause termination
> 
> ------Case 2: RunPeriod name=blank---------------------------
> ** Severe  ** IP: IDF line~307 Error detected in
> Object=WEATHERPROPERTY:SKYTEMPERATURE
>    **   ~~~   ** Field [Name] is required but was blank
>    ** Severe  ** IP: Blank "required" fields found in input
>    ** Severe  ** IP: Out of "range" values and/or blank required fields
>    found in input
>    **  Fatal  ** IP: Errors occurred on processing IDF file. Preceding
>    condition(s) cause termination.
> ---------------------------------------------------------------
> -----------IDF File--------------------------------------------
> ---------------------------------------------------------------
> !-Generator IDFEditor 1.37c
> !-Option SortedOrder
> 
> !-NOTE: All comments with '!-' are ignored by the IDFEditor and are
> generated automatically.
> !-      Use '!' comments if they need to be retained when using the
> IDFEditor.
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: VERSION ===========
> 
> ! Generated by EPXMLPreproc2 (Windows 32 Version 0.1.2.32)
> ! Created on 05/08/2010 19:22:48
> !***** This data and software ("Data") is provided by the National
> Renewable *****
> !***** Energy Laboratory ("NREL"), which is operated by the Alliance for
> *****
> !***** Sustainable Energy, LLC ("ALLIANCE") for the U.S. Department Of
> *****
> !***** Energy ("DOE"). *****
> !***** Access to and use of these Data shall impose the following
> obligations *****
> !***** on the user, as set forth in this Agreement.  The user is granted
> the *****
> !***** right, without any fee or cost, to use, copy, modify, alter,
> enhance *****
> !***** and distribute these Data for any purpose whatsoever, provided
that
> this *****
> !***** entire notice appears in all copies of the Data.  Further, the
user
> *****
> !***** agrees to credit DOE/NREL/ALLIANCE in any publication that
results
> from *****
> !***** the use of these Data.  The names DOE/NREL/ALLIANCE, however, may
> not *****
> !***** be used in any advertising or publicity to endorse or promote any
> products *****
> !***** or commercial entities unless specific written permission is
> obtained from *****
> !***** DOE/NREL/ ALLIANCE.  The user also understands that
> DOE/NREL/Alliance is *****
> !***** not obligated to provide the user with any support, consulting,
> training *****
> !***** or assistance of any kind with regard to the use of these Data or
> to *****
> !***** provide the user with any updates, revisions or new versions of
> these Data. *****
> !***** YOU AGREE TO INDEMNIFY DOE/NREL/Alliance, AND ITS SUBSIDIARIES,
> AFFILIATES, *****
> !***** OFFICERS, AGENTS, AND EMPLOYEES AGAINST ANY CLAIM OR DEMAND,
> INCLUDING *****
> !***** 'REASONABLE ATTORNEYS' FEES, RELATED TO YOUR USE OF THESE DATA. 
> THESE DATA *****
> !***** ARE PROVIDED BY DOE/NREL/Alliance "AS IS" AND ANY EXPRESS OR
> IMPLIED *****
> !***** WARRANTIES, INCLUDING BUT NOT LIMITED TO, THE IMPLIED WARRANTIES
OF
> *****
> !***** MERCHANTABILITY AND FITNESS FOR A PARTICULAR PURPOSE ARE
> DISCLAIMED.  IN *****
> !***** NO EVENT SHALL DOE/NREL/ALLIANCE BE LIABLE FOR ANY SPECIAL,
> INDIRECT OR *****
> !***** CONSEQUENTIAL DAMAGES OR ANY DAMAGES WHATSOEVER, INCLUDING BUT
NOT
> LIMITED *****
> !***** TO CLAIMS ASSOCIATED WITH THE LOSS OF DATA OR PROFITS, WHICH MAY
> RESULT *****
> !***** FROM AN ACTION IN CONTRACT, NEGLIGENCE OR OTHER TORTIOUS CLAIM
THAT
> *****
> !***** ARISES OUT OF OR IN CONNECTION WITH THE ACCESS, USE OR
PERFORMANCE
> OF *****
> !***** THESE DATA. *****
> ! Building Description
> ! Simple Office Building for roof temp comparison
> ! Start SimMetaData
> ! WeatherFileName=USA_OR_Portland_TMY2.epw
> ! RoofConstruction=Insulation Entirely Above Deck
> ! ExtWallConstruction=Steel-Framed
> ! End SimMetaData
> ! Start WebInterface Parameters
> ! EMAIL_ADDRESS=adam.scherba@xxxxxxxxx
> ! BUILDING_DESCRIPTION=Simple Office Building for roof temp comparison
> ! BUILDING_TYPE=Office/Professional
> ! CITY=PORTLAND
> ! COUNTRY=USA
> ! ELECTRICAL_PLUG_INTENSITY_INPUT=SmartDefault
> ! ENERGYPLUSVERSION=5.0
> ! GAS_APPLIANCE_INTENSITY_INPUT=SmartDefault
> ! GEOCHG=false
> ! IDF_UPLOAD=0
> ! MODEL=Simple
> ! NUMBER_OF_FLOORS=5
> ! PEOPLE_DENSITY_INPUT=SmartDefault
> ! ROOF_TYPE=Insulation Entirely above Deck
> ! ROOF_TYPE_INPUT=CUSTOM
> ! STATE=OR
> ! TARGETED_STANDARD=ASHRAE 90.1-2007
> ! TOTAL_FLOOR_AREA=2000
> ! VERSION=5.0
> ! WALL_TYPE_INPUT=SmartDefault
> ! WEATHER_FILE=USA_OR_Portland_TMY2.epw
> ! WEATHER_FILE_KEY=USA_OR_PORTLAND
> ! WEBINTERFACEVERSION=5.0
> !
> ! End WebInterface Parameters
> ! Number of Zones: 15
> Version,
>     5.0.0;                   !- Version Identifier
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIMULATIONCONTROL ===========
> 
> SimulationControl,
>     Yes,                     !- Do Zone Sizing Calculation
>     Yes,                     !- Do System Sizing Calculation
>     Yes,                     !- Do Plant Sizing Calculation
>     No,                      !- Run Simulation for Sizing Periods
>     Yes;                     !- Run Simulation for Weather File Run
Periods
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BUILDING ===========
> 
> Building,
>     Simple Office Building for roof temp comparison,  !- Name
>     0.0000,                  !- North Axis {deg}
>     City,                    !- Terrain
>     0.0400,                  !- Loads Convergence Tolerance Value
>     0.2000,                  !- Temperature Convergence Tolerance Value
>     {deltaC}
>     FullExterior,            !- Solar Distribution
>     25;                      !- Maximum Number of Warmup Days
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SHADOWCALCULATION ===========
> 
> ShadowCalculation,
>     30,                      !- Calculation Frequency
>     15000;                   !- Maximum Figures in Shadow Overlap
>     Calculations
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS:
SURFACECONVECTIONALGORITHM:INSIDE
> ===========
> 
> SurfaceConvectionAlgorithm:Inside,
>     Detailed;                !- Algorithm
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS:
SURFACECONVECTIONALGORITHM:OUTSIDE
> ===========
> 
> SurfaceConvectionAlgorithm:Outside,
>     DOE-2;                   !- Algorithm
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: HEATBALANCEALGORITHM ===========
> 
> HeatBalanceAlgorithm,
>     ConductionTransferFunction,  !- Algorithm
>     200.0000;                !- Surface Temperature Upper Limit
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONEAIRHEATBALANCEALGORITHM
> ===========
> 
> ZoneAirHeatBalanceAlgorithm,
>     AnalyticalSolution;      !- Algorithm
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: TIMESTEP ===========
> 
> Timestep,
>     30;                      !- Number of Timesteps per Hour
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONVERGENCELIMITS ===========
> 
> ConvergenceLimits,
>     5,                       !- Minimum System Timestep {minutes}
>     25;                      !- Maximum HVAC Iterations
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SITE:LOCATION ===========
> 
> !  VERSION,
> !    3.1;                    !- Version Identifier
> Site:Location,
>     USA OR-PORTLAND,         !- Name
>     45.58,                   !- Latitude {deg}
>     -122.58,                 !- Longitude {deg}
>     -8.0,                    !- Time Zone {hr}
>     12;                      !- Elevation {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIZINGPERIOD:DESIGNDAY
===========
> 
> ! PORTLAND_OR_USA Annual Heating 99.6%, MaxDB=-5.6°C
> SizingPeriod:DesignDay,
>     PORTLAND Ann Htg 99.6% Condns DB,  !- Name
>     -5.6,                    !- Maximum Dry-Bulb Temperature {C}
>     0.0,                     !- Daily Temperature Range {deltaC}
>     -5.6,                    !- Humidity Indicating Conditions at
Maximum
>     Dry-Bulb
>     101181.,                 !- Barometric Pressure {Pa}
>     6,                       !- Wind Speed {m/s}
>     120,                     !- Wind Direction {deg}
>     0.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day of Month
>     1,                       !- Month
>     WinterDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     WetBulb;                 !- Humidity Indicating Type
> 
> ! PORTLAND_OR_USA Annual Cooling (DB=>MWB) .4%, MaxDB=32.7°C MWB=19.7°C
> SizingPeriod:DesignDay,
>     PORTLAND Ann Clg .4% Condns DB=>MWB,  !- Name
>     32.7,                    !- Maximum Dry-Bulb Temperature {C}
>     11.9,                    !- Daily Temperature Range {deltaC}
>     19.7,                    !- Humidity Indicating Conditions at
Maximum
>     Dry-Bulb
>     101181.,                 !- Barometric Pressure {Pa}
>     4.8,                     !- Wind Speed {m/s}
>     310,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     WetBulb;                 !- Humidity Indicating Type
> 
> ! PORTLAND_OR_USA Annual Cooling (WB=>MDB) .4%, MDB=30.7°C WB=20.7°C
> SizingPeriod:DesignDay,
>     PORTLAND Ann Clg .4% Condns WB=>MDB,  !- Name
>     30.7,                    !- Maximum Dry-Bulb Temperature {C}
>     11.9,                    !- Daily Temperature Range {deltaC}
>     20.7,                    !- Humidity Indicating Conditions at
Maximum
>     Dry-Bulb
>     101181.,                 !- Barometric Pressure {Pa}
>     4.8,                     !- Wind Speed {m/s}
>     310,                     !- Wind Direction {deg}
>     1.00,                    !- Sky Clearness
>     0,                       !- Rain Indicator
>     0,                       !- Snow Indicator
>     21,                      !- Day of Month
>     8,                       !- Month
>     SummerDesignDay,         !- Day Type
>     0,                       !- Daylight Saving Time Indicator
>     WetBulb;                 !- Humidity Indicating Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: RUNPERIOD ===========
> 
> RunPeriod,
>     JulyDay,                 !- Name
>     7,                       !- Begin Month
>     15,                      !- Begin Day of Month
>     7,                       !- End Month
>     17,                      !- End Day of Month
>     Wednesday,               !- Day of Week for Start Day
>     No,                      !- Use Weather File Holidays and Special
Days
>     No,                      !- Use Weather File Daylight Saving Period
>     No,                      !- Apply Weekend Holiday Rule
>     Yes,                     !- Use Weather File Rain Indicators
>     Yes,                     !- Use Weather File Snow Indicators
>     1.0000;                  !- Number of Times Runperiod to be Repeated
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: RUNPERIODCONTROL:SPECIALDAYS
> ===========
> 
> ! US National Holidays
> RunPeriodControl:SpecialDays,
>     New Years Day,           !- Name
>     January 1,               !- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> RunPeriodControl:SpecialDays,
>     Veterans Day,            !- Name
>     November 11,             !- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> RunPeriodControl:SpecialDays,
>     Christmas,               !- Name
>     December 25,             !- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> RunPeriodControl:SpecialDays,
>     Independence Day,        !- Name
>     July 4,                  !- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> RunPeriodControl:SpecialDays,
>     MLK Day,                 !- Name
>     3rd Monday in January,   !- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> RunPeriodControl:SpecialDays,
>     Presidents Day,          !- Name
>     3rd Monday in February,  !- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> RunPeriodControl:SpecialDays,
>     Memorial Day,            !- Name
>     Last Monday in May,      !- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> RunPeriodControl:SpecialDays,
>     Labor Day,               !- Name
>     1st Monday in September, !- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> RunPeriodControl:SpecialDays,
>     Columbus Day,            !- Name
>     2nd Monday in October,   !- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> RunPeriodControl:SpecialDays,
>     Thanksgiving,            !- Name
>     4th Thursday in November,!- Start Date
>     1,                       !- Duration {days}
>     Holiday;                 !- Special Day Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS:
> RUNPERIODCONTROL:DAYLIGHTSAVINGTIME ===========
> 
> ! Daylight Saving Period in US
> RunPeriodControl:DaylightSavingTime,
>     2nd Sunday in March,     !- Start Date
>     1st Sunday in November;  !- End Date
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: WEATHERPROPERTY:SKYTEMPERATURE
> ===========
> 
> WeatherProperty:SkyTemperature,
>     JulyDay,                 !- Name
>     ScheduleValue,           !- Calculation Type
>     SkyTemp_SCH;             !- Schedule Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS:
> SITE:GROUNDTEMPERATURE:BUILDINGSURFACE ===========
> 
> Site:GroundTemperature:BuildingSurface,
>     19.776,                  !- January Ground Temperature {C}
>     19.761,                  !- February Ground Temperature {C}
>     19.789,                  !- March Ground Temperature {C}
>     19.814,                  !- April Ground Temperature {C}
>     19.905,                  !- May Ground Temperature {C}
>     20.385,                  !- June Ground Temperature {C}
>     21.476,                  !- July Ground Temperature {C}
>     22.177,                  !- August Ground Temperature {C}
>     20.950,                  !- September Ground Temperature {C}
>     20.084,                  !- October Ground Temperature {C}
>     19.917,                  !- November Ground Temperature {C}
>     19.847;                  !- December Ground Temperature {C}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SITE:WATERMAINSTEMPERATURE
> ===========
> 
> Site:WaterMainsTemperature,
>     CORRELATION,             !- Calculation Method
>     ,                        !- Temperature Schedule Name
>     11.70,                   !- Annual Average Outdoor Air Temperature
{C}
>     16.40;                   !- Maximum Difference In Monthly Average
>     Outdoor Air Temperatures {deltaC}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SCHEDULETYPELIMITS ===========
> 
> !***** Schedule Set *****
> ScheduleTypeLimits,
>     Any Number;              !- Name
> 
> ScheduleTypeLimits,
>     Fraction,                !- Name
>     0.0,                     !- Lower Limit Value
>     1.0,                     !- Upper Limit Value
>     CONTINUOUS;              !- Numeric Type
> 
> ScheduleTypeLimits,
>     Temperature,             !- Name
>     -60,                     !- Lower Limit Value
>     200,                     !- Upper Limit Value
>     CONTINUOUS;              !- Numeric Type
> 
> ScheduleTypeLimits,
>     On/Off,                  !- Name
>     0,                       !- Lower Limit Value
>     1,                       !- Upper Limit Value
>     DISCRETE;                !- Numeric Type
> 
> ScheduleTypeLimits,
>     Control Type,            !- Name
>     0,                       !- Lower Limit Value
>     4,                       !- Upper Limit Value
>     DISCRETE;                !- Numeric Type
> 
> ScheduleTypeLimits,
>     Humidity,                !- Name
>     10,                      !- Lower Limit Value
>     90,                      !- Upper Limit Value
>     CONTINUOUS;              !- Numeric Type
> 
> ScheduleTypeLimits,
>     Number;                  !- Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SCHEDULE:COMPACT ===========
> 
> ! Schedule set    Schedule_Office_ASHRAE_90.1-1989_TypTstatSetback[]
> ! Hours: Weekly: 92, Yearly: 4797
> ! Schedule Office Lighting,  ASHRAE 90.1-1989, Section 13 w/addenda
> Schedule:Compact,
>     BLDG_LIGHT_SCH,          !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays,           !- Field 2
>     Until: 05:00,            !- Field 3
>     0.05,                    !- Field 4
>     Until: 07:00,            !- Field 5
>     0.1,                     !- Field 6
>     Until: 08:00,            !- Field 7
>     0.3,                     !- Field 8
>     Until: 17:00,            !- Field 9
>     0.9,                     !- Field 10
>     Until: 18:00,            !- Field 11
>     0.5,                     !- Field 12
>     Until: 20:00,            !- Field 13
>     0.3,                     !- Field 14
>     Until: 22:00,            !- Field 15
>     0.2,                     !- Field 16
>     Until: 23:00,            !- Field 17
>     0.1,                     !- Field 18
>     Until: 24:00,            !- Field 19
>     0.05,                    !- Field 20
>     For: SummerDesignDay,    !- Field 21
>     Until: 24:00,            !- Field 22
>     1.0,                     !- Field 23
>     For: Saturday,           !- Field 24
>     Until: 06:00,            !- Field 25
>     0.05,                    !- Field 26
>     Until: 08:00,            !- Field 27
>     0.1,                     !- Field 28
>     Until: 12:00,            !- Field 29
>     0.3,                     !- Field 30
>     Until: 17:00,            !- Field 31
>     0.15,                    !- Field 32
>     Until: 24:00,            !- Field 33
>     0.05,                    !- Field 34
>     For: WinterDesignDay,    !- Field 35
>     Until: 24:00,            !- Field 36
>     0.0,                     !- Field 37
>     For: Sunday Holidays AllOtherDays,  !- Field 38
>     Until: 24:00,            !- Field 39
>     0.05;                    !- Field 40
> 
> ! Schedule Office Receptacle,  ASHRAE 90.1-1989, Section 13
> ! MODIFIED for increased off-hours plug loads (to account for more IT
> equipment)
> ! Hours: Weekly: 86.15, Yearly: 4492
> Schedule:Compact,
>     BLDG_EQUIP_SCH,          !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays,           !- Field 2
>     Until: 08:00,            !- Field 3
>     0.40,                    !- Field 4
>     Until: 12:00,            !- Field 5
>     0.90,                    !- Field 6
>     Until: 13:00,            !- Field 7
>     0.80,                    !- Field 8
>     Until: 17:00,            !- Field 9
>     0.90,                    !- Field 10
>     Until: 18:00,            !- Field 11
>     0.50,                    !- Field 12
>     Until: 24:00,            !- Field 13
>     0.40,                    !- Field 14
>     For: SummerDesignDay,    !- Field 15
>     Until: 24:00,            !- Field 16
>     1.0,                     !- Field 17
>     For: Saturday,           !- Field 18
>     Until: 06:00,            !- Field 19
>     0.30,                    !- Field 20
>     Until: 08:00,            !- Field 21
>     0.4,                     !- Field 22
>     Until: 12:00,            !- Field 23
>     0.5,                     !- Field 24
>     Until: 17:00,            !- Field 25
>     0.35,                    !- Field 26
>     Until: 24:00,            !- Field 27
>     0.30,                    !- Field 28
>     For: WinterDesignDay,    !- Field 29
>     Until: 24:00,            !- Field 30
>     0.0,                     !- Field 31
>     For: Sunday Holidays AllOtherDays,  !- Field 32
>     Until: 24:00,            !- Field 33
>     0.30;                    !- Field 34
> 
> ! Schedule Office Occupancy,
> Schedule:Compact,
>     BLDG_OCC_SCH,            !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays,           !- Field 2
>     Until: 06:00,            !- Field 3
>     0.0,                     !- Field 4
>     Until: 07:00,            !- Field 5
>     0.1,                     !- Field 6
>     Until: 08:00,            !- Field 7
>     0.2,                     !- Field 8
>     Until: 12:00,            !- Field 9
>     0.95,                    !- Field 10
>     Until: 13:00,            !- Field 11
>     0.5,                     !- Field 12
>     Until: 17:00,            !- Field 13
>     0.95,                    !- Field 14
>     Until: 18:00,            !- Field 15
>     0.3,                     !- Field 16
>     Until: 20:00,            !- Field 17
>     0.1,                     !- Field 18
>     Until: 24:00,            !- Field 19
>     0.05,                    !- Field 20
>     For: SummerDesignDay,    !- Field 21
>     Until: 06:00,            !- Field 22
>     0.0,                     !- Field 23
>     Until: 22:00,            !- Field 24
>     1.0,                     !- Field 25
>     Until: 24:00,            !- Field 26
>     0.05,                    !- Field 27
>     For: Saturday,           !- Field 28
>     Until: 06:00,            !- Field 29
>     0.0,                     !- Field 30
>     Until: 08:00,            !- Field 31
>     0.1,                     !- Field 32
>     Until: 12:00,            !- Field 33
>     0.3,                     !- Field 34
>     Until: 17:00,            !- Field 35
>     0.1,                     !- Field 36
>     Until: 19:00,            !- Field 37
>     0.0,                     !- Field 38
>     Until: 24:00,            !- Field 39
>     0.0,                     !- Field 40
>     For: WinterDesignDay,    !- Field 41
>     Until: 24:00,            !- Field 42
>     0.0,                     !- Field 43
>     For: Sunday Holidays AllOtherDays,  !- Field 44
>     Until: 06:00,            !- Field 45
>     0.0,                     !- Field 46
>     Until: 18:00,            !- Field 47
>     0.0,                     !- Field 48
>     Until: 24:00,            !- Field 49
>     0.0;                     !- Field 50
> 
> ! Schedule Elevator
> Schedule:Compact,
>     BLDG_ELEVATORS,          !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 07:00,            !- Field 3
>     0.0,                     !- Field 4
>     Until: 08:00,            !- Field 5
>     0.35,                    !- Field 6
>     Until: 09:00,            !- Field 7
>     0.69,                    !- Field 8
>     Until: 10:00,            !- Field 9
>     0.43,                    !- Field 10
>     Until: 11:00,            !- Field 11
>     0.37,                    !- Field 12
>     Until: 12:00,            !- Field 13
>     0.43,                    !- Field 14
>     Until: 13:00,            !- Field 15
>     0.58,                    !- Field 16
>     Until: 14:00,            !- Field 17
>     0.48,                    !- Field 18
>     Until: 15:00,            !- Field 19
>     0.37,                    !- Field 20
>     Until: 16:00,            !- Field 21
>     0.37,                    !- Field 22
>     Until: 17:00,            !- Field 23
>     0.46,                    !- Field 24
>     Until: 18:00,            !- Field 25
>     0.62,                    !- Field 26
>     Until: 19:00,            !- Field 27
>     0.12,                    !- Field 28
>     Until: 20:00,            !- Field 29
>     0.04,                    !- Field 30
>     Until: 21:00,            !- Field 31
>     0.04,                    !- Field 32
>     Until: 24:00,            !- Field 33
>     0.00,                    !- Field 34
>     For: Saturday WinterDesignDay,  !- Field 35
>     Until: 07:00,            !- Field 36
>     0.0,                     !- Field 37
>     Until: 08:00,            !- Field 38
>     0.16,                    !- Field 39
>     Until: 09:00,            !- Field 40
>     0.14,                    !- Field 41
>     Until: 10:00,            !- Field 42
>     0.21,                    !- Field 43
>     Until: 11:00,            !- Field 44
>     0.18,                    !- Field 45
>     Until: 12:00,            !- Field 46
>     0.25,                    !- Field 47
>     Until: 13:00,            !- Field 48
>     0.21,                    !- Field 49
>     Until: 14:00,            !- Field 50
>     0.13,                    !- Field 51
>     Until: 15:00,            !- Field 52
>     0.08,                    !- Field 53
>     Until: 16:00,            !- Field 54
>     0.04,                    !- Field 55
>     Until: 17:00,            !- Field 56
>     0.05,                    !- Field 57
>     Until: 18:00,            !- Field 58
>     0.06,                    !- Field 59
>     Until: 24:00,            !- Field 60
>     0.00,                    !- Field 61
>     For: Sunday Holidays AllOtherDays,  !- Field 62
>     Until: 24:00,            !- Field 63
>     0.0;                     !- Field 64
> 
> Schedule:Compact,
>     INFIL_SCH,               !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 06:00,            !- Field 3
>     1.0,                     !- Field 4
>     Until: 22:00,            !- Field 5
>     0.0,                     !- Field 6
>     Until: 24:00,            !- Field 7
>     1.0,                     !- Field 8
>     For: Saturday WinterDesignDay,  !- Field 9
>     Until: 06:00,            !- Field 10
>     1.0,                     !- Field 11
>     Until: 18:00,            !- Field 12
>     0.0,                     !- Field 13
>     Until: 24:00,            !- Field 14
>     1.0,                     !- Field 15
>     For: Sunday Holidays AllOtherDays,  !- Field 16
>     Until: 24:00,            !- Field 17
>     1.0;                     !- Field 18
> 
> Schedule:Compact,
>     INFIL_HALF_ON_SCH,       !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 06:00,            !- Field 3
>     1.0,                     !- Field 4
>     Until: 22:00,            !- Field 5
>     0.5,                     !- Field 6
>     Until: 24:00,            !- Field 7
>     1.0,                     !- Field 8
>     For: Saturday WinterDesignDay,  !- Field 9
>     Until: 06:00,            !- Field 10
>     1.0,                     !- Field 11
>     Until: 18:00,            !- Field 12
>     0.5,                     !- Field 13
>     Until: 24:00,            !- Field 14
>     1.0,                     !- Field 15
>     For: Sunday Holidays AllOtherDays,  !- Field 16
>     Until: 24:00,            !- Field 17
>     1.0;                     !- Field 18
> 
> Schedule:Compact,
>     INFIL_QUARTER_ON_SCH,    !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 06:00,            !- Field 3
>     1.0,                     !- Field 4
>     Until: 22:00,            !- Field 5
>     0.25,                    !- Field 6
>     Until: 24:00,            !- Field 7
>     1.0,                     !- Field 8
>     For: Saturday WinterDesignDay,  !- Field 9
>     Until: 06:00,            !- Field 10
>     1.0,                     !- Field 11
>     Until: 18:00,            !- Field 12
>     0.25,                    !- Field 13
>     Until: 24:00,            !- Field 14
>     1.0,                     !- Field 15
>     For: Sunday Holidays AllOtherDays,  !- Field 16
>     Until: 24:00,            !- Field 17
>     1.0;                     !- Field 18
> 
> ! Schedule Office Service Water Heating, ASHRAE 90.1-1989, Section 13
> Schedule:Compact,
>     BLDG_SWH_SCH,            !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 05:00,            !- Field 3
>     0.05,                    !- Field 4
>     Until: 06:00,            !- Field 5
>     0.08,                    !- Field 6
>     Until: 07:00,            !- Field 7
>     0.07,                    !- Field 8
>     Until: 08:00,            !- Field 9
>     0.19,                    !- Field 10
>     Until: 09:00,            !- Field 11
>     0.35,                    !- Field 12
>     Until: 10:00,            !- Field 13
>     0.38,                    !- Field 14
>     Until: 11:00,            !- Field 15
>     0.39,                    !- Field 16
>     Until: 12:00,            !- Field 17
>     0.47,                    !- Field 18
>     Until: 13:00,            !- Field 19
>     0.57,                    !- Field 20
>     Until: 14:00,            !- Field 21
>     0.54,                    !- Field 22
>     Until: 15:00,            !- Field 23
>     0.34,                    !- Field 24
>     Until: 16:00,            !- Field 25
>     0.33,                    !- Field 26
>     Until: 17:00,            !- Field 27
>     0.44,                    !- Field 28
>     Until: 18:00,            !- Field 29
>     0.26,                    !- Field 30
>     Until: 19:00,            !- Field 31
>     0.21,                    !- Field 32
>     Until: 20:00,            !- Field 33
>     0.15,                    !- Field 34
>     Until: 21:00,            !- Field 35
>     0.17,                    !- Field 36
>     Until: 22:00,            !- Field 37
>     0.08,                    !- Field 38
>     Until: 24:00,            !- Field 39
>     0.05,                    !- Field 40
>     For: Saturday WinterDesignDay,  !- Field 41
>     Until: 05:00,            !- Field 42
>     0.05,                    !- Field 43
>     Until: 06:00,            !- Field 44
>     0.08,                    !- Field 45
>     Until: 07:00,            !- Field 46
>     0.07,                    !- Field 47
>     Until: 08:00,            !- Field 48
>     0.11,                    !- Field 49
>     Until: 09:00,            !- Field 50
>     0.15,                    !- Field 51
>     Until: 10:00,            !- Field 52
>     0.21,                    !- Field 53
>     Until: 11:00,            !- Field 54
>     0.19,                    !- Field 55
>     Until: 12:00,            !- Field 56
>     0.23,                    !- Field 57
>     Until: 13:00,            !- Field 58
>     0.20,                    !- Field 59
>     Until: 14:00,            !- Field 60
>     0.19,                    !- Field 61
>     Until: 15:00,            !- Field 62
>     0.15,                    !- Field 63
>     Until: 16:00,            !- Field 64
>     0.13,                    !- Field 65
>     Until: 17:00,            !- Field 66
>     0.14,                    !- Field 67
>     Until: 21:00,            !- Field 68
>     0.07,                    !- Field 69
>     Until: 22:00,            !- Field 70
>     0.09,                    !- Field 71
>     Until: 24:00,            !- Field 72
>     0.05,                    !- Field 73
>     For: Sunday Holidays AllOtherDays,  !- Field 74
>     Until: 05:00,            !- Field 75
>     0.04,                    !- Field 76
>     Until: 06:00,            !- Field 77
>     0.07,                    !- Field 78
>     Until: 11:00,            !- Field 79
>     0.04,                    !- Field 80
>     Until: 13:00,            !- Field 81
>     0.06,                    !- Field 82
>     Until: 14:00,            !- Field 83
>     0.09,                    !- Field 84
>     Until: 15:00,            !- Field 85
>     0.06,                    !- Field 86
>     Until: 21:00,            !- Field 87
>     0.04,                    !- Field 88
>     Until: 22:00,            !- Field 89
>     0.07,                    !- Field 90
>     Until: 24:00,            !- Field 91
>     0.04;                    !- Field 92
> 
> Schedule:Compact,
>     Hours_of_operation,      !- Name
>     On/Off,                  !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 06:00,            !- Field 3
>     0.0,                     !- Field 4
>     Until: 22:00,            !- Field 5
>     1.0,                     !- Field 6
>     Until: 24:00,            !- Field 7
>     0.0,                     !- Field 8
>     For: Saturday WinterDesignDay,  !- Field 9
>     Until: 06:00,            !- Field 10
>     0.0,                     !- Field 11
>     Until: 18:00,            !- Field 12
>     1.0,                     !- Field 13
>     Until: 24:00,            !- Field 14
>     0.0,                     !- Field 15
>     For: Sunday Holidays AllOtherDays,  !- Field 16
>     Until: 24:00,            !- Field 17
>     0.0;                     !- Field 18
> 
> Schedule:Compact,
>     ALWAYS_ON,               !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     1.0;                     !- Field 4
> 
> Schedule:Compact,
>     ALWAYS_OFF,              !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     0.0;                     !- Field 4
> 
> ! Schedule Office HVAC Systems, ASHRAE 90.1-1989, Section 13
> !  Equivalent Full-Load Hours: Weekdays 16, Saturday 12, Sunday/Holidays
0
> Schedule:Compact,
>     HVACOperationSchd,       !- Name
>     On/Off,                  !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 06:00,            !- Field 3
>     0.0,                     !- Field 4
>     Until: 22:00,            !- Field 5
>     1.0,                     !- Field 6
>     Until: 24:00,            !- Field 7
>     0.0,                     !- Field 8
>     For: Saturday WinterDesignDay,  !- Field 9
>     Until: 06:00,            !- Field 10
>     0.0,                     !- Field 11
>     Until: 18:00,            !- Field 12
>     1.0,                     !- Field 13
>     Until: 24:00,            !- Field 14
>     0.0,                     !- Field 15
>     For: Sunday Holidays AllOtherDays,  !- Field 16
>     Until: 24:00,            !- Field 17
>     0.0;                     !- Field 18
> 
> Schedule:Compact,
>     PlantOnSched,            !- Name
>     On/Off,                  !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     1.0;                     !- Field 4
> 
> Schedule:Compact,
>     FAN_SCH,                 !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     1.0;                     !- Field 4
> 
> Schedule:Compact,
>     ReheatCoilAvailSched,    !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     1.0;                     !- Field 4
> 
> Schedule:Compact,
>     CoolingCoilAvailSched,   !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     1.0;                     !- Field 4
> 
> Schedule:Compact,
>     HTGSETP_SCH,             !- Name
>     Temperature,             !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays,           !- Field 2
>     Until: 05:00,            !- Field 3
>     15.6,                    !- Field 4
>     Until: 19:00,            !- Field 5
>     21.0,                    !- Field 6
>     Until: 24:00,            !- Field 7
>     15.6,                    !- Field 8
>     For SummerDesignDay,     !- Field 9
>     Until: 24:00,            !- Field 10
>     15.6,                    !- Field 11
>     For: Saturday,           !- Field 12
>     Until: 06:00,            !- Field 13
>     15.6,                    !- Field 14
>     Until: 17:00,            !- Field 15
>     21.0,                    !- Field 16
>     Until: 24:00,            !- Field 17
>     15.6,                    !- Field 18
>     For: WinterDesignDay,    !- Field 19
>     Until: 24:00,            !- Field 20
>     21.0,                    !- Field 21
>     For: Sunday Holidays AllOtherDays,  !- Field 22
>     Until: 24:00,            !- Field 23
>     15.6;                    !- Field 24
> 
> Schedule:Compact,
>     CLGSETP_SCH,             !- Name
>     Temperature,             !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 06:00,            !- Field 3
>     30.0,                    !- Field 4
>     Until: 22:00,            !- Field 5
>     24.0,                    !- Field 6
>     Until: 24:00,            !- Field 7
>     30.0,                    !- Field 8
>     For: Saturday,           !- Field 9
>     Until: 06:00,            !- Field 10
>     30.0,                    !- Field 11
>     Until: 18:00,            !- Field 12
>     24.0,                    !- Field 13
>     Until: 24:00,            !- Field 14
>     30.0,                    !- Field 15
>     For WinterDesignDay,     !- Field 16
>     Until: 24:00,            !- Field 17
>     30.0,                    !- Field 18
>     For: Sunday Holidays AllOtherDays,  !- Field 19
>     Until: 24:00,            !- Field 20
>     30.0;                    !- Field 21
> 
> Schedule:Compact,
>     Humidity Setpoint Schedule,  !- Name
>     Humidity,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 24:00,            !- Field 3
>     50,                      !- Field 4
>     For: Saturday WinterDesignDay,  !- Field 5
>     Until: 24:00,            !- Field 6
>     50,                      !- Field 7
>     For: Sunday Holidays AllOtherDays,  !- Field 8
>     Until: 24:00,            !- Field 9
>     50;                      !- Field 10
> 
> Schedule:Compact,
>     MinRelHumSetSch,         !- Name
>     Humidity,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     30;                      !- Field 4
> 
> Schedule:Compact,
>     MaxRelHumSetSch,         !- Name
>     Humidity,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     60;                      !- Field 4
> 
> Schedule:Compact,
>     MinOA_MotorizedDamper_Sched,  !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: Weekdays SummerDesignDay,  !- Field 2
>     Until: 07:00,            !- Field 3
>     0.0,                     !- Field 4
>     Until: 22:00,            !- Field 5
>     1.0,                     !- Field 6
>     Until: 24:00,            !- Field 7
>     0.0,                     !- Field 8
>     For: Saturday WinterDesignDay,  !- Field 9
>     Until: 07:00,            !- Field 10
>     0.0,                     !- Field 11
>     Until: 18:00,            !- Field 12
>     1.0,                     !- Field 13
>     Until: 24:00,            !- Field 14
>     0.0,                     !- Field 15
>     For: Sunday Holidays AllOtherDays,  !- Field 16
>     Until: 24:00,            !- Field 17
>     0.0;                     !- Field 18
> 
> Schedule:Compact,
>     MinOA_Sched,             !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     1.0;                     !- Field 4
> 
> Schedule:Compact,
>     Dual Zone Control Type Sched,  !- Name
>     Control Type,            !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     4;                       !- Field 4
> 
> Schedule:Compact,
>     Seasonal-Reset-Supply-Air-Temp-Sch,  !- Name
>     Temperature,             !- Schedule Type Limits Name
>     Through: 3/31,           !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     13.0,                    !- Field 4
>     Through: 9/30,           !- Field 5
>     For: AllDays,            !- Field 6
>     Until: 24:00,            !- Field 7
>     13.0,                    !- Field 8
>     Through: 12/31,          !- Field 9
>     For: AllDays,            !- Field 10
>     Until: 24:00,            !- Field 11
>     13.0;                    !- Field 12
> 
> Schedule:Compact,
>     CW-Loop-Temp-Schedule,   !- Name
>     Temperature,             !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     6.7;                     !- Field 4
> 
> Schedule:Compact,
>     HW-Loop-Temp-Schedule,   !- Name
>     Temperature,             !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     60.;                     !- Field 4
> 
> Schedule:Compact,
>     Heating-Supply-Air-Temp-Sch,  !- Name
>     Temperature,             !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     16.0;                    !- Field 4
> 
> Schedule:Compact,
>     ACTIVITY_SCH,            !- Name
>     Any Number,              !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     120.;                    !- Field 4
> 
> Schedule:Compact,
>     WORK_EFF_SCH,            !- Name
>     Fraction,                !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     0.0;                     !- Field 4
> 
> Schedule:Compact,
>     AIR_VELO_SCH,            !- Name
>     Any Number,              !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     0.2;                     !- Field 4
> 
> Schedule:Compact,
>     CLOTHING_SCH,            !- Name
>     Any Number,              !- Schedule Type Limits Name
>     Through: 04/30,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     1.0,                     !- Field 4
>     Through: 09/30,          !- Field 5
>     For: AllDays,            !- Field 6
>     Until: 24:00,            !- Field 7
>     0.5,                     !- Field 8
>     Through: 12/31,          !- Field 9
>     For: AllDays,            !- Field 10
>     Until: 24:00,            !- Field 11
>     1.0;                     !- Field 12
> 
> Schedule:Compact,
>     SHADING_SCH,             !- Name
>     Any Number,              !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Until: 24:00,            !- Field 3
>     0.0;                     !- Field 4
> 
> Schedule:Compact,
>     SkyTemp_SCH,             !- Name
>     Temperature,             !- Schedule Type Limits Name
>     Through: 12/31,          !- Field 1
>     For: AllDays,            !- Field 2
>     Interpolate: Yes,        !- Field 3
>     Until: 24:00,            !- Field 4
>      150;                    !- Field 5
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: MATERIAL ===========
> 
> Material,
>     Roof Membrane Black,     !- Name
>     VeryRough,               !- Roughness
>     0.0095,                  !- Thickness {m}
>     0.1600,                  !- Conductivity {W/m-K}
>     1121.2900,               !- Density {kg/m3}
>     1460.0000,               !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.934,                   !- Solar Absorptance
>     0.934;                   !- Visible Absorptance
> 
> Material,
>     Roof Insulation [14],    !- Name
>     MediumRough,             !- Roughness
>     0.1673,                  !- Thickness {m}
>     0.0490,                  !- Conductivity {W/m-K}
>     265.0000,                !- Density {kg/m3}
>     836.8000,                !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.7000,                  !- Solar Absorptance
>     0.7000;                  !- Visible Absorptance
> 
> Material,
>     Metal Decking,           !- Name
>     MediumSmooth,            !- Roughness
>     0.0015,                  !- Thickness {m}
>     45.0060,                 !- Conductivity {W/m-K}
>     7680.0000,               !- Density {kg/m3}
>     418.4000,                !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.7000,                  !- Solar Absorptance
>     0.3000;                  !- Visible Absorptance
> 
> Material,
>     GP01 1/2 GYPSUM,         !- Name
>     Smooth,                  !- Roughness
>     0.0127,                  !- Thickness {m}
>     0.1600,                  !- Conductivity {W/m-K}
>     800.0000,                !- Density {kg/m3}
>     1090.0000,               !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.7000,                  !- Solar Absorptance
>     0.5000;                  !- Visible Absorptance
> 
> Material,
>     Wall Insulation [10],    !- Name
>     MediumRough,             !- Roughness
>     0.0971,                  !- Thickness {m}
>     0.0450,                  !- Conductivity {W/m-K}
>     265.0000,                !- Density {kg/m3}
>     836.8000,                !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.7000,                  !- Solar Absorptance
>     0.7000;                  !- Visible Absorptance
> 
> Material,
>     1/2IN Gypsum,            !- Name
>     Smooth,                  !- Roughness
>     0.0127,                  !- Thickness {m}
>     0.1600,                  !- Conductivity {W/m-K}
>     784.9000,                !- Density {kg/m3}
>     830.0000,                !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.9200,                  !- Solar Absorptance
>     0.9200;                  !- Visible Absorptance
> 
> Material,
>     MAT-CC05 8 HW CONCRETE,  !- Name
>     Rough,                   !- Roughness
>     0.2032,                  !- Thickness {m}
>     1.3110,                  !- Conductivity {W/m-K}
>     2240.0000,               !- Density {kg/m3}
>     836.8000,                !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.7000,                  !- Solar Absorptance
>     0.7000;                  !- Visible Absorptance
> 
> Material,
>     Floor Insulation [2],    !- Name
>     MediumRough,             !- Roughness
>     0.0636,                  !- Thickness {m}
>     0.0450,                  !- Conductivity {W/m-K}
>     265.0000,                !- Density {kg/m3}
>     836.8000,                !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.7000,                  !- Solar Absorptance
>     0.7000;                  !- Visible Absorptance
> 
> Material,
>     METAL Door Medium 18Ga_1,!- Name
>     Smooth,                  !- Roughness
>     0.0013,                  !- Thickness {m}
>     45.3149,                 !- Conductivity {W/m-K}
>     7833.0300,               !- Density {kg/m3}
>     502.0800,                !- Specific Heat {J/kg-K}
>     0.8000,                  !- Thermal Absorptance
>     0.5000,                  !- Solar Absorptance
>     0.5000;                  !- Visible Absorptance
> 
> Material,
>     METAL Door Medium 18Ga_2,!- Name
>     Smooth,                  !- Roughness
>     0.0013,                  !- Thickness {m}
>     45.3149,                 !- Conductivity {W/m-K}
>     7833.0300,               !- Density {kg/m3}
>     502.0800,                !- Specific Heat {J/kg-K}
>     0.8000,                  !- Thermal Absorptance
>     0.5000,                  !- Solar Absorptance
>     0.5000;                  !- Visible Absorptance
> 
> Material,
>     METAL Door Medium 18Ga,  !- Name
>     Smooth,                  !- Roughness
>     0.0013,                  !- Thickness {m}
>     45.3149,                 !- Conductivity {W/m-K}
>     7833.0300,               !- Density {kg/m3}
>     502.0800,                !- Specific Heat {J/kg-K}
>     0.8000,                  !- Thermal Absorptance
>     0.5000,                  !- Solar Absorptance
>     0.5000;                  !- Visible Absorptance
> 
> Material,
>     Std Wood 6inch,          !- Name
>     MediumSmooth,            !- Roughness
>     0.15,                    !- Thickness {m}
>     0.12,                    !- Conductivity {W/m-K}
>     540.0000,                !- Density {kg/m3}
>     1210,                    !- Specific Heat {J/kg-K}
>     0.9000000,               !- Thermal Absorptance
>     0.7000000,               !- Solar Absorptance
>     0.7000000;               !- Visible Absorptance
> 
> Material,
>     Std 1.5  MW CONCRETE,    !- Name
>     Rough,                   !- Roughness
>     0.038,                   !- Thickness {m}
>     0.858,                   !- Conductivity {W/m-K}
>     1968,                    !- Density {kg/m3}
>     836.8,                   !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.7;                     !- Visible Absorptance
> 
> Material,
>     Std AC02,                !- Name
>     MediumSmooth,            !- Roughness
>     1.2700000E-02,           !- Thickness {m}
>     5.7000000E-02,           !- Conductivity {W/m-K}
>     288.0000,                !- Density {kg/m3}
>     1339.000,                !- Specific Heat {J/kg-K}
>     0.9000000,               !- Thermal Absorptance
>     0.7000000,               !- Solar Absorptance
>     0.2000000;               !- Visible Absorptance
> 
> Material,
>     Std MAT-CC05 4  MW CONCRETE,  !- Name
>     Rough,                   !- Roughness
>     0.1000,                  !- Thickness {m}
>     0.858,                   !- Conductivity {W/m-K}
>     1968,                    !- Density {kg/m3}
>     836.8,                   !- Specific Heat {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.2;                     !- Visible Absorptance
> 
> Material,
>     Std Very High Reflectivity Surface,  !- Name
>     Smooth,                  !- Roughness
>     0.0005,                  !- Thickness {m}
>     237,                     !- Conductivity {W/m-K}
>     2702,                    !- Density {kg/m3}
>     903,                     !- Specific Heat {J/kg-K}
>     0.90,                    !- Thermal Absorptance
>     0.05,                    !- Solar Absorptance
>     0.05;                    !- Visible Absorptance
> 
> Material,
>     Std PW05,                !- Name
>     MediumSmooth,            !- Roughness
>     1.9099999E-02,           !- Thickness {m}
>     0.1150000,               !- Conductivity {W/m-K}
>     545.0000,                !- Density {kg/m3}
>     1213.000,                !- Specific Heat {J/kg-K}
>     0.9000000,               !- Thermal Absorptance
>     0.7800000,               !- Solar Absorptance
>     0.7800000;               !- Visible Absorptance
> 
> Material,
>     Std Steel_Brown_Regular, !- Name
>     Smooth,                  !- Roughness
>     1.5000000E-03,           !- Thickness {m}
>     44.96960,                !- Conductivity {W/m-K}
>     7689.000,                !- Density {kg/m3}
>     418.0000,                !- Specific Heat {J/kg-K}
>     0.9000000,               !- Thermal Absorptance
>     0.9200000,               !- Solar Absorptance
>     0.92000000;              !- Visible Absorptance
> 
> Material,
>     Std Steel_Brown_Cool,    !- Name
>     Smooth,                  !- Roughness
>     1.5000000E-03,           !- Thickness {m}
>     44.96960,                !- Conductivity {W/m-K}
>     7689.000,                !- Density {kg/m3}
>     418.0000,                !- Specific Heat {J/kg-K}
>     0.9000000,               !- Thermal Absorptance
>     0.7300000,               !- Solar Absorptance
>     0.73000000;              !- Visible Absorptance
> 
> Material,
>     PW05_Plywood3/4_in,      !- Name
>     MediumSmooth,            !- Roughness
>     0.0191,                  !- Thickness {m}
>     0.1150,                  !- Conductivity {W/m-K}
>     545.0000,                !- Density {kg/m3}
>     1213.0000,               !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.7000,                  !- Solar Absorptance
>     0.7800;                  !- Visible Absorptance
> 
> Material,
>     Roof Membrane Gray,      !- Name
>     VeryRough,               !- Roughness
>     0.0095,                  !- Thickness {m}
>     0.1600,                  !- Conductivity {W/m-K}
>     1121.2900,               !- Density {kg/m3}
>     1460.0000,               !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.66,                    !- Solar Absorptance
>     0.66;                    !- Visible Absorptance
> 
> Material,
>     Roof Membrane White,     !- Name
>     VeryRough,               !- Roughness
>     0.0095,                  !- Thickness {m}
>     0.1600,                  !- Conductivity {W/m-K}
>     1121.2900,               !- Density {kg/m3}
>     1460.0000,               !- Specific Heat {J/kg-K}
>     0.9000,                  !- Thermal Absorptance
>     0.42,                    !- Solar Absorptance
>     0.42;                    !- Visible Absorptance
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: MATERIAL:NOMASS ===========
> 
> Material:NoMass,
>     MAT-SHEATH,              !- Name
>     Rough,                   !- Roughness
>     0.3626,                  !- Thermal Resistance {m2-K/W}
>     0.9000,                  !- Thermal Absorptance
>     0.7000,                  !- Solar Absorptance
>     0.7000;                  !- Visible Absorptance
> 
> Material:NoMass,
>     CP02 CARPET PAD,         !- Name
>     VeryRough,               !- Roughness
>     0.2165,                  !- Thermal Resistance {m2-K/W}
>     0.9000,                  !- Thermal Absorptance
>     0.7000,                  !- Solar Absorptance
>     0.8000;                  !- Visible Absorptance
> 
> Material:NoMass,
>     AIR,                     !- Name
>     Smooth,                  !- Roughness
>     0.2515,                  !- Thermal Resistance {m2-K/W}
>     0.8000,                  !- Thermal Absorptance
>     0.5000,                  !- Solar Absorptance
>     0.5000;                  !- Visible Absorptance
> 
> Material:NoMass,
>     AIR [3],                 !- Name
>     Smooth,                  !- Roughness
>     0.1134,                  !- Thermal Resistance {m2-K/W}
>     0.8000,                  !- Thermal Absorptance
>     0.5000,                  !- Solar Absorptance
>     0.5000;                  !- Visible Absorptance
> 
> Material:NoMass,
>     Std CP02 CARPET PAD,     !- Name
>     VeryRough,               !- Roughness
>     0.21648,                 !- Thermal Resistance {m2-K/W}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.8;                     !- Visible Absorptance
> 
> Material:NoMass,
>     MAT-AIR-WALL,            !- Name
>     Rough,                   !- Roughness
>     0.2079491,               !- Thermal Resistance {m2-K/W}
>     0.9,                     !- Thermal Absorptance
>     0.7;                     !- Solar Absorptance
> 
> Material:NoMass,
>     Std Opaque Door panel_con,  !- Name
>     MediumRough,             !- Roughness
>     0.12327,                 !- Thermal Resistance {m2-K/W}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.7;                     !- Visible Absorptance
> 
> Material:NoMass,
>     Std Opaque Door panel_semi,  !- Name
>     MediumRough,             !- Roughness
>     0.12327,                 !- Thermal Resistance {m2-K/W}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.7;                     !- Visible Absorptance
> 
> Material:NoMass,
>     Std Overhead Door Panel, !- Name
>     MediumRough,             !- Roughness
>     0.255345,                !- Thermal Resistance {m2-K/W}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.7;                     !- Visible Absorptance
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: MATERIAL:ROOFVEGETATION
===========
> 
> Material:RoofVegetation,
>     Ecoroof,                 !- Name
>     0.2,                     !- Height of Plants {m}
>     5,                       !- Leaf Area Index {dimensionless}
>     0.22,                    !- Leaf Reflectivity {dimensionless}
>     0.95,                    !- Leaf Emissivity
>     180,                     !- Minimum Stomatal Resistance {s/m}
>     Ecoroof Soil,            !- Soil Layer Name
>     VeryRough,               !- Roughness
>     0.15,                    !- Thickness {m}
>     0.4,                     !- Conductivity of Dry Soil {W/m-K}
>     500,                     !- Density of Dry Soil {kg/m3}
>     1000,                    !- Specific Heat of Dry Soil {J/kg-K}
>     0.9,                     !- Thermal Absorptance
>     0.7,                     !- Solar Absorptance
>     0.75,                    !- Visible Absorptance
>     0.5,                     !- Saturation Volumetric Moisture Content
of
>     the Soil Layer
>     0.01,                    !- Residual Volumetric Moisture Content of
>     the Soil Layer
>     0.15;                    !- Initial Volumetric Moisture Content of
the
>     Soil Layer
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: WINDOWMATERIAL:GLAZING
===========
> 
> WindowMaterial:Glazing,
>     Theoretical Glass [182], !- Name
>     SpectralAverage,         !- Optical Data Type
>     ,                        !- Window Glass Spectral Data Set Name
>     0.0030,                  !- Thickness {m}
>     0.3933,                  !- Solar Transmittance at Normal Incidence
>     0.5567,                  !- Front Side Solar Reflectance at Normal
>     Incidence
>     0.5567,                  !- Back Side Solar Reflectance at Normal
>     Incidence
>     0.5079,                  !- Visible Transmittance at Normal
Incidence
>     0.4421,                  !- Front Side Visible Reflectance at Normal
>     Incidence
>     0.4421,                  !- Back Side Visible Reflectance at Normal
>     Incidence
>     0.0000,                  !- Infrared Transmittance at Normal
Incidence
>     0.9000,                  !- Front Side Infrared Hemispherical
>     Emissivity
>     0.9000,                  !- Back Side Infrared Hemispherical
Emissivity
>     0.0185,                  !- Conductivity {W/m-K}
>     1.0000,                  !- Dirt Correction Factor for Solar and
>     Visible Transmittance
>     No;                      !- Solar Diffusing
> 
> WindowMaterial:Glazing,
>     Theoretical Glass [146], !- Name
>     SpectralAverage,         !- Optical Data Type
>     ,                        !- Window Glass Spectral Data Set Name
>     0.0030,                  !- Thickness {m}
>     0.4818,                  !- Solar Transmittance at Normal Incidence
>     0.4682,                  !- Front Side Solar Reflectance at Normal
>     Incidence
>     0.4682,                  !- Back Side Solar Reflectance at Normal
>     Incidence
>     0.6216,                  !- Visible Transmittance at Normal
Incidence
>     0.3284,                  !- Front Side Visible Reflectance at Normal
>     Incidence
>     0.3284,                  !- Back Side Visible Reflectance at Normal
>     Incidence
>     0.0000,                  !- Infrared Transmittance at Normal
Incidence
>     0.9000,                  !- Front Side Infrared Hemispherical
>     Emissivity
>     0.9000,                  !- Back Side Infrared Hemispherical
Emissivity
>     0.0303,                  !- Conductivity {W/m-K}
>     1.0000,                  !- Dirt Correction Factor for Solar and
>     Visible Transmittance
>     No;                      !- Solar Diffusing
> 
> WindowMaterial:Glazing,
>     Std Clear Acrylic Plastic,  !- Name
>     SpectralAverage,         !- Optical Data Type
>     ,                        !- Window Glass Spectral Data Set Name
>     0.003,                   !- Thickness {m}
>     0.92,                    !- Solar Transmittance at Normal Incidence
>     0.05,                    !- Front Side Solar Reflectance at Normal
>     Incidence
>     0.05,                    !- Back Side Solar Reflectance at Normal
>     Incidence
>     0.92,                    !- Visible Transmittance at Normal
Incidence
>     0.05,                    !- Front Side Visible Reflectance at Normal
>     Incidence
>     0.05,                    !- Back Side Visible Reflectance at Normal
>     Incidence
>     0.00,                    !- Infrared Transmittance at Normal
Incidence
>     0.90,                    !- Front Side Infrared Hemispherical
>     Emissivity
>     0.90,                    !- Back Side Infrared Hemispherical
Emissivity
>     0.90;                    !- Conductivity {W/m-K}
> 
> WindowMaterial:Glazing,
>     Std Diffusing Acrylic Plastic,  !- Name
>     SpectralAverage,         !- Optical Data Type
>     ,                        !- Window Glass Spectral Data Set Name
>     0.0022,                  !- Thickness {m}
>     0.90,                    !- Solar Transmittance at Normal Incidence
>     0.08,                    !- Front Side Solar Reflectance at Normal
>     Incidence
>     0.08,                    !- Back Side Solar Reflectance at Normal
>     Incidence
>     0.90,                    !- Visible Transmittance at Normal
Incidence
>     0.08,                    !- Front Side Visible Reflectance at Normal
>     Incidence
>     0.08,                    !- Back Side Visible Reflectance at Normal
>     Incidence
>     0.00,                    !- Infrared Transmittance at Normal
Incidence
>     0.90,                    !- Front Side Infrared Hemispherical
>     Emissivity
>     0.90,                    !- Back Side Infrared Hemispherical
Emissivity
>     0.90;                    !- Conductivity {W/m-K}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONSTRUCTION ===========
> 
> Construction,
>     InteriorFurnishings,     !- Name
>     Std Wood 6inch;          !- Outside Layer
> 
> Construction,
>     INT-FLOOR-TOPSIDE,       !- Name
>     Std MAT-CC05 4  MW CONCRETE,  !- Outside Layer
>     Std CP02 CARPET PAD;     !- Layer 2
> 
> Construction,
>     INT-FLOOR-UNDERSIDE,     !- Name
>     Std CP02 CARPET PAD,     !- Outside Layer
>     Std MAT-CC05 4  MW CONCRETE;  !- Layer 2
> 
> Construction,
>     INT-FLOOR-SLAB,          !- Name
>     Std MAT-CC05 4  MW CONCRETE;  !- Outside Layer
> 
> Construction,
>     DropCeiling,             !- Name
>     Std AC02;                !- Outside Layer
> 
> Construction,
>     INT-CEILING_SIMPLE,      !- Name
>     PW05_Plywood3/4_in;      !- Outside Layer
> 
> Construction,
>     Raised-Floor-TopSide,    !- Name
>     Std 1.5  MW CONCRETE,    !- Outside Layer
>     Std CP02 CARPET PAD;     !- Layer 2
> 
> Construction,
>     Raised-Floor-UnderSide,  !- Name
>     Std CP02 CARPET PAD,     !- Outside Layer
>     Std 1.5  MW CONCRETE;    !- Layer 2
> 
> Construction,
>     TDD_Pipe,                !- Name
>     Std Very High Reflectivity Surface;  !- Outside Layer
> 
> Construction,
>     TDD_Dome,                !- Name
>     Std Clear Acrylic Plastic;  !- Outside Layer
> 
> Construction,
>     TDD_Diffuser,            !- Name
>     Std Diffusing Acrylic Plastic;  !- Outside Layer
> 
> Construction,
>     Sloped_Metal_Roof,       !- Name
>     Std Steel_Brown_Regular, !- Outside Layer
>     Std PW05;                !- Layer 2
> 
> Construction,
>     Gable_Wall,              !- Name
>     Std PW05;                !- Outside Layer
> 
> Construction,
>     AIR-WALL,                !- Name
>     MAT-AIR-WALL;            !- Outside Layer
> 
> Construction,
>     Std Swinging Door_con,   !- Name
>     Std Opaque Door panel_con;  !- Outside Layer
> 
> Construction,
>     Std Swinging Door_semi,  !- Name
>     Std Opaque Door panel_semi;  !- Outside Layer
> 
> Construction,
>     Std Overhead Door,       !- Name
>     Std Overhead Door Panel; !- Outside Layer
> 
> Construction,
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508,  !- Name
>     Theoretical Glass [182]; !- Outside Layer
> 
> Construction,
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_east,  !- Name
>     Theoretical Glass [182]; !- Outside Layer
> 
> Construction,
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_north,  !- Name
>     Theoretical Glass [182]; !- Outside Layer
> 
> Construction,
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_west,  !- Name
>     Theoretical Glass [182]; !- Outside Layer
> 
> Construction,
>     std_window_UValue_3.919_SHGC_0.49_VT_0.622,  !- Name
>     Theoretical Glass [146]; !- Outside Layer
> 
> Construction,
>     Roof Construction,       !- Name
>     Roof Membrane Black,     !- Outside Layer
>     Roof Insulation [14],    !- Layer 2
>     Metal Decking;           !- Layer 3
> 
> Construction,
>     Standard_Int-Wall,       !- Name
>     GP01 1/2 GYPSUM,         !- Outside Layer
>     GP01 1/2 GYPSUM;         !- Layer 2
> 
> Construction,
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Name
>     MAT-SHEATH,              !- Outside Layer
>     Wall Insulation [10],    !- Layer 2
>     1/2IN Gypsum;            !- Layer 3
> 
> Construction,
>     Unheated - 8in Slab with Carpet_Ext-slab,  !- Name
>     MAT-CC05 8 HW CONCRETE,  !- Outside Layer
>     CP02 CARPET PAD;         !- Layer 2
> 
> Construction,
>     Mass_R-8.3 ci_ExposedFloor,  !- Name
>     Floor Insulation [2],    !- Outside Layer
>     MAT-CC05 8 HW CONCRETE,  !- Layer 2
>     CP02 CARPET PAD;         !- Layer 3
> 
> Construction,
>     Swinging_door,           !- Name
>     METAL Door Medium 18Ga_1,!- Outside Layer
>     AIR,                     !- Layer 2
>     METAL Door Medium 18Ga_2;!- Layer 3
> 
> Construction,
>     Non-Swinging_NR_door,    !- Name
>     METAL Door Medium 18Ga,  !- Outside Layer
>     AIR [3],                 !- Layer 2
>     METAL Door Medium 18Ga_2;!- Layer 3
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: GLOBALGEOMETRYRULES ===========
> 
> GlobalGeometryRules,
>     UpperLeftCorner,         !- Starting Vertex Position
>     Counterclockwise,        !- Vertex Entry Direction
>     Relative,                !- Coordinate System
>     Relative,                !- Daylighting Reference Point Coordinate
>     System
>     Relative;                !- Rectangular Surface Coordinate System
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONE ===========
> 
> Zone,
>     ZN_1_FLR_1_SEC_1,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     0.0000,                  !- X Origin {m}
>     0.0000,                  !- Y Origin {m}
>     0.0000,                  !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     411.8220,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_2_SEC_1,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     0.0000,                  !- X Origin {m}
>     0.0000,                  !- Y Origin {m}
>     7.6000,                  !- Z Origin {m}
>     1,                       !- Type
>     3,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     411.8220,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_3_SEC_1,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     0.0000,                  !- X Origin {m}
>     0.0000,                  !- Y Origin {m}
>     15.2000,                 !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     411.8220,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_1_SEC_2,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     28.2843,                 !- X Origin {m}
>     0.0000,                  !- Y Origin {m}
>     0.0000,                  !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     166.2297,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_2_SEC_2,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     28.2843,                 !- X Origin {m}
>     0.0000,                  !- Y Origin {m}
>     7.6000,                  !- Z Origin {m}
>     1,                       !- Type
>     3,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     166.2297,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_3_SEC_2,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     28.2843,                 !- X Origin {m}
>     0.0000,                  !- Y Origin {m}
>     15.2000,                 !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     166.2297,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_1_SEC_3,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     4.5700,                  !- X Origin {m}
>     9.5721,                  !- Y Origin {m}
>     0.0000,                  !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     411.8220,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_2_SEC_3,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     4.5700,                  !- X Origin {m}
>     9.5721,                  !- Y Origin {m}
>     7.6000,                  !- Z Origin {m}
>     1,                       !- Type
>     3,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     411.8220,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_3_SEC_3,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     4.5700,                  !- X Origin {m}
>     9.5721,                  !- Y Origin {m}
>     15.2000,                 !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     411.8220,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_1_SEC_4,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     0.0000,                  !- X Origin {m}
>     0.0000,                  !- Y Origin {m}
>     0.0000,                  !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     166.2297,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_2_SEC_4,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     0.0000,                  !- X Origin {m}
>     0.0000,                  !- Y Origin {m}
>     7.6000,                  !- Z Origin {m}
>     1,                       !- Type
>     3,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     166.2297,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_3_SEC_4,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     0.0000,                  !- X Origin {m}
>     0.0000,                  !- Y Origin {m}
>     15.2000,                 !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     166.2297,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_1_SEC_5,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     4.5700,                  !- X Origin {m}
>     4.5700,                  !- Y Origin {m}
>     0.0000,                  !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     363.8965,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_2_SEC_5,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     4.5700,                  !- X Origin {m}
>     4.5700,                  !- Y Origin {m}
>     7.6000,                  !- Z Origin {m}
>     1,                       !- Type
>     3,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     363.8965,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> Zone,
>     ZN_1_FLR_3_SEC_5,        !- Name
>     0.0000,                  !- Direction of Relative North {deg}
>     4.5700,                  !- X Origin {m}
>     4.5700,                  !- Y Origin {m}
>     15.2000,                 !- Z Origin {m}
>     1,                       !- Type
>     1,                       !- Multiplier
>     3.8000,                  !- Ceiling Height {m}
>     363.8965,                !- Volume {m3}
>     ,                        !- Zone Inside Convection Algorithm
>     ,                        !- Zone Outside Convection Algorithm
>     Yes;                     !- Part of Total Floor Area
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BUILDINGSURFACE:DETAILED
> ===========
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_1_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     28.284300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     28.284300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_1_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_2_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     28.284300000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     28.284300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     23.714300000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     23.714300000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_1_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_5_Wall_1, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     23.714300000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_1_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_4_Wall_1, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_1_Floor,  !- Name
>     Floor,                   !- Surface Type
>     Unheated - 8in Slab with Carpet_Ext-slab,  !- Construction Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     Ground,                  !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     28.284300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_1_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_1_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     28.284300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     23.714300000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_1_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     28.284300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     28.284300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_1_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_2_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     28.284300000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     28.284300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     23.714300000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     23.714300000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_1_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_5_Wall_1, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     23.714300000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_1_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_4_Wall_1, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_1_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_1_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     28.284300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_1_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_1_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     28.284300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     23.714300000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_1_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     28.284300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     28.284300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_1_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_2_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     28.284300000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     28.284300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     23.714300000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     23.714300000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_1_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_5_Wall_1, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     23.714300000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_1_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_4_Wall_1, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_1_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_1_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     28.284300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     Roof Section 1,          !- Name
>     Roof,                    !- Surface Type
>     Roof Construction,       !- Construction Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     28.284300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     23.714300000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_2_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     14.142100000000,         !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_2_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_3_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     14.142100000000,         !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     9.572100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_2_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_5_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     9.572100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_2_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_1_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_2_Floor,  !- Name
>     Floor,                   !- Surface Type
>     Unheated - 8in Slab with Carpet_Ext-slab,  !- Construction Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     Ground,                  !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_2_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_2_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_2_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     14.142100000000,         !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_2_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_3_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     14.142100000000,         !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     9.572100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_2_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_5_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     9.572100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_2_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_1_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_2_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_2_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_2_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_2_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_2_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     14.142100000000,         !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_2_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_3_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     14.142100000000,         !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     9.572100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_2_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_5_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     9.572100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_2_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_1_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_2_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_2_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     Roof Section 2,          !- Name
>     Roof,                    !- Surface Type
>     Roof Construction,       !- Construction Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_3_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_5_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_3_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_2_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     23.714300000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     23.714300000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_3_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     23.714300000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_3_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_4_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_3_Floor,  !- Name
>     Floor,                   !- Surface Type
>     Unheated - 8in Slab with Carpet_Ext-slab,  !- Construction Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     Ground,                  !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_3_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_3_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     23.714300000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_3_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_5_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_3_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_2_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     23.714300000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     23.714300000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_3_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     23.714300000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_3_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_4_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_3_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_3_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_3_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_3_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     23.714300000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_3_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_5_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_3_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_2_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     23.714300000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     23.714300000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_3_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     23.714300000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_3_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_4_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_3_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_3_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     23.714300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.570000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     Roof Section 3,          !- Name
>     Roof,                    !- Surface Type
>     Roof Construction,       !- Construction Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     -4.570000000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     23.714300000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_4_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_1_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_4_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_5_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     9.572100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_4_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_3_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     9.572100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     14.142100000000,         !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_4_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     14.142100000000,         !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_4_Floor,  !- Name
>     Floor,                   !- Surface Type
>     Unheated - 8in Slab with Carpet_Ext-slab,  !- Construction Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     Ground,                  !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_4_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_4_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_4_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_1_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_4_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_5_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     9.572100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_4_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_3_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     9.572100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     14.142100000000,         !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_4_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     14.142100000000,         !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_4_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_4_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_4_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_4_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_4_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_1_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_4_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_5_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     9.572100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_4_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_3_Wall_4, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     9.572100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     14.142100000000,         !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_4_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Construction Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     14.142100000000,         !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_4_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_4_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     4.570000000000,          !- Vertex 1 X-coordinate {m}
>     9.572100000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     4.570000000000,          !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.142100000000,         !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     Roof Section 4,          !- Name
>     Roof,                    !- Surface Type
>     Roof Construction,       !- Construction Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.142100000000,         !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     4.570000000000,          !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     4.570000000000,          !- Vertex 4 X-coordinate {m}
>     9.572100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_5_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_1_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_5_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_2_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     5.002100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_5_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_3_Wall_1, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     5.002100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     5.002100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_5_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_4_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     5.002100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_5_Floor,  !- Name
>     Floor,                   !- Surface Type
>     Unheated - 8in Slab with Carpet_Ext-slab,  !- Construction Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     Ground,                  !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_1_SEC_5_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_1_SEC_5_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_5_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_1_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_5_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_2_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     5.002100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_5_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_3_Wall_1, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     5.002100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     5.002100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_5_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_4_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     5.002100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_5_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_5_Ceiling,!- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_2_SEC_5_Ceiling,!- Name
>     Ceiling,                 !- Surface Type
>     INT-FLOOR-UNDERSIDE,     !- Construction Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_2_SEC_5_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_5_Wall_1, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_1_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_5_Wall_2, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_2_Wall_3, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     5.002100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_5_Wall_3, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_3_Wall_1, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     5.002100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     5.002100000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_5_Wall_4, !- Name
>     Wall,                    !- Surface Type
>     Standard_Int-Wall,       !- Construction Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_4_Wall_2, !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     5.002100000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     ZN_1_FLR_3_SEC_5_Floor,  !- Name
>     Floor,                   !- Surface Type
>     INT-FLOOR-TOPSIDE,       !- Construction Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     Surface,                 !- Outside Boundary Condition
>     ZN_1_FLR_3_SEC_5_Floor,  !- Outside Boundary Condition Object
>     NoSun,                   !- Sun Exposure
>     NoWind,                  !- Wind Exposure
>     AutoCalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     19.144300000000,         !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     0.000000000000,          !- Vertex 1 Z-coordinate {m}
>     19.144300000000,         !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     0.000000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     0.000000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     0.000000000000;          !- Vertex 4 Z-coordinate {m}
> 
> BuildingSurface:Detailed,
>     Roof,                    !- Name
>     Roof,                    !- Surface Type
>     Roof Construction,       !- Construction Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     Outdoors,                !- Outside Boundary Condition
>     ,                        !- Outside Boundary Condition Object
>     SunExposed,              !- Sun Exposure
>     WindExposed,             !- Wind Exposure
>     autocalculate,           !- View Factor to Ground
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     5.002100000000,          !- Vertex 1 Y-coordinate {m}
>     3.800000000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     3.800000000000,          !- Vertex 2 Z-coordinate {m}
>     19.144300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     3.800000000000,          !- Vertex 3 Z-coordinate {m}
>     19.144300000000,         !- Vertex 4 X-coordinate {m}
>     5.002100000000,          !- Vertex 4 Y-coordinate {m}
>     3.800000000000;          !- Vertex 4 Z-coordinate {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: FENESTRATIONSURFACE:DETAILED
> ===========
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_1_SEC_1_Wall_1_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508,  !- Construction Name
>     ZN_1_FLR_1_SEC_1_Wall_1, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     0.050000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     2.625400000000,          !- Vertex 1 Z-coordinate {m}
>     0.050000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     28.234300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     28.234300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     2.625400000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_2_SEC_1_Wall_1_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508,  !- Construction Name
>     ZN_1_FLR_2_SEC_1_Wall_1, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     0.050000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     2.625400000000,          !- Vertex 1 Z-coordinate {m}
>     0.050000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     28.234300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     28.234300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     2.625400000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_3_SEC_1_Wall_1_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508,  !- Construction Name
>     ZN_1_FLR_3_SEC_1_Wall_1, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     0.050000000000,          !- Vertex 1 X-coordinate {m}
>     0.000000000000,          !- Vertex 1 Y-coordinate {m}
>     2.625400000000,          !- Vertex 1 Z-coordinate {m}
>     0.050000000000,          !- Vertex 2 X-coordinate {m}
>     0.000000000000,          !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     28.234300000000,         !- Vertex 3 X-coordinate {m}
>     0.000000000000,          !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     28.234300000000,         !- Vertex 4 X-coordinate {m}
>     0.000000000000,          !- Vertex 4 Y-coordinate {m}
>     2.625400000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_1_SEC_2_Wall_1_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_east,  !- Construction
Name
>     ZN_1_FLR_1_SEC_2_Wall_1, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.050000000000,          !- Vertex 1 Y-coordinate {m}
>     2.630800000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.050000000000,          !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     14.092100000000,         !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.092100000000,         !- Vertex 4 Y-coordinate {m}
>     2.630800000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_2_SEC_2_Wall_1_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_east,  !- Construction
Name
>     ZN_1_FLR_2_SEC_2_Wall_1, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.050000000000,          !- Vertex 1 Y-coordinate {m}
>     2.630800000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.050000000000,          !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     14.092100000000,         !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.092100000000,         !- Vertex 4 Y-coordinate {m}
>     2.630800000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_3_SEC_2_Wall_1_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_east,  !- Construction
Name
>     ZN_1_FLR_3_SEC_2_Wall_1, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     0.050000000000,          !- Vertex 1 Y-coordinate {m}
>     2.630800000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     0.050000000000,          !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     14.092100000000,         !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     14.092100000000,         !- Vertex 4 Y-coordinate {m}
>     2.630800000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_1_SEC_3_Wall_3_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_north,  !- Construction
Name
>     ZN_1_FLR_1_SEC_3_Wall_3, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     23.664300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     2.625400000000,          !- Vertex 1 Z-coordinate {m}
>     23.664300000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.520000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.520000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     2.625400000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_2_SEC_3_Wall_3_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_north,  !- Construction
Name
>     ZN_1_FLR_2_SEC_3_Wall_3, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     23.664300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     2.625400000000,          !- Vertex 1 Z-coordinate {m}
>     23.664300000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.520000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.520000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     2.625400000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_3_SEC_3_Wall_3_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_north,  !- Construction
Name
>     ZN_1_FLR_3_SEC_3_Wall_3, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     23.664300000000,         !- Vertex 1 X-coordinate {m}
>     4.570000000000,          !- Vertex 1 Y-coordinate {m}
>     2.625400000000,          !- Vertex 1 Z-coordinate {m}
>     23.664300000000,         !- Vertex 2 X-coordinate {m}
>     4.570000000000,          !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     -4.520000000000,         !- Vertex 3 X-coordinate {m}
>     4.570000000000,          !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     -4.520000000000,         !- Vertex 4 X-coordinate {m}
>     4.570000000000,          !- Vertex 4 Y-coordinate {m}
>     2.625400000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_1_SEC_4_Wall_4_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_west,  !- Construction
Name
>     ZN_1_FLR_1_SEC_4_Wall_4, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.092100000000,         !- Vertex 1 Y-coordinate {m}
>     2.630800000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     14.092100000000,         !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.050000000000,          !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.050000000000,          !- Vertex 4 Y-coordinate {m}
>     2.630800000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_2_SEC_4_Wall_4_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_west,  !- Construction
Name
>     ZN_1_FLR_2_SEC_4_Wall_4, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.092100000000,         !- Vertex 1 Y-coordinate {m}
>     2.630800000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     14.092100000000,         !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.050000000000,          !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.050000000000,          !- Vertex 4 Y-coordinate {m}
>     2.630800000000;          !- Vertex 4 Z-coordinate {m}
> 
> FenestrationSurface:Detailed,
>     ZN_1_FLR_3_SEC_4_Wall_4_window_1,  !- Name
>     Window,                  !- Surface Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_west,  !- Construction
Name
>     ZN_1_FLR_3_SEC_4_Wall_4, !- Building Surface Name
>     ,                        !- Outside Boundary Condition Object
>     AutoCalculate,           !- View Factor to Ground
>     ,                        !- Shading Control Name
>     ,                        !- Frame and Divider Name
>     1.0000,                  !- Multiplier
>     4,                       !- Number of Vertices
>     0.000000000000,          !- Vertex 1 X-coordinate {m}
>     14.092100000000,         !- Vertex 1 Y-coordinate {m}
>     2.630800000000,          !- Vertex 1 Z-coordinate {m}
>     0.000000000000,          !- Vertex 2 X-coordinate {m}
>     14.092100000000,         !- Vertex 2 Y-coordinate {m}
>     1.100000000000,          !- Vertex 2 Z-coordinate {m}
>     0.000000000000,          !- Vertex 3 X-coordinate {m}
>     0.050000000000,          !- Vertex 3 Y-coordinate {m}
>     1.100000000000,          !- Vertex 3 Z-coordinate {m}
>     0.000000000000,          !- Vertex 4 X-coordinate {m}
>     0.050000000000,          !- Vertex 4 Y-coordinate {m}
>     2.630800000000;          !- Vertex 4 Z-coordinate {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: INTERNALMASS ===========
> 
> InternalMass,
>     ZN_1_FLR_1_SEC_1 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     216.7484;                !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_2_SEC_1 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     216.7484;                !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_3_SEC_1 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     216.7484;                !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_1_SEC_2 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     87.4893;                 !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_2_SEC_2 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     87.4893;                 !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_3_SEC_2 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     87.4893;                 !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_1_SEC_3 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     216.7484;                !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_2_SEC_3 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     216.7484;                !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_3_SEC_3 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     216.7484;                !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_1_SEC_4 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     87.4893;                 !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_2_SEC_4 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     87.4893;                 !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_3_SEC_4 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     87.4893;                 !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_1_SEC_5 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     191.5245;                !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_2_SEC_5 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     191.5245;                !- Surface Area {m2}
> 
> InternalMass,
>     ZN_1_FLR_3_SEC_5 Internal Mass,  !- Name
>     InteriorFurnishings,     !- Construction Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     191.5245;                !- Surface Area {m2}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SHADING:SITE:DETAILED
===========
> 
> Shading:Site:Detailed,
>     Rooftop Shading 1,       !- Name
>     ,                        !- Transmittance Schedule Name
>     4,                       !- Number of Vertices
>     37.937588430941,         !- Vertex 1 X-coordinate {m}
>     19.961275956516,         !- Vertex 1 Y-coordinate {m}
>     21.341951493770,         !- Vertex 1 Z-coordinate {m}
>     37.937588430941,         !- Vertex 2 X-coordinate {m}
>     -7.171885496620,         !- Vertex 2 Y-coordinate {m}
>     21.341951493770,         !- Vertex 2 Z-coordinate {m}
>     -10.972411569059,        !- Vertex 3 X-coordinate {m}
>     -7.171885496620,         !- Vertex 3 Y-coordinate {m}
>     21.341951493770,         !- Vertex 3 Z-coordinate {m}
>     -10.972411569059,        !- Vertex 4 X-coordinate {m}
>     19.961275956516,         !- Vertex 4 Y-coordinate {m}
>     21.341951493770;         !- Vertex 4 Z-coordinate {m}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PEOPLE ===========
> 
> People,
>     ZN_1_FLR_1_SEC_1 People, !- Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     4.2374,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_2_SEC_1 People, !- Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     4.2374,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_3_SEC_1 People, !- Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     4.2374,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_1_SEC_2 People, !- Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     1.7104,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_2_SEC_2 People, !- Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     1.7104,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_3_SEC_2 People, !- Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     1.7104,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_1_SEC_3 People, !- Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     4.2374,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_2_SEC_3 People, !- Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     4.2374,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_3_SEC_3 People, !- Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     4.2374,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_1_SEC_4 People, !- Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     1.7104,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_2_SEC_4 People, !- Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     1.7104,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_3_SEC_4 People, !- Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     1.7104,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_1_SEC_5 People, !- Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     3.7443,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_2_SEC_5 People, !- Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     3.7443,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> People,
>     ZN_1_FLR_3_SEC_5 People, !- Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     BLDG_OCC_SCH,            !- Number of People Schedule Name
>     People,                  !- Number of People Calculation Method
>     3.7443,                  !- Number of People
>     ,                        !- People per Zone Floor Area {person/m2}
>     ,                        !- Zone Floor Area per Person {m2/person}
>     0.3000,                  !- Fraction Radiant
>     AUTOCALCULATE,           !- Sensible Heat Fraction
>     ACTIVITY_SCH,            !- Activity Level Schedule Name
>     No,                      !- Enable ASHRAE 55 Comfort Warnings
>     ZoneAveraged,            !- Mean Radiant Temperature Calculation
Type
>     ,                        !- Surface Name/Angle Factor List Name
>     WORK_EFF_SCH,            !- Work Efficiency Schedule Name
>     CLOTHING_SCH,            !- Clothing Insulation Schedule Name
>     AIR_VELO_SCH,            !- Air Velocity Schedule Name
>     FANGER;                  !- Thermal Comfort Model 1 Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: LIGHTS ===========
> 
> Lights,
>     ZN_1_FLR_1_SEC_1_Lights, !- Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     1166.1066,               !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_2_SEC_1_Lights, !- Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     1166.1066,               !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_3_SEC_1_Lights, !- Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     1166.1066,               !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_1_SEC_2_Lights, !- Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     470.6925,                !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_2_SEC_2_Lights, !- Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     470.6925,                !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_3_SEC_2_Lights, !- Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     470.6925,                !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_1_SEC_3_Lights, !- Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     1166.1066,               !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_2_SEC_3_Lights, !- Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     1166.1066,               !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_3_SEC_3_Lights, !- Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     1166.1066,               !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_1_SEC_4_Lights, !- Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     470.6925,                !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_2_SEC_4_Lights, !- Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     470.6925,                !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_3_SEC_4_Lights, !- Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     470.6925,                !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_1_SEC_5_Lights, !- Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     1030.4017,               !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_2_SEC_5_Lights, !- Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     1030.4017,               !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> Lights,
>     ZN_1_FLR_3_SEC_5_Lights, !- Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     BLDG_LIGHT_SCH,          !- Schedule Name
>     LightingLevel,           !- Design Level Calculation Method
>     1030.4017,               !- Lighting Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Return Air Fraction
>     0.7000,                  !- Fraction Radiant
>     0.2000,                  !- Fraction Visible
>     1.0000,                  !- Fraction Replaceable
>     General,                 !- End-Use Subcategory
>     No;                      !- Return Air Fraction Calculated from
Plenum
>     Temperature
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ELECTRICEQUIPMENT ===========
> 
> ElectricEquipment,
>     ZN_1_FLR_1_SEC_1_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     874.5800,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_2_SEC_1_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     874.5800,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_3_SEC_1_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     874.5800,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_1_SEC_2_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     353.0194,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_2_SEC_2_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     353.0194,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_3_SEC_2_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     353.0194,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_1_SEC_3_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     874.5800,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_2_SEC_3_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     874.5800,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_3_SEC_3_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     874.5800,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_1_SEC_4_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     353.0194,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_2_SEC_4_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     353.0194,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_3_SEC_4_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     353.0194,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_1_SEC_5_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     772.8013,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_2_SEC_5_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     772.8013,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> ElectricEquipment,
>     ZN_1_FLR_3_SEC_5_PlugMisc_Equip,  !- Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     BLDG_EQUIP_SCH,          !- Schedule Name
>     EquipmentLevel,          !- Design Level Calculation Method
>     772.8013,                !- Design Level {W}
>     ,                        !- Watts per Zone Floor Area {W/m2}
>     ,                        !- Watts per Person {W/person}
>     0.0000,                  !- Fraction Latent
>     0.5000,                  !- Fraction Radiant
>     0.0000,                  !- Fraction Lost
>     General;                 !- End-Use Subcategory
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONEINFILTRATION:DESIGNFLOWRATE
> ===========
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_1_SEC_1_Infiltration,  !- Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0343,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_2_SEC_1_Infiltration,  !- Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0343,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_3_SEC_1_Infiltration,  !- Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0343,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_1_SEC_2_Infiltration,  !- Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0139,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_2_SEC_2_Infiltration,  !- Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0139,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_3_SEC_2_Infiltration,  !- Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0139,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_1_SEC_3_Infiltration,  !- Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0343,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_2_SEC_3_Infiltration,  !- Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0343,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_3_SEC_3_Infiltration,  !- Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0343,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_1_SEC_4_Infiltration,  !- Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0139,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_2_SEC_4_Infiltration,  !- Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0139,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_3_SEC_4_Infiltration,  !- Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0139,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_1_SEC_5_Infiltration,  !- Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0303,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_2_SEC_5_Infiltration,  !- Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0303,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> ZoneInfiltration:DesignFlowRate,
>     ZN_1_FLR_3_SEC_5_Infiltration,  !- Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     INFIL_SCH,               !- Schedule Name
>     Flow/Zone,               !- Design Flow Rate Calculation Method
>     0.0303,                  !- Design Flow Rate {m3/s}
>     ,                        !- Flow per Zone Floor Area {m3/s-m2}
>     ,                        !- Flow per Exterior Surface Area {m3/s-m2}
>     ,                        !- Air Changes per Hour
>     1.0000,                  !- Constant Term Coefficient
>     0.0000,                  !- Temperature Term Coefficient
>     0.0000,                  !- Velocity Term Coefficient
>     0.0000;                  !- Velocity Squared Term Coefficient
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIZING:PARAMETERS ===========
> 
> Sizing:Parameters,
>     1.2,                     !- Sizing Factor
>     4;                       !- Timesteps in Averaging Window
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIZING:ZONE ===========
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_1_SEC_1 *****
> Sizing:Zone,
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0431058458462583,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_2_SEC_1 *****
> Sizing:Zone,
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0431058458462583,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_3_SEC_1 *****
> Sizing:Zone,
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0431058458462583,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_1_SEC_2 *****
> Sizing:Zone,
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0173994384356292,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_2_SEC_2 *****
> Sizing:Zone,
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0173994384356292,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_3_SEC_2 *****
> Sizing:Zone,
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0173994384356292,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_1_SEC_3 *****
> Sizing:Zone,
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0431058458462583,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_2_SEC_3 *****
> Sizing:Zone,
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0431058458462583,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_3_SEC_3 *****
> Sizing:Zone,
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0431058458462583,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_1_SEC_4 *****
> Sizing:Zone,
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0173994384356292,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_2_SEC_4 *****
> Sizing:Zone,
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0173994384356292,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_3_SEC_4 *****
> Sizing:Zone,
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.0173994384356292,      !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_1_SEC_5 *****
> Sizing:Zone,
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.038089431436225,       !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_2_SEC_5 *****
> Sizing:Zone,
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.038089431436225,       !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> !***** Space Conditioning For Zone: ZN_1_FLR_3_SEC_5 *****
> Sizing:Zone,
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     14.0000,                 !- Zone Cooling Design Supply Air
Temperature
>     {C}
>     40.0000,                 !- Zone Heating Design Supply Air
Temperature
>     {C}
>     0.0085,                  !- Zone Cooling Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     0.0080,                  !- Zone Heating Design Supply Air Humidity
>     Ratio {kg-H2O/kg-air}
>     Flow/Zone,               !- Outdoor Air Method
>     0.0,                     !- Outdoor Air Flow per Person {m3/s}
>     0.0,                     !- Outdoor Air Flow per Zone Floor Area
>     {m3/s-m2}
>     0.038089431436225,       !- Outdoor Air Flow per Zone {m3/s}
>     ,                        !- Zone Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     ,                        !- Cooling Design Air Flow Rate {m3/s}
>     ,                        !- Cooling Minimum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Cooling Minimum Air Flow {m3/s}
>     0.0,                     !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0,                     !- Heating Design Air Flow Rate {m3/s}
>     ,                        !- Heating Maximum Air Flow per Zone Floor
>     Area {m3/s-m2}
>     ,                        !- Heating Maximum Air Flow {m3/s}
>     ;                        !- Heating Maximum Air Flow Fraction
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIZING:SYSTEM ===========
> 
> Sizing:System,
>     PVAV_REHEAT_1,           !- AirLoop Name
>     Sensible,                !- Type of Load to Size On
>     AUTOSIZE,                !- Design Outdoor Air Flow Rate {m3/s}
>     0.3000,                  !- Minimum System Air Flow Ratio
>     7.0,                     !- Preheat Design Temperature {C}
>     0.008,                   !- Preheat Design Humidity Ratio
>     {kg-H2O/kg-Air}
>     12.8000,                 !- Precool Design Temperature {C}
>     0.008,                   !- Precool Design Humidity Ratio
>     {kg-H2O/kg-Air}
>     12.8000,                 !- Central Cooling Design Supply Air
>     Temperature {C}
>     16.7000,                 !- Central Heating Design Supply Air
>     Temperature {C}
>     NonCoincident,           !- Sizing Option
>     No,                      !- 100% Outdoor Air in Cooling
>     No,                      !- 100% Outdoor Air in Heating
>     0.0085,                  !- Central Cooling Design Supply Air
Humidity
>     Ratio {kg-H2O/kg-Air}
>     0.0080,                  !- Central Heating Design Supply Air
Humidity
>     Ratio {kg-H2O/kg-Air}
>     DesignDay,               !- Cooling Design Air Flow Method
>     0.0,                     !- Cooling Design Air Flow Rate {m3/s}
>     DesignDay,               !- Heating Design Air Flow Method
>     0.0;                     !- Heating Design Air Flow Rate {m3/s}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SIZING:PLANT ===========
> 
> Sizing:Plant,
>     HeatSys1,                !- Plant or Condenser Loop Name
>     Heating,                 !- Loop Type
>     82.2,                    !- Design Loop Exit Temperature {C}
>     11.1;                    !- Loop Design Temperature Difference
{deltaC}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT
===========
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_1_SEC_1 Thermostat,  !- Name
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_1_SEC_1 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_2_SEC_1 Thermostat,  !- Name
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_2_SEC_1 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_3_SEC_1 Thermostat,  !- Name
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_3_SEC_1 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_1_SEC_2 Thermostat,  !- Name
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_1_SEC_2 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_2_SEC_2 Thermostat,  !- Name
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_2_SEC_2 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_3_SEC_2 Thermostat,  !- Name
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_3_SEC_2 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_1_SEC_3 Thermostat,  !- Name
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_1_SEC_3 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_2_SEC_3 Thermostat,  !- Name
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_2_SEC_3 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_3_SEC_3 Thermostat,  !- Name
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_3_SEC_3 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_1_SEC_4 Thermostat,  !- Name
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_1_SEC_4 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_2_SEC_4 Thermostat,  !- Name
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_2_SEC_4 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_3_SEC_4 Thermostat,  !- Name
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_3_SEC_4 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_1_SEC_5 Thermostat,  !- Name
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_1_SEC_5 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_2_SEC_5 Thermostat,  !- Name
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_2_SEC_5 DualSPSched;  !- Control 1 Name
> 
> ZoneControl:Thermostat,
>     ZN_1_FLR_3_SEC_5 Thermostat,  !- Name
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     Dual Zone Control Type Sched,  !- Control Type Schedule Name
>     ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
>     ZN_1_FLR_3_SEC_5 DualSPSched;  !- Control 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:DUALSETPOINT
> ===========
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_1_SEC_1 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_2_SEC_1 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_3_SEC_1 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_1_SEC_2 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_2_SEC_2 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_3_SEC_2 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_1_SEC_3 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_2_SEC_3 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_3_SEC_3 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_1_SEC_4 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_2_SEC_4 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_3_SEC_4 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_1_SEC_5 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_2_SEC_5 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> ThermostatSetpoint:DualSetpoint,
>     ZN_1_FLR_3_SEC_5 DualSPSched,  !- Name
>     HTGSETP_SCH,             !- Heating Setpoint Temperature Schedule
Name
>     CLGSETP_SCH;             !- Cooling Setpoint Temperature Schedule
Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS:
AIRTERMINAL:SINGLEDUCT:VAV:REHEAT
> ===========
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_1_SEC_1 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_1_SEC_1 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_1_SEC_1 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_1_SEC_1 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_1_SEC_1 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_2_SEC_1 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_2_SEC_1 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_2_SEC_1 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_2_SEC_1 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_2_SEC_1 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_3_SEC_1 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_3_SEC_1 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_3_SEC_1 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_3_SEC_1 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_3_SEC_1 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_1_SEC_2 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_1_SEC_2 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_1_SEC_2 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_1_SEC_2 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_1_SEC_2 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_2_SEC_2 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_2_SEC_2 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_2_SEC_2 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_2_SEC_2 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_2_SEC_2 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_3_SEC_2 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_3_SEC_2 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_3_SEC_2 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_3_SEC_2 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_3_SEC_2 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_1_SEC_3 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_1_SEC_3 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_1_SEC_3 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_1_SEC_3 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_1_SEC_3 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_2_SEC_3 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_2_SEC_3 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_2_SEC_3 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_2_SEC_3 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_2_SEC_3 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_3_SEC_3 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_3_SEC_3 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_3_SEC_3 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_3_SEC_3 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_3_SEC_3 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_1_SEC_4 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_1_SEC_4 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_1_SEC_4 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_1_SEC_4 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_1_SEC_4 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_2_SEC_4 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_2_SEC_4 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_2_SEC_4 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_2_SEC_4 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_2_SEC_4 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_3_SEC_4 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_3_SEC_4 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_3_SEC_4 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_3_SEC_4 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_3_SEC_4 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_1_SEC_5 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_1_SEC_5 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_1_SEC_5 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_1_SEC_5 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_1_SEC_5 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_2_SEC_5 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_2_SEC_5 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_2_SEC_5 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_2_SEC_5 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_2_SEC_5 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> AirTerminal:SingleDuct:VAV:Reheat,
>     ZN_1_FLR_3_SEC_5 VAV Box Component,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     ZN_1_FLR_3_SEC_5 VAV Box Damper Node,  !- Damper Air Outlet Node
Name
>     ZN_1_FLR_3_SEC_5 VAV Box Inlet Node Name,  !- Air Inlet Node Name
>     AUTOSIZE,                !- Maximum Air Flow Rate {m3/s}
>     Constant,                !- Zone Minimum Air Flow Input Method
>     0.3000,                  !- Constant Minimum Air Flow Fraction
>     ,                        !- Fixed Minimum Air Flow Rate {m3/s}
>     ,                        !- Minimum Air Flow Fraction Schedule Name
>     Coil:Heating:Water,      !- Reheat Coil Object Type
>     ZN_1_FLR_3_SEC_5 VAV Box Reheat Coil,  !- Reheat Coil Name
>     AUTOSIZE,                !- Maximum Hot Water or Steam Flow Rate
{m3/s}
>     0.0,                     !- Minimum Hot Water or Steam Flow Rate
{m3/s}
>     ZN_1_FLR_3_SEC_5 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     0.001,                   !- Convergence Tolerance
>     Reverse;                 !- Damper Heating Action
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:AIRDISTRIBUTIONUNIT
> ===========
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_1_SEC_1 VAV Box,!- Name
>     ZN_1_FLR_1_SEC_1 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_1_SEC_1 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_2_SEC_1 VAV Box,!- Name
>     ZN_1_FLR_2_SEC_1 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_2_SEC_1 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_3_SEC_1 VAV Box,!- Name
>     ZN_1_FLR_3_SEC_1 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_3_SEC_1 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_1_SEC_2 VAV Box,!- Name
>     ZN_1_FLR_1_SEC_2 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_1_SEC_2 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_2_SEC_2 VAV Box,!- Name
>     ZN_1_FLR_2_SEC_2 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_2_SEC_2 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_3_SEC_2 VAV Box,!- Name
>     ZN_1_FLR_3_SEC_2 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_3_SEC_2 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_1_SEC_3 VAV Box,!- Name
>     ZN_1_FLR_1_SEC_3 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_1_SEC_3 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_2_SEC_3 VAV Box,!- Name
>     ZN_1_FLR_2_SEC_3 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_2_SEC_3 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_3_SEC_3 VAV Box,!- Name
>     ZN_1_FLR_3_SEC_3 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_3_SEC_3 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_1_SEC_4 VAV Box,!- Name
>     ZN_1_FLR_1_SEC_4 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_1_SEC_4 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_2_SEC_4 VAV Box,!- Name
>     ZN_1_FLR_2_SEC_4 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_2_SEC_4 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_3_SEC_4 VAV Box,!- Name
>     ZN_1_FLR_3_SEC_4 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_3_SEC_4 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_1_SEC_5 VAV Box,!- Name
>     ZN_1_FLR_1_SEC_5 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_1_SEC_5 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_2_SEC_5 VAV Box,!- Name
>     ZN_1_FLR_2_SEC_5 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_2_SEC_5 VAV Box Component;  !- Air Terminal Name
> 
> ZoneHVAC:AirDistributionUnit,
>     ZN_1_FLR_3_SEC_5 VAV Box,!- Name
>     ZN_1_FLR_3_SEC_5 VAV Box Outlet Node Name,  !- Air Distribution Unit
>     Outlet Node Name
>     AirTerminal:SingleDuct:VAV:Reheat,  !- Air Terminal Object Type
>     ZN_1_FLR_3_SEC_5 VAV Box Component;  !- Air Terminal Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST
===========
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_1_SEC_1 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_1_SEC_1 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_2_SEC_1 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_2_SEC_1 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_3_SEC_1 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_3_SEC_1 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_1_SEC_2 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_1_SEC_2 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_2_SEC_2 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_2_SEC_2 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_3_SEC_2 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_3_SEC_2 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_1_SEC_3 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_1_SEC_3 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_2_SEC_3 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_2_SEC_3 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_3_SEC_3 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_3_SEC_3 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_1_SEC_4 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_1_SEC_4 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_2_SEC_4 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_2_SEC_4 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_3_SEC_4 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_3_SEC_4 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_1_SEC_5 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_1_SEC_5 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_2_SEC_5 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_2_SEC_5 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> ZoneHVAC:EquipmentList,
>     ZN_1_FLR_3_SEC_5 Equipment,  !- Name
>     ZoneHVAC:AirDistributionUnit,  !- Zone Equipment 1 Object Type
>     ZN_1_FLR_3_SEC_5 VAV Box,!- Zone Equipment 1 Name
>     1,                       !- Zone Equipment 1 Cooling Sequence
>     1;                       !- Zone Equipment 1 Heating or No-Load
>     Sequence
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS
> ===========
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_1_SEC_1,        !- Zone Name
>     ZN_1_FLR_1_SEC_1 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_1_SEC_1 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_1_SEC_1 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_1_SEC_1 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_2_SEC_1,        !- Zone Name
>     ZN_1_FLR_2_SEC_1 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_2_SEC_1 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_2_SEC_1 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_2_SEC_1 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_3_SEC_1,        !- Zone Name
>     ZN_1_FLR_3_SEC_1 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_3_SEC_1 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_3_SEC_1 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_3_SEC_1 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_1_SEC_2,        !- Zone Name
>     ZN_1_FLR_1_SEC_2 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_1_SEC_2 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_1_SEC_2 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_1_SEC_2 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_2_SEC_2,        !- Zone Name
>     ZN_1_FLR_2_SEC_2 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_2_SEC_2 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_2_SEC_2 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_2_SEC_2 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_3_SEC_2,        !- Zone Name
>     ZN_1_FLR_3_SEC_2 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_3_SEC_2 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_3_SEC_2 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_3_SEC_2 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_1_SEC_3,        !- Zone Name
>     ZN_1_FLR_1_SEC_3 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_1_SEC_3 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_1_SEC_3 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_1_SEC_3 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_2_SEC_3,        !- Zone Name
>     ZN_1_FLR_2_SEC_3 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_2_SEC_3 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_2_SEC_3 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_2_SEC_3 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_3_SEC_3,        !- Zone Name
>     ZN_1_FLR_3_SEC_3 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_3_SEC_3 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_3_SEC_3 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_3_SEC_3 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_1_SEC_4,        !- Zone Name
>     ZN_1_FLR_1_SEC_4 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_1_SEC_4 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_1_SEC_4 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_1_SEC_4 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_2_SEC_4,        !- Zone Name
>     ZN_1_FLR_2_SEC_4 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_2_SEC_4 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_2_SEC_4 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_2_SEC_4 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_3_SEC_4,        !- Zone Name
>     ZN_1_FLR_3_SEC_4 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_3_SEC_4 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_3_SEC_4 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_3_SEC_4 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_1_SEC_5,        !- Zone Name
>     ZN_1_FLR_1_SEC_5 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_1_SEC_5 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_1_SEC_5 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_1_SEC_5 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_2_SEC_5,        !- Zone Name
>     ZN_1_FLR_2_SEC_5 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_2_SEC_5 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_2_SEC_5 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_2_SEC_5 Return Air Node Name;  !- Zone Return Air Node Name
> 
> ZoneHVAC:EquipmentConnections,
>     ZN_1_FLR_3_SEC_5,        !- Zone Name
>     ZN_1_FLR_3_SEC_5 Equipment,  !- Zone Conditioning Equipment List
Name
>     ZN_1_FLR_3_SEC_5 Inlet Nodes,  !- Zone Air Inlet Node or NodeList
Name
>     ,                        !- Zone Air Exhaust Node or NodeList Name
>     ZN_1_FLR_3_SEC_5 Air Node,  !- Zone Air Node Name
>     ZN_1_FLR_3_SEC_5 Return Air Node Name;  !- Zone Return Air Node Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: FAN:VARIABLEVOLUME ===========
> 
> Fan:VariableVolume,
>     PVAV_REHEAT_1_Fan,       !- Name
>     HVACOperationSchd,       !- Availability Schedule Name
>     0.253131,                !- Fan Efficiency
>     600,                     !- Pressure Rise {Pa}
>     AUTOSIZE,                !- Maximum Flow Rate {m3/s}
>     0.0000,                  !- Minimum Flow Rate {m3/s}
>     0.9300,                  !- Motor Efficiency
>     1.0,                     !- Motor In Airstream Fraction
>     0.0407598940,            !- Fan Coefficient 1
>     0.08804497,              !- Fan Coefficient 2
>     -0.072926120,            !- Fan Coefficient 3
>     0.9437398230,            !- Fan Coefficient 4
>     0,                       !- Fan Coefficient 5
>     PVAV_REHEAT_1_HeatC-PVAV_REHEAT_1_FanNode,  !- Air Inlet Node Name
>     PVAV_REHEAT_1 Supply Equipment Outlet Node,  !- Air Outlet Node Name
>     Fan Energy;              !- End-Use Subcategory
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: COIL:COOLING:DX:TWOSPEED
> ===========
> 
> Coil:Cooling:DX:TwoSpeed,
>     PVAV_REHEAT_1_CoolC DXCoil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- Rated High Speed Total Cooling Capacity
{W}
>     AUTOSIZE,                !- Rated High Speed Sensible Heat Ratio
>     4.23877,                 !- Rated High Speed COP
>     AUTOSIZE,                !- Rated High Speed Air Flow Rate {m3/s}
>     PVAV_REHEAT_1_OA-PVAV_REHEAT_1_CoolCNode,  !- Air Inlet Node Name
>     PVAV_REHEAT_1_CoolC-PVAV_REHEAT_1_HeatCNode,  !- Air Outlet Node
Name
>     PVAV_REHEAT_1_CoolCStandard10Ton_CapFT,  !- Total Cooling Capacity
>     Function of Temperature Curve Name
>     PVAV_REHEAT_1_CoolCStandard10Ton_CapFF,  !- Total Cooling Capacity
>     Function of Flow Fraction Curve Name
>     PVAV_REHEAT_1_CoolCStandard10Ton_EIRFT,  !- Energy Input Ratio
>     Function of Temperature Curve Name
>     PVAV_REHEAT_1_CoolCStandard10Ton_EIRFFF,  !- Energy Input Ratio
>     Function of Flow Fraction Curve Name
>     PVAV_REHEAT_1_CoolCStandard10Ton_PLR,  !- Part Load Fraction
>     Correlation Curve Name
>     AUTOSIZE,                !- Rated Low Speed Total Cooling Capacity
{W}
>     0.69,                    !- Rated Low Speed Sensible Heat Ratio
>     4.23877,                 !- Rated Low Speed COP
>     AUTOSIZE,                !- Rated Low Speed Air Flow Rate {m3/s}
>     PVAV_REHEAT_1_CoolCStandard10Ton_CapFT,  !- Low Speed Total Cooling
>     Capacity Function of Temperature Curve Name
>     PVAV_REHEAT_1_CoolCStandard10Ton_EIRFT,  !- Low Speed Energy Input
>     Ratio Function of Temperature Curve Name
>     PVAV_REHEAT_1_CoolC Cond OA node;  !- Condenser Air Inlet Node Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: COIL:HEATING:WATER ===========
> 
> Coil:Heating:Water,
>     ZN_1_FLR_1_SEC_1 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_1_SEC_1 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_1_SEC_1 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_1_SEC_1 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_1_SEC_1 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_2_SEC_1 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_2_SEC_1 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_2_SEC_1 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_2_SEC_1 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_2_SEC_1 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_3_SEC_1 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_3_SEC_1 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_3_SEC_1 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_3_SEC_1 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_3_SEC_1 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_1_SEC_2 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_1_SEC_2 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_1_SEC_2 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_1_SEC_2 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_1_SEC_2 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_2_SEC_2 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_2_SEC_2 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_2_SEC_2 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_2_SEC_2 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_2_SEC_2 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_3_SEC_2 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_3_SEC_2 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_3_SEC_2 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_3_SEC_2 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_3_SEC_2 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_1_SEC_3 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_1_SEC_3 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_1_SEC_3 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_1_SEC_3 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_1_SEC_3 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_2_SEC_3 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_2_SEC_3 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_2_SEC_3 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_2_SEC_3 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_2_SEC_3 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_3_SEC_3 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_3_SEC_3 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_3_SEC_3 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_3_SEC_3 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_3_SEC_3 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_1_SEC_4 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_1_SEC_4 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_1_SEC_4 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_1_SEC_4 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_1_SEC_4 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_2_SEC_4 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_2_SEC_4 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_2_SEC_4 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_2_SEC_4 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_2_SEC_4 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_3_SEC_4 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_3_SEC_4 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_3_SEC_4 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_3_SEC_4 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_3_SEC_4 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_1_SEC_5 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_1_SEC_5 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_1_SEC_5 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_1_SEC_5 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_1_SEC_5 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_2_SEC_5 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_2_SEC_5 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_2_SEC_5 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_2_SEC_5 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_2_SEC_5 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     ZN_1_FLR_3_SEC_5 VAV Box Reheat Coil,  !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     ZN_1_FLR_3_SEC_5 VAV Box Reheat CoilDemand Inlet Node,  !- Water
Inlet
>     Node Name
>     ZN_1_FLR_3_SEC_5 VAV Box Reheat CoilDemand Outlet Node,  !- Water
>     Outlet Node Name
>     ZN_1_FLR_3_SEC_5 VAV Box Damper Node,  !- Air Inlet Node Name
>     ZN_1_FLR_3_SEC_5 VAV Box Outlet Node Name,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> Coil:Heating:Water,
>     PVAV_REHEAT_1_HeatC,     !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     AUTOSIZE,                !- U-Factor Times Area Value {W/K}
>     AUTOSIZE,                !- Maximum Water Flow Rate {m3/s}
>     PVAV_REHEAT_1_HeatCDemand Inlet Node,  !- Water Inlet Node Name
>     PVAV_REHEAT_1_HeatCDemand Outlet Node,  !- Water Outlet Node Name
>     PVAV_REHEAT_1_CoolC-PVAV_REHEAT_1_HeatCNode,  !- Air Inlet Node Name
>     PVAV_REHEAT_1_HeatC-PVAV_REHEAT_1_FanNode,  !- Air Outlet Node Name
>     UFactorTimesAreaAndDesignWaterFlowRate,  !- Performance Input Method
>     AUTOSIZE,                !- Rated Capacity {W}
>     82.2,                    !- Rated Inlet Water Temperature {C}
>     16.6,                    !- Rated Inlet Air Temperature {C}
>     71.1,                    !- Rated Outlet Water Temperature {C}
>     32.2;                    !- Rated Outlet Air Temperature {C}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:UNITARYCOOLONLY
> ===========
> 
> AirLoopHVAC:UnitaryCoolOnly,
>     PVAV_REHEAT_1_CoolC,     !- Name
>     ALWAYS_ON,               !- Availability Schedule Name
>     PVAV_REHEAT_1_OA-PVAV_REHEAT_1_CoolCNode,  !- DX Cooling Coil System
>     Inlet Node Name
>     PVAV_REHEAT_1_CoolC-PVAV_REHEAT_1_HeatCNode,  !- DX Cooling Coil
>     System Outlet Node Name
>     PVAV_REHEAT_1_CoolC-PVAV_REHEAT_1_HeatCNode,  !- DX Cooling Coil
>     System Sensor Node Name
>     Coil:Cooling:DX:TwoSpeed,!- Cooling Coil Object Type
>     PVAV_REHEAT_1_CoolC DXCoil;  !- Cooling Coil Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONTROLLER:WATERCOIL ===========
> 
> Controller:WaterCoil,
>     PVAV_REHEAT_1_HeatC_Controller,  !- Name
>     Temperature,             !- Control Variable
>     Normal,                  !- Action
>     Flow,                    !- Actuator Variable
>     PVAV_REHEAT_1_HeatC-PVAV_REHEAT_1_FanNode,  !- Sensor Node Name
>     PVAV_REHEAT_1_HeatCDemand Inlet Node,  !- Actuator Node Name
>     0.0001,                  !- Controller Convergence Tolerance
{deltaC}
>     AUTOSIZE,                !- Maximum Actuated Flow {m3/s}
>     0.0;                     !- Minimum Actuated Flow {m3/s}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONTROLLER:OUTDOORAIR
===========
> 
> Controller:OutdoorAir,
>     PVAV_REHEAT_1_OA_Controller,  !- Name
>     PVAV_REHEAT_1_OARelief Node,  !- Relief Air Outlet Node Name
>     PVAV_REHEAT_1 Supply Equipment Inlet Node,  !- Return Air Node Name
>     PVAV_REHEAT_1_OA-PVAV_REHEAT_1_CoolCNode,  !- Mixed Air Node Name
>     PVAV_REHEAT_1_OAInlet Node,  !- Actuator Node Name
>     AUTOSIZE,                !- Minimum Outdoor Air Flow Rate {m3/s}
>     AUTOSIZE,                !- Maximum Outdoor Air Flow Rate {m3/s}
>     DifferentialEnthalpy,    !- Economizer Control Type
>     ModulateFlow,            !- Economizer Control Action Type
>     28.0,                    !- Economizer Maximum Limit Dry-Bulb
>     Temperature {C}
>     64000.0,                 !- Economizer Maximum Limit Enthalpy {J/kg}
>     ,                        !- Economizer Maximum Limit Dewpoint
>     Temperature {C}
>     ,                        !- Electronic Enthalpy Limit Curve Name
>     -100.0,                  !- Economizer Minimum Limit Dry-Bulb
>     Temperature {C}
>     NoLockout,               !- Lockout Type
>     FixedMinimum,            !- Minimum Limit Type
>     MinOA_MotorizedDamper_Sched,  !- Minimum Outdoor Air Schedule Name
>     ,                        !- Minimum Fraction of Outdoor Air Schedule
>     Name
>     ,                        !- Maximum Fraction of Outdoor Air Schedule
>     Name
>     ,                        !- Mechanical Ventilation Controller Name
>     No,                      !- Time of Day Economizer Control Schedule
>     Name
>     ,                        !- High Humidity Control
>     ,                        !- Humidistat Control Zone Name
>     ,                        !- High Humidity Outdoor Air Flow Ratio
>     BypassWhenOAFlowGreaterThanMinimum;  !- Control High Indoor Humidity
>     Based on Outdoor Humidity Ratio
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:CONTROLLERLIST
> ===========
> 
> AirLoopHVAC:ControllerList,
>     PVAV_REHEAT_1_Controllers,  !- Name
>     Controller:WaterCoil,    !- Controller 1 Object Type
>     PVAV_REHEAT_1_HeatC_Controller;  !- Controller 1 Name
> 
> AirLoopHVAC:ControllerList,
>     PVAV_REHEAT_1_OA_Controllers,  !- Name
>     Controller:OutdoorAir,   !- Controller 1 Object Type
>     PVAV_REHEAT_1_OA_Controller;  !- Controller 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC ===========
> 
> !***** Air Loop: PVAV_REHEAT_1 *****
> AirLoopHVAC,
>     PVAV_REHEAT_1,           !- Name
>     PVAV_REHEAT_1_Controllers,  !- Controller List Name
>     PVAV_REHEAT_1 Availability Manager List,  !- Availability Manager
List
>     Name
>     AUTOSIZE,                !- Design Supply Air Flow Rate {m3/s}
>     PVAV_REHEAT_1 Air Loop Branches,  !- Branch List Name
>     ,                        !- Connector List Name
>     PVAV_REHEAT_1 Supply Equipment Inlet Node,  !- Supply Side Inlet
Node
>     Name
>     PVAV_REHEAT_1 Zone Equipment Outlet Node,  !- Demand Side Outlet
Node
>     Name
>     PVAV_REHEAT_1 Zone Equipment Inlet Node,  !- Demand Side Inlet Node
>     Names
>     PVAV_REHEAT_1 Supply Equipment Outlet Node;  !- Supply Side Outlet
>     Node Names
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS:
> AIRLOOPHVAC:OUTDOORAIRSYSTEM:EQUIPMENTLIST ===========
> 
> AirLoopHVAC:OutdoorAirSystem:EquipmentList,
>     PVAV_REHEAT_1_OA_Equipment,  !- Name
>     OutdoorAir:Mixer,        !- Component 1 Object Type
>     PVAV_REHEAT_1_OAMixing Box;  !- Component 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:OUTDOORAIRSYSTEM
> ===========
> 
> AirLoopHVAC:OutdoorAirSystem,
>     PVAV_REHEAT_1_OA,        !- Name
>     PVAV_REHEAT_1_OA_Controllers,  !- Controller List Name
>     PVAV_REHEAT_1_OA_Equipment,  !- Outdoor Air Equipment List Name
>     PVAV_REHEAT_1 Availability Manager List;  !- Availability Manager
List
>     Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTDOORAIR:MIXER ===========
> 
> OutdoorAir:Mixer,
>     PVAV_REHEAT_1_OAMixing Box,  !- Name
>     PVAV_REHEAT_1_OA-PVAV_REHEAT_1_CoolCNode,  !- Mixed Air Node Name
>     PVAV_REHEAT_1_OAInlet Node,  !- Outdoor Air Stream Node Name
>     PVAV_REHEAT_1_OARelief Node,  !- Relief Air Stream Node Name
>     PVAV_REHEAT_1 Supply Equipment Inlet Node;  !- Return Air Stream
Node
>     Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:ZONESPLITTER
> ===========
> 
> AirLoopHVAC:ZoneSplitter,
>     PVAV_REHEAT_1 Supply Air Splitter,  !- Name
>     PVAV_REHEAT_1 Zone Equipment Inlet Node,  !- Inlet Node Name
>     ZN_1_FLR_1_SEC_1 VAV Box Inlet Node Name,  !- Outlet 1 Node Name
>     ZN_1_FLR_2_SEC_1 VAV Box Inlet Node Name,  !- Outlet 2 Node Name
>     ZN_1_FLR_3_SEC_1 VAV Box Inlet Node Name,  !- Outlet 3 Node Name
>     ZN_1_FLR_1_SEC_2 VAV Box Inlet Node Name,  !- Outlet 4 Node Name
>     ZN_1_FLR_2_SEC_2 VAV Box Inlet Node Name,  !- Outlet 5 Node Name
>     ZN_1_FLR_3_SEC_2 VAV Box Inlet Node Name,  !- Outlet 6 Node Name
>     ZN_1_FLR_1_SEC_3 VAV Box Inlet Node Name,  !- Outlet 7 Node Name
>     ZN_1_FLR_2_SEC_3 VAV Box Inlet Node Name,  !- Outlet 8 Node Name
>     ZN_1_FLR_3_SEC_3 VAV Box Inlet Node Name,  !- Outlet 9 Node Name
>     ZN_1_FLR_1_SEC_4 VAV Box Inlet Node Name,  !- Outlet 10 Node Name
>     ZN_1_FLR_2_SEC_4 VAV Box Inlet Node Name,  !- Outlet 11 Node Name
>     ZN_1_FLR_3_SEC_4 VAV Box Inlet Node Name,  !- Outlet 12 Node Name
>     ZN_1_FLR_1_SEC_5 VAV Box Inlet Node Name,  !- Outlet 13 Node Name
>     ZN_1_FLR_2_SEC_5 VAV Box Inlet Node Name,  !- Outlet 14 Node Name
>     ZN_1_FLR_3_SEC_5 VAV Box Inlet Node Name;  !- Outlet 15 Node Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:SUPPLYPATH
===========
> 
> AirLoopHVAC:SupplyPath,
>     PVAV_REHEAT_1,           !- Name
>     PVAV_REHEAT_1 Zone Equipment Inlet Node,  !- Supply Air Path Inlet
>     Node Name
>     AirLoopHVAC:ZoneSplitter,!- Component 1 Object Type
>     PVAV_REHEAT_1 Supply Air Splitter;  !- Component 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:ZONEMIXER
===========
> 
> AirLoopHVAC:ZoneMixer,
>     PVAV_REHEAT_1 Return Air Mixer,  !- Name
>     PVAV_REHEAT_1 Zone Equipment Outlet Node,  !- Outlet Node Name
>     ZN_1_FLR_1_SEC_1 Return Air Node Name,  !- Inlet 1 Node Name
>     ZN_1_FLR_2_SEC_1 Return Air Node Name,  !- Inlet 2 Node Name
>     ZN_1_FLR_3_SEC_1 Return Air Node Name,  !- Inlet 3 Node Name
>     ZN_1_FLR_1_SEC_2 Return Air Node Name,  !- Inlet 4 Node Name
>     ZN_1_FLR_2_SEC_2 Return Air Node Name,  !- Inlet 5 Node Name
>     ZN_1_FLR_3_SEC_2 Return Air Node Name,  !- Inlet 6 Node Name
>     ZN_1_FLR_1_SEC_3 Return Air Node Name,  !- Inlet 7 Node Name
>     ZN_1_FLR_2_SEC_3 Return Air Node Name,  !- Inlet 8 Node Name
>     ZN_1_FLR_3_SEC_3 Return Air Node Name,  !- Inlet 9 Node Name
>     ZN_1_FLR_1_SEC_4 Return Air Node Name,  !- Inlet 10 Node Name
>     ZN_1_FLR_2_SEC_4 Return Air Node Name,  !- Inlet 11 Node Name
>     ZN_1_FLR_3_SEC_4 Return Air Node Name,  !- Inlet 12 Node Name
>     ZN_1_FLR_1_SEC_5 Return Air Node Name,  !- Inlet 13 Node Name
>     ZN_1_FLR_2_SEC_5 Return Air Node Name,  !- Inlet 14 Node Name
>     ZN_1_FLR_3_SEC_5 Return Air Node Name;  !- Inlet 15 Node Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: AIRLOOPHVAC:RETURNPATH
===========
> 
> AirLoopHVAC:ReturnPath,
>     PVAV_REHEAT_1 Return Air Path,  !- Name
>     PVAV_REHEAT_1 Zone Equipment Outlet Node,  !- Return Air Path Outlet
>     Node Name
>     AirLoopHVAC:ZoneMixer,   !- Component 1 Object Type
>     PVAV_REHEAT_1 Return Air Mixer;  !- Component 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BRANCH ===========
> 
> Branch,
>     PVAV_REHEAT_1 Air Loop Main Branch,  !- Name
>     AUTOSIZE,                !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     AirLoopHVAC:OutdoorAirSystem,  !- Component 1 Object Type
>     PVAV_REHEAT_1_OA,        !- Component 1 Name
>     PVAV_REHEAT_1 Supply Equipment Inlet Node,  !- Component 1 Inlet
Node
>     Name
>     PVAV_REHEAT_1_OA-PVAV_REHEAT_1_CoolCNode,  !- Component 1 Outlet
Node
>     Name
>     Passive,                 !- Component 1 Branch Control Type
>     AirLoopHVAC:UnitaryCoolOnly,  !- Component 2 Object Type
>     PVAV_REHEAT_1_CoolC,     !- Component 2 Name
>     PVAV_REHEAT_1_OA-PVAV_REHEAT_1_CoolCNode,  !- Component 2 Inlet Node
>     Name
>     PVAV_REHEAT_1_CoolC-PVAV_REHEAT_1_HeatCNode,  !- Component 2 Outlet
>     Node Name
>     Passive,                 !- Component 2 Branch Control Type
>     Coil:Heating:Water,      !- Component 3 Object Type
>     PVAV_REHEAT_1_HeatC,     !- Component 3 Name
>     PVAV_REHEAT_1_CoolC-PVAV_REHEAT_1_HeatCNode,  !- Component 3 Inlet
>     Node Name
>     PVAV_REHEAT_1_HeatC-PVAV_REHEAT_1_FanNode,  !- Component 3 Outlet
Node
>     Name
>     Passive,                 !- Component 3 Branch Control Type
>     Fan:VariableVolume,      !- Component 4 Object Type
>     PVAV_REHEAT_1_Fan,       !- Component 4 Name
>     PVAV_REHEAT_1_HeatC-PVAV_REHEAT_1_FanNode,  !- Component 4 Inlet
Node
>     Name
>     PVAV_REHEAT_1 Supply Equipment Outlet Node,  !- Component 4 Outlet
>     Node Name
>     Active;                  !- Component 4 Branch Control Type
> 
> Branch,
>     HeatSys1 Supply Inlet Branch,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Pump:VariableSpeed,      !- Component 1 Object Type
>     HeatSys1 Pump,           !- Component 1 Name
>     HeatSys1 Supply Inlet Node,  !- Component 1 Inlet Node Name
>     HeatSys1 Pump-HeatSys1 BoilerNodeviaConnector,  !- Component 1
Outlet
>     Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Supply Equipment Branch,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Boiler:HotWater,         !- Component 1 Object Type
>     HeatSys1 Boiler,         !- Component 1 Name
>     HeatSys1 Pump-HeatSys1 BoilerNode,  !- Component 1 Inlet Node Name
>     HeatSys1 Supply Equipment Outlet Node,  !- Component 1 Outlet Node
Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Supply Equipment Bypass Branch,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Pipe:Adiabatic,          !- Component 1 Object Type
>     HeatSys1 Supply Equipment Bypass Pipe,  !- Component 1 Name
>     HeatSys1 Supply Equip Bypass Inlet Node,  !- Component 1 Inlet Node
>     Name
>     HeatSys1 Supply Equip Bypass Outlet Node,  !- Component 1 Outlet
Node
>     Name
>     Bypass;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Supply Outlet Branch,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Pipe:Adiabatic,          !- Component 1 Object Type
>     HeatSys1 Supply Outlet Pipe,  !- Component 1 Name
>     HeatSys1 Supply Mixer-HeatSys1 Supply Outlet Pipe,  !- Component 1
>     Inlet Node Name
>     HeatSys1 Supply Outlet Node,  !- Component 1 Outlet Node Name
>     Passive;                 !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Inlet Branch,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Pipe:Adiabatic,          !- Component 1 Object Type
>     HeatSys1 Demand Inlet Pipe,  !- Component 1 Name
>     HeatSys1 Demand Inlet Node,  !- Component 1 Inlet Node Name
>     HeatSys1 Demand Inlet Pipe-HeatSys1 Demand Mixer,  !- Component 1
>     Outlet Node Name
>     Passive;                 !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 1,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_1_SEC_1 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_1_SEC_1 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_1_SEC_1 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 2,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_2_SEC_1 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_2_SEC_1 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_2_SEC_1 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 3,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_3_SEC_1 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_3_SEC_1 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_3_SEC_1 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 4,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_1_SEC_2 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_1_SEC_2 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_1_SEC_2 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 5,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_2_SEC_2 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_2_SEC_2 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_2_SEC_2 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 6,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_3_SEC_2 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_3_SEC_2 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_3_SEC_2 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 7,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_1_SEC_3 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_1_SEC_3 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_1_SEC_3 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 8,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_2_SEC_3 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_2_SEC_3 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_2_SEC_3 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 9,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_3_SEC_3 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_3_SEC_3 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_3_SEC_3 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 10,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_1_SEC_4 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_1_SEC_4 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_1_SEC_4 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 11,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_2_SEC_4 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_2_SEC_4 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_2_SEC_4 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 12,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_3_SEC_4 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_3_SEC_4 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_3_SEC_4 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 13,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_1_SEC_5 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_1_SEC_5 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_1_SEC_5 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 14,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_2_SEC_5 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_2_SEC_5 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_2_SEC_5 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 15,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     ZN_1_FLR_3_SEC_5 VAV Box Reheat Coil,  !- Component 1 Name
>     ZN_1_FLR_3_SEC_5 VAV Box Reheat CoilDemand Inlet Node,  !- Component
1
>     Inlet Node Name
>     ZN_1_FLR_3_SEC_5 VAV Box Reheat CoilDemand Outlet Node,  !-
Component
>     1 Outlet Node Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Load Branch 16,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Coil:Heating:Water,      !- Component 1 Object Type
>     PVAV_REHEAT_1_HeatC,     !- Component 1 Name
>     PVAV_REHEAT_1_HeatCDemand Inlet Node,  !- Component 1 Inlet Node
Name
>     PVAV_REHEAT_1_HeatCDemand Outlet Node,  !- Component 1 Outlet Node
Name
>     Active;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Bypass Branch,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Pipe:Adiabatic,          !- Component 1 Object Type
>     HeatSys1 Demand Bypass Pipe,  !- Component 1 Name
>     HeatSys1 Demand Bypass Pipe Inlet Node,  !- Component 1 Inlet Node
Name
>     HeatSys1 Demand Bypass Pipe Outlet Node,  !- Component 1 Outlet Node
>     Name
>     Bypass;                  !- Component 1 Branch Control Type
> 
> Branch,
>     HeatSys1 Demand Outlet Branch,  !- Name
>     ,                        !- Maximum Flow Rate {m3/s}
>     ,                        !- Pressure Drop Curve Name
>     Pipe:Adiabatic,          !- Component 1 Object Type
>     HeatSys1 Demand Outlet Pipe,  !- Component 1 Name
>     HeatSys1 Demand Mixer-HeatSys1 Demand Outlet Pipe,  !- Component 1
>     Inlet Node Name
>     HeatSys1 Demand Outlet Node,  !- Component 1 Outlet Node Name
>     Passive;                 !- Component 1 Branch Control Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BRANCHLIST ===========
> 
> BranchList,
>     PVAV_REHEAT_1 Air Loop Branches,  !- Name
>     PVAV_REHEAT_1 Air Loop Main Branch;  !- Branch 1 Name
> 
> BranchList,
>     HeatSys1 Supply Branches,!- Name
>     HeatSys1 Supply Inlet Branch,  !- Branch 1 Name
>     HeatSys1 Supply Equipment Branch,  !- Branch 2 Name
>     HeatSys1 Supply Equipment Bypass Branch,  !- Branch 3 Name
>     HeatSys1 Supply Outlet Branch;  !- Branch 4 Name
> 
> BranchList,
>     HeatSys1 Demand Branches,!- Name
>     HeatSys1 Demand Inlet Branch,  !- Branch 1 Name
>     HeatSys1 Demand Load Branch 1,  !- Branch 2 Name
>     HeatSys1 Demand Load Branch 2,  !- Branch 3 Name
>     HeatSys1 Demand Load Branch 3,  !- Branch 4 Name
>     HeatSys1 Demand Load Branch 4,  !- Branch 5 Name
>     HeatSys1 Demand Load Branch 5,  !- Branch 6 Name
>     HeatSys1 Demand Load Branch 6,  !- Branch 7 Name
>     HeatSys1 Demand Load Branch 7,  !- Branch 8 Name
>     HeatSys1 Demand Load Branch 8,  !- Branch 9 Name
>     HeatSys1 Demand Load Branch 9,  !- Branch 10 Name
>     HeatSys1 Demand Load Branch 10,  !- Branch 11 Name
>     HeatSys1 Demand Load Branch 11,  !- Branch 12 Name
>     HeatSys1 Demand Load Branch 12,  !- Branch 13 Name
>     HeatSys1 Demand Load Branch 13,  !- Branch 14 Name
>     HeatSys1 Demand Load Branch 14,  !- Branch 15 Name
>     HeatSys1 Demand Load Branch 15,  !- Branch 16 Name
>     HeatSys1 Demand Load Branch 16,  !- Branch 17 Name
>     HeatSys1 Demand Bypass Branch,  !- Branch 18 Name
>     HeatSys1 Demand Outlet Branch;  !- Branch 19 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONNECTOR:SPLITTER ===========
> 
> Connector:Splitter,
>     HeatSys1 Supply Splitter,!- Name
>     HeatSys1 Supply Inlet Branch,  !- Inlet Branch Name
>     HeatSys1 Supply Equipment Branch,  !- Outlet Branch 1 Name
>     HeatSys1 Supply Equipment Bypass Branch;  !- Outlet Branch 2 Name
> 
> Connector:Splitter,
>     HeatSys1 Demand Splitter,!- Name
>     HeatSys1 Demand Inlet Branch,  !- Inlet Branch Name
>     HeatSys1 Demand Load Branch 1,  !- Outlet Branch 1 Name
>     HeatSys1 Demand Load Branch 2,  !- Outlet Branch 2 Name
>     HeatSys1 Demand Load Branch 3,  !- Outlet Branch 3 Name
>     HeatSys1 Demand Load Branch 4,  !- Outlet Branch 4 Name
>     HeatSys1 Demand Load Branch 5,  !- Outlet Branch 5 Name
>     HeatSys1 Demand Load Branch 6,  !- Outlet Branch 6 Name
>     HeatSys1 Demand Load Branch 7,  !- Outlet Branch 7 Name
>     HeatSys1 Demand Load Branch 8,  !- Outlet Branch 8 Name
>     HeatSys1 Demand Load Branch 9,  !- Outlet Branch 9 Name
>     HeatSys1 Demand Load Branch 10,  !- Outlet Branch 10 Name
>     HeatSys1 Demand Load Branch 11,  !- Outlet Branch 11 Name
>     HeatSys1 Demand Load Branch 12,  !- Outlet Branch 12 Name
>     HeatSys1 Demand Load Branch 13,  !- Outlet Branch 13 Name
>     HeatSys1 Demand Load Branch 14,  !- Outlet Branch 14 Name
>     HeatSys1 Demand Load Branch 15,  !- Outlet Branch 15 Name
>     HeatSys1 Demand Load Branch 16,  !- Outlet Branch 16 Name
>     HeatSys1 Demand Bypass Branch;  !- Outlet Branch 17 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONNECTOR:MIXER ===========
> 
> Connector:Mixer,
>     HeatSys1 Supply Mixer,   !- Name
>     HeatSys1 Supply Outlet Branch,  !- Outlet Branch Name
>     HeatSys1 Supply Equipment Branch,  !- Inlet Branch 1 Name
>     HeatSys1 Supply Equipment Bypass Branch;  !- Inlet Branch 2 Name
> 
> Connector:Mixer,
>     HeatSys1 Demand Mixer,   !- Name
>     HeatSys1 Demand Outlet Branch,  !- Outlet Branch Name
>     HeatSys1 Demand Load Branch 1,  !- Inlet Branch 1 Name
>     HeatSys1 Demand Load Branch 2,  !- Inlet Branch 2 Name
>     HeatSys1 Demand Load Branch 3,  !- Inlet Branch 3 Name
>     HeatSys1 Demand Load Branch 4,  !- Inlet Branch 4 Name
>     HeatSys1 Demand Load Branch 5,  !- Inlet Branch 5 Name
>     HeatSys1 Demand Load Branch 6,  !- Inlet Branch 6 Name
>     HeatSys1 Demand Load Branch 7,  !- Inlet Branch 7 Name
>     HeatSys1 Demand Load Branch 8,  !- Inlet Branch 8 Name
>     HeatSys1 Demand Load Branch 9,  !- Inlet Branch 9 Name
>     HeatSys1 Demand Load Branch 10,  !- Inlet Branch 10 Name
>     HeatSys1 Demand Load Branch 11,  !- Inlet Branch 11 Name
>     HeatSys1 Demand Load Branch 12,  !- Inlet Branch 12 Name
>     HeatSys1 Demand Load Branch 13,  !- Inlet Branch 13 Name
>     HeatSys1 Demand Load Branch 14,  !- Inlet Branch 14 Name
>     HeatSys1 Demand Load Branch 15,  !- Inlet Branch 15 Name
>     HeatSys1 Demand Load Branch 16,  !- Inlet Branch 16 Name
>     HeatSys1 Demand Bypass Branch;  !- Inlet Branch 17 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CONNECTORLIST ===========
> 
> ConnectorList,
>     HeatSys1 Supply Connectors,  !- Name
>     Connector:Splitter,      !- Connector 1 Object Type
>     HeatSys1 Supply Splitter,!- Connector 1 Name
>     Connector:Mixer,         !- Connector 2 Object Type
>     HeatSys1 Supply Mixer;   !- Connector 2 Name
> 
> ConnectorList,
>     HeatSys1 Demand Connectors,  !- Name
>     Connector:Splitter,      !- Connector 1 Object Type
>     HeatSys1 Demand Splitter,!- Connector 1 Name
>     Connector:Mixer,         !- Connector 2 Object Type
>     HeatSys1 Demand Mixer;   !- Connector 2 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: NODELIST ===========
> 
> NodeList,
>     ZN_1_FLR_1_SEC_1 Inlet Nodes,  !- Name
>     ZN_1_FLR_1_SEC_1 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_2_SEC_1 Inlet Nodes,  !- Name
>     ZN_1_FLR_2_SEC_1 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_3_SEC_1 Inlet Nodes,  !- Name
>     ZN_1_FLR_3_SEC_1 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_1_SEC_2 Inlet Nodes,  !- Name
>     ZN_1_FLR_1_SEC_2 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_2_SEC_2 Inlet Nodes,  !- Name
>     ZN_1_FLR_2_SEC_2 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_3_SEC_2 Inlet Nodes,  !- Name
>     ZN_1_FLR_3_SEC_2 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_1_SEC_3 Inlet Nodes,  !- Name
>     ZN_1_FLR_1_SEC_3 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_2_SEC_3 Inlet Nodes,  !- Name
>     ZN_1_FLR_2_SEC_3 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_3_SEC_3 Inlet Nodes,  !- Name
>     ZN_1_FLR_3_SEC_3 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_1_SEC_4 Inlet Nodes,  !- Name
>     ZN_1_FLR_1_SEC_4 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_2_SEC_4 Inlet Nodes,  !- Name
>     ZN_1_FLR_2_SEC_4 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_3_SEC_4 Inlet Nodes,  !- Name
>     ZN_1_FLR_3_SEC_4 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_1_SEC_5 Inlet Nodes,  !- Name
>     ZN_1_FLR_1_SEC_5 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_2_SEC_5 Inlet Nodes,  !- Name
>     ZN_1_FLR_2_SEC_5 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     ZN_1_FLR_3_SEC_5 Inlet Nodes,  !- Name
>     ZN_1_FLR_3_SEC_5 VAV Box Outlet Node Name;  !- Node 1 Name
> 
> NodeList,
>     PVAV_REHEAT_1_OANode List,  !- Name
>     PVAV_REHEAT_1_OAInlet Node;  !- Node 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTDOORAIR:NODE ===========
> 
> OutdoorAir:Node,
>     PVAV_REHEAT_1_CoolC Cond OA node;  !- Name
> 
> OutdoorAir:Node,
>     PVAV_REHEAT_1_CoolCOA Ref node;  !- Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTDOORAIR:NODELIST ===========
> 
> OutdoorAir:NodeList,
>     PVAV_REHEAT_1_OANode List;  !- Node or NodeList Name 1
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PIPE:ADIABATIC ===========
> 
> Pipe:Adiabatic,
>     HeatSys1 Supply Equipment Bypass Pipe,  !- Name
>     HeatSys1 Supply Equip Bypass Inlet Node,  !- Inlet Node Name
>     HeatSys1 Supply Equip Bypass Outlet Node;  !- Outlet Node Name
> 
> Pipe:Adiabatic,
>     HeatSys1 Supply Outlet Pipe,  !- Name
>     HeatSys1 Supply Mixer-HeatSys1 Supply Outlet Pipe,  !- Inlet Node
Name
>     HeatSys1 Supply Outlet Node;  !- Outlet Node Name
> 
> Pipe:Adiabatic,
>     HeatSys1 Demand Inlet Pipe,  !- Name
>     HeatSys1 Demand Inlet Node,  !- Inlet Node Name
>     HeatSys1 Demand Inlet Pipe-HeatSys1 Demand Mixer;  !- Outlet Node
Name
> 
> Pipe:Adiabatic,
>     HeatSys1 Demand Bypass Pipe,  !- Name
>     HeatSys1 Demand Bypass Pipe Inlet Node,  !- Inlet Node Name
>     HeatSys1 Demand Bypass Pipe Outlet Node;  !- Outlet Node Name
> 
> Pipe:Adiabatic,
>     HeatSys1 Demand Outlet Pipe,  !- Name
>     HeatSys1 Demand Mixer-HeatSys1 Demand Outlet Pipe,  !- Inlet Node
Name
>     HeatSys1 Demand Outlet Node;  !- Outlet Node Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PUMP:VARIABLESPEED ===========
> 
> Pump:VariableSpeed,
>     HeatSys1 Pump,           !- Name
>     HeatSys1 Supply Inlet Node,  !- Inlet Node Name
>     HeatSys1 Pump-HeatSys1 BoilerNodeviaConnector,  !- Outlet Node Name
>     AUTOSIZE,                !- Rated Flow Rate {m3/s}
>     179352,                  !- Rated Pump Head {Pa}
>     AUTOSIZE,                !- Rated Power Consumption {W}
>     0.9,                     !- Motor Efficiency
>     0.0,                     !- Fraction of Motor Inefficiencies to
Fluid
>     Stream
>     0,                       !- Coefficient 1 of the Part Load
Performance
>     Curve
>     1,                       !- Coefficient 2 of the Part Load
Performance
>     Curve
>     0,                       !- Coefficient 3 of the Part Load
Performance
>     Curve
>     0,                       !- Coefficient 4 of the Part Load
Performance
>     Curve
>     0.0,                     !- Minimum Flow Rate {m3/s}
>     Intermittent;            !- Pump Control Type
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: BOILER:HOTWATER ===========
> 
> Boiler:HotWater,
>     HeatSys1 Boiler,         !- Name
>     NATURALGAS,              !- Fuel Type
>     AUTOSIZE,                !- Nominal Capacity {W}
>     0.8,                     !- Nominal Thermal Efficiency
>     ,                        !- Normalized Boiler Efficiency Curve Name
>     82.2000,                 !- Design Water Outlet Temperature {C}
>     AUTOSIZE,                !- Design Water Flow Rate {m3/s}
>     0.0,                     !- Minimum Part Load Ratio
>     1.2,                     !- Maximum Part Load Ratio
>     1.0,                     !- Optimum Part Load Ratio
>     HeatSys1 Pump-HeatSys1 BoilerNode,  !- Boiler Water Inlet Node Name
>     HeatSys1 Supply Equipment Outlet Node,  !- Boiler Water Outlet Node
>     Name
>     95.0,                    !- Water Outlet Upper Temperature Limit {C}
>     VariableFlow,            !- Boiler Flow Mode
>     0.0000,                  !- Parasitic Electric Load {W}
>     1.0000;                  !- Sizing Factor
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PLANTLOOP ===========
> 
> !***** Plant Loop: HeatSys1 *****
> PlantLoop,
>     HeatSys1,                !- Name
>     Water,                   !- Fluid Type
>     HeatSys1 Loop Operation Scheme List,  !- Plant Equipment Operation
>     Scheme Name
>     HeatSys1 Supply Outlet Node,  !- Loop Temperature Setpoint Node Name
>     100.0,                   !- Maximum Loop Temperature {C}
>     10.0,                    !- Minimum Loop Temperature {C}
>     AUTOSIZE,                !- Maximum Loop Flow Rate {m3/s}
>     0.0,                     !- Minimum Loop Flow Rate {m3/s}
>     AUTOSIZE,                !- Plant Loop Volume {m3}
>     HeatSys1 Supply Inlet Node,  !- Plant Side Inlet Node Name
>     HeatSys1 Supply Outlet Node,  !- Plant Side Outlet Node Name
>     HeatSys1 Supply Branches,!- Plant Side Branch List Name
>     HeatSys1 Supply Connectors,  !- Plant Side Connector List Name
>     HeatSys1 Demand Inlet Node,  !- Demand Side Inlet Node Name
>     HeatSys1 Demand Outlet Node,  !- Demand Side Outlet Node Name
>     HeatSys1 Demand Branches,!- Demand Side Branch List Name
>     HeatSys1 Demand Connectors,  !- Demand Side Connector List Name
>     Optimal;                 !- Load Distribution Scheme
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTLIST ===========
> 
> PlantEquipmentList,
>     HeatSys1 Equipment List, !- Name
>     Boiler:HotWater,         !- Equipment 1 Object Type
>     HeatSys1 Boiler;         !- Equipment 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS:
> PLANTEQUIPMENTOPERATION:HEATINGLOAD ===========
> 
> PlantEquipmentOperation:HeatingLoad,
>     HeatSys1 Operation Scheme,  !- Name
>     0.0,                     !- Load Range 1 Lower Limit {W}
>     1000000000000000,        !- Load Range 1 Upper Limit {W}
>     HeatSys1 Equipment List; !- Priority Control 1 Equipment List Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: PLANTEQUIPMENTOPERATIONSCHEMES
> ===========
> 
> PlantEquipmentOperationSchemes,
>     HeatSys1 Loop Operation Scheme List,  !- Name
>     PlantEquipmentOperation:HeatingLoad,  !- Control Scheme 1 Object
Type
>     HeatSys1 Operation Scheme,  !- Control Scheme 1 Name
>     PlantOnSched;            !- Control Scheme 1 Schedule Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: AVAILABILITYMANAGER:NIGHTCYCLE
> ===========
> 
> AvailabilityManager:NightCycle,
>     PVAV_REHEAT_1 Availability Manager,  !- Name
>     ALWAYS_ON,               !- Applicability Schedule Name
>     HVACOperationSchd,       !- Fan Schedule Name
>     CycleOnAny,              !- Control Type
>     1.0,                     !- Thermostat Tolerance {deltaC}
>     1800;                    !- Cycling Run Time {s}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS:
AVAILABILITYMANAGERASSIGNMENTLIST
> ===========
> 
> AvailabilityManagerAssignmentList,
>     PVAV_REHEAT_1 Availability Manager List,  !- Name
>     AvailabilityManager:NightCycle,  !- Availability Manager 1 Object
Type
>     PVAV_REHEAT_1 Availability Manager;  !- Availability Manager 1 Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SETPOINTMANAGER:SCHEDULED
> ===========
> 
> SetpointManager:Scheduled,
>     PVAV_REHEAT_1 SAT setpoint,  !- Name
>     Temperature,             !- Control Variable
>     Seasonal-Reset-Supply-Air-Temp-Sch,  !- Schedule Name
>     PVAV_REHEAT_1 Supply Equipment Outlet Node;  !- Setpoint Node or
>     NodeList Name
> 
> SetpointManager:Scheduled,
>     HeatSys1 Loop Setpoint Manager,  !- Name
>     Temperature,             !- Control Variable
>     HW-Loop-Temp-Schedule,   !- Schedule Name
>     HeatSys1 Supply Outlet Node;  !- Setpoint Node or NodeList Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: SETPOINTMANAGER:MIXEDAIR
> ===========
> 
> SetpointManager:MixedAir,
>     PVAV_REHEAT_1_CoolC SAT Manager,  !- Name
>     Temperature,             !- Control Variable
>     PVAV_REHEAT_1 Supply Equipment Outlet Node,  !- Reference Setpoint
>     Node Name
>     PVAV_REHEAT_1_HeatC-PVAV_REHEAT_1_FanNode,  !- Fan Inlet Node Name
>     PVAV_REHEAT_1 Supply Equipment Outlet Node,  !- Fan Outlet Node Name
>     PVAV_REHEAT_1_CoolC-PVAV_REHEAT_1_HeatCNode;  !- Setpoint Node or
>     NodeList Name
> 
> SetpointManager:MixedAir,
>     PVAV_REHEAT_1_HeatC SAT Manager,  !- Name
>     Temperature,             !- Control Variable
>     PVAV_REHEAT_1 Supply Equipment Outlet Node,  !- Reference Setpoint
>     Node Name
>     PVAV_REHEAT_1_HeatC-PVAV_REHEAT_1_FanNode,  !- Fan Inlet Node Name
>     PVAV_REHEAT_1 Supply Equipment Outlet Node,  !- Fan Outlet Node Name
>     PVAV_REHEAT_1_HeatC-PVAV_REHEAT_1_FanNode;  !- Setpoint Node or
>     NodeList Name
> 
> SetpointManager:MixedAir,
>     PVAV_REHEAT_1_OAMixed Air Temp Manager,  !- Name
>     Temperature,             !- Control Variable
>     PVAV_REHEAT_1 Supply Equipment Outlet Node,  !- Reference Setpoint
>     Node Name
>     PVAV_REHEAT_1_HeatC-PVAV_REHEAT_1_FanNode,  !- Fan Inlet Node Name
>     PVAV_REHEAT_1 Supply Equipment Outlet Node,  !- Fan Outlet Node Name
>     PVAV_REHEAT_1_OA-PVAV_REHEAT_1_CoolCNode;  !- Setpoint Node or
>     NodeList Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CURVE:QUADRATIC ===========
> 
> Curve:Quadratic,
>     PVAV_REHEAT_1_CoolCStandard10Ton_CapFF,  !- Name
>     0.77136,                 !- Coefficient1 Constant
>     0.34053,                 !- Coefficient2 x
>     -0.11088,                !- Coefficient3 x**2
>     0.75918,                 !- Minimum Value of x
>     1.13877;                 !- Maximum Value of x
> 
> Curve:Quadratic,
>     PVAV_REHEAT_1_CoolCStandard10Ton_EIRFFF,  !- Name
>     1.20550,                 !- Coefficient1 Constant
>     -0.32953,                !- Coefficient2 x
>     0.12308,                 !- Coefficient3 x**2
>     0.75918,                 !- Minimum Value of x
>     1.13877;                 !- Maximum Value of x
> 
> Curve:Quadratic,
>     PVAV_REHEAT_1_CoolCStandard10Ton_PLR,  !- Name
>     0.77100,                 !- Coefficient1 Constant
>     0.22900,                 !- Coefficient2 x
>     0.0,                     !- Coefficient3 x**2
>     0.0,                     !- Minimum Value of x
>     1.0;                     !- Maximum Value of x
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: CURVE:BIQUADRATIC ===========
> 
> Curve:Biquadratic,
>     PVAV_REHEAT_1_CoolCStandard10Ton_CapFT,  !- Name
>     0.42415,                 !- Coefficient1 Constant
>     0.04426,                 !- Coefficient2 x
>     -0.00042,                !- Coefficient3 x**2
>     0.00333,                 !- Coefficient4 y
>     -0.00008,                !- Coefficient5 y**2
>     -0.00021,                !- Coefficient6 x*y
>     17.00000,                !- Minimum Value of x
>     22.00000,                !- Maximum Value of x
>     13.00000,                !- Minimum Value of y
>     46.00000;                !- Maximum Value of y
> 
> Curve:Biquadratic,
>     PVAV_REHEAT_1_CoolCStandard10Ton_EIRFT,  !- Name
>     1.23649,                 !- Coefficient1 Constant
>     -0.02431,                !- Coefficient2 x
>     0.00057,                 !- Coefficient3 x**2
>     -0.01434,                !- Coefficient4 y
>     0.00063,                 !- Coefficient5 y**2
>     -0.00038,                !- Coefficient6 x*y
>     17.00000,                !- Minimum Value of x
>     22.00000,                !- Maximum Value of x
>     13.00000,                !- Minimum Value of y
>     46.00000;                !- Maximum Value of y
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: COMPONENTCOST:LINEITEM
===========
> 
> ComponentCost:LineItem,
>     Interior Furnishings,    !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     InteriorFurnishings,     !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1;                       !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Interior Floor,          !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     INT-FLOOR-UNDERSIDE,     !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     15;                      !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Interior Floor Slab,     !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     INT-FLOOR-SLAB,          !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     35;                      !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Drop Ceiling,            !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     DropCeiling,             !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     10;                      !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Sloped Metal Roof,       !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Sloped_Metal_Roof,       !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1;                       !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Gable Wall,              !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Gable_Wall,              !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1;                       !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Air Wall,                !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     AIR-WALL,                !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1;                       !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Swinging Door Conditioned,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Std Swinging Door_con,   !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1;                       !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Swinging Door Semi-conditioned,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Std Swinging Door_semi,  !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1;                       !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Overhead Door,           !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Std Overhead Door,       !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1;                       !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     south:std_window_UValue_3.124_SHGC_0.4_VT_0.508,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508,  !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     219.5200;                !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     east:std_window_UValue_3.124_SHGC_0.4_VT_0.508_east,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_east,  !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     219.5200;                !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     north:std_window_UValue_3.124_SHGC_0.4_VT_0.508_north,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_north,  !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     219.5200;                !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     west:std_window_UValue_3.124_SHGC_0.4_VT_0.508_west,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     std_window_UValue_3.124_SHGC_0.4_VT_0.508_west,  !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     219.5200;                !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     SkylightConst:std_window_UValue_3.919_SHGC_0.49_VT_0.622,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     std_window_UValue_3.919_SHGC_0.49_VT_0.622,  !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     215.9700;                !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     roofs:IEAD_R-20 ci_Roof, !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     IEAD_R-20 ci_Roof,       !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     36.9496;                 !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     int-walls:Standard_Int-Wall,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Standard_Int-Wall,       !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1.0000;                  !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     ext-walls:Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Steel-Framed_R-13 + R-7.5 ci_Ext-wall,  !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     41.5357;                 !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     ext-slab:Unheated - 8in Slab with Carpet_Ext-slab,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Unheated - 8in Slab with Carpet_Ext-slab,  !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     24.8600;                 !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     exposed-floor:Mass_R-8.3 ci_ExposedFloor,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Mass_R-8.3 ci_ExposedFloor,  !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     34.6727;                 !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     door:Swinging_door,      !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Swinging_door,           !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1.0000;                  !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     non-swinging-door:Non-Swinging_NR_door,  !- Name
>     ,                        !- Type
>     Construction,            !- Line Item Type
>     Non-Swinging_NR_door,    !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     1.0000;                  !- Cost per Area {$/m2}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_1_SEC_1,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0343;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_1_SEC_1, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     4.2374;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_1_SEC_1,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_1_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_1_SEC_1:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.8746;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_2_SEC_1,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.1030;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_2_SEC_1, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     12.7123;                 !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_2_SEC_1,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_2_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_2_SEC_1:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     2.6237;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_3_SEC_1,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0343;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_3_SEC_1, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     4.2374;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_3_SEC_1,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_3_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_3_SEC_1:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_1,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.8746;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_1_SEC_2,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0139;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_1_SEC_2, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     1.7104;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_1_SEC_2,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_1_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_1_SEC_2:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.3530;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_2_SEC_2,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0416;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_2_SEC_2, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     5.1312;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_2_SEC_2,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_2_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_2_SEC_2:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     1.0591;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_3_SEC_2,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0139;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_3_SEC_2, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     1.7104;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_3_SEC_2,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_3_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_3_SEC_2:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_2,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.3530;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_1_SEC_3,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0343;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_1_SEC_3, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     4.2374;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_1_SEC_3,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_1_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_1_SEC_3:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.8746;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_2_SEC_3,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.1030;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_2_SEC_3, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     12.7123;                 !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_2_SEC_3,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_2_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_2_SEC_3:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     2.6237;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_3_SEC_3,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0343;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_3_SEC_3, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     4.2374;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_3_SEC_3,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_3_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_3_SEC_3:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_3,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.8746;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_1_SEC_4,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0139;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_1_SEC_4, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     1.7104;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_1_SEC_4,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_1_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_1_SEC_4:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.3530;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_2_SEC_4,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0416;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_2_SEC_4, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     5.1312;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_2_SEC_4,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_2_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_2_SEC_4:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     1.0591;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_3_SEC_4,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0139;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_3_SEC_4, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     1.7104;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_3_SEC_4,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_3_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_3_SEC_4:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_4,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.3530;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_1_SEC_5,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0303;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_1_SEC_5, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     3.7443;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_1_SEC_5,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_1_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_1_SEC_5:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_1_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.7728;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_2_SEC_5,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0910;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_2_SEC_5, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     11.2329;                 !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_2_SEC_5,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_2_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_2_SEC_5:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_2_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     2.3184;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     Infiltration:ZN_1_FLR_3_SEC_5,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.0303;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     People:ZN_1_FLR_3_SEC_5, !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     3.7443;                  !- Quantity {dimensionless}
> 
> ComponentCost:LineItem,
>     LIGHTING EQUIP:ZN_1_FLR_3_SEC_5,  !- Name
>     ,                        !- Type
>     Lights,                  !- Line Item Type
>     ZN_1_FLR_3_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     ,                        !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     1.0000;                  !- Cost per Unit of Output Capacity {$/kW}
> 
> ComponentCost:LineItem,
>     ElectricEquipment:ZN_1_FLR_3_SEC_5:PlugMisc,  !- Name
>     ,                        !- Type
>     General,                 !- Line Item Type
>     ZN_1_FLR_3_SEC_5,        !- Item Name
>     ,                        !- Object End Use Key
>     1.0000,                  !- Cost per Each {$}
>     ,                        !- Cost per Area {$/m2}
>     ,                        !- Cost per Unit of Output Capacity {$/kW}
>     ,                        !- Cost per Unit of Output Capacity per COP
>     {$/kW}
>     ,                        !- Cost per Volume {$/m3}
>     ,                        !- Cost per Volume Rate {$/(m3/s)}
>     ,                        !- Cost per Energy per Temperature
Difference
>     {$/(W/K)}
>     0.7728;                  !- Quantity {dimensionless}
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: UTILITYCOST:TARIFF ===========
> 
> UtilityCost:Tariff,
>     PacifiCorp_48LargeGeneralService,  !- Name
>     ElectricityNet:Facility, !- Output Meter Name
>     kWh,                     !- Conversion Factor Choice
>     ,                        !- Energy Conversion Factor
>     ,                        !- Demand Conversion Factor
>     ,                        !- Time of Use Period Schedule Name
>     ,                        !- Season Schedule Name
>     ,                        !- Month Schedule Name
>     ,                        !- Demand Window Length
>     240.00,                  !- Monthly Charge or Variable Name
>     ,                        !- Minimum Monthly Charge or Variable Name
>     ,                        !- Real Time Pricing Charge Schedule Name
>     ,                        !- Customer Baseline Load Schedule Name
>     Comm Elect;              !- Group Name
> 
> !end  PacifiCorp_48LargeGeneralService,
> UtilityCost:Tariff,
>     PacifiCorp_30GeneralServicePartC,  !- Name
>     ElectricityNet:Facility, !- Output Meter Name
>     kWh,                     !- Conversion Factor Choice
>     ,                        !- Energy Conversion Factor
>     ,                        !- Demand Conversion Factor
>     ,                        !- Time of Use Period Schedule Name
>     ,                        !- Season Schedule Name
>     ,                        !- Month Schedule Name
>     ,                        !- Demand Window Length
>     260.00,                  !- Monthly Charge or Variable Name
>     ,                        !- Minimum Monthly Charge or Variable Name
>     ,                        !- Real Time Pricing Charge Schedule Name
>     ,                        !- Customer Baseline Load Schedule Name
>     Comm Elect;              !- Group Name
> 
> !end PacifiCorp_30GeneralServicePartC,
> UtilityCost:Tariff,
>     PacifiCorp_30GeneralServicePartB,  !- Name
>     ElectricityNet:Facility, !- Output Meter Name
>     kWh,                     !- Conversion Factor Choice
>     ,                        !- Energy Conversion Factor
>     ,                        !- Demand Conversion Factor
>     ,                        !- Time of Use Period Schedule Name
>     ,                        !- Season Schedule Name
>     ,                        !- Month Schedule Name
>     ,                        !- Demand Window Length
>     100.00,                  !- Monthly Charge or Variable Name
>     ,                        !- Minimum Monthly Charge or Variable Name
>     ,                        !- Real Time Pricing Charge Schedule Name
>     ,                        !- Customer Baseline Load Schedule Name
>     Comm Elect;              !- Group Name
> 
> !end PacifiCorp_30GeneralServicePartB,
> UtilityCost:Tariff,
>     PacifiCorp_30GeneralServicePartA,  !- Name
>     ElectricityNet:Facility, !- Output Meter Name
>     kWh,                     !- Conversion Factor Choice
>     ,                        !- Energy Conversion Factor
>     ,                        !- Demand Conversion Factor
>     ,                        !- Time of Use Period Schedule Name
>     ,                        !- Season Schedule Name
>     ,                        !- Month Schedule Name
>     ,                        !- Demand Window Length
>     320.00,                  !- Monthly Charge or Variable Name
>     ,                        !- Minimum Monthly Charge or Variable Name
>     ,                        !- Real Time Pricing Charge Schedule Name
>     ,                        !- Customer Baseline Load Schedule Name
>     Comm Elect;              !- Group Name
> 
> !end PacifiCorp_30GeneralServicePartA,
> UtilityCost:Tariff,
>     PacifiCorp_28LargeGeneralServicePartA,  !- Name
>     ElectricityNet:Facility, !- Output Meter Name
>     kWh,                     !- Conversion Factor Choice
>     ,                        !- Energy Conversion Factor
>     ,                        !- Demand Conversion Factor
>     ,                        !- Time of Use Period Schedule Name
>     ,                        !- Season Schedule Name
>     ,                        !- Month Schedule Name
>     ,                        !- Demand Window Length
>     16.00,                   !- Monthly Charge or Variable Name
>     ,                        !- Minimum Monthly Charge or Variable Name
>     ,                        !- Real Time Pricing Charge Schedule Name
>     ,                        !- Customer Baseline Load Schedule Name
>     Comm Elect;              !- Group Name
> 
> !end  PacifiCorp_28LargeGeneralServicePartA
> UtilityCost:Tariff,
>     PacifiCorp_28LargeGeneralServicePartB,  !- Name
>     ElectricityNet:Facility, !- Output Meter Name
>     kWh,                     !- Conversion Factor Choice
>     ,                        !- Energy Conversion Factor
>     ,                        !- Demand Conversion Factor
>     ,                        !- Time of Use Period Schedule Name
>     ,                        !- Season Schedule Name
>     ,                        !- Month Schedule Name
>     ,                        !- Demand Window Length
>     28.00,                   !- Monthly Charge or Variable Name
>     ,                        !- Minimum Monthly Charge or Variable Name
>     ,                        !- Real Time Pricing Charge Schedule Name
>     ,                        !- Customer Baseline Load Schedule Name
>     Comm Elect;              !- Group Name
> 
> !end  PacifiCorp_28LargeGeneralServicePartB
> UtilityCost:Tariff,
>     PacifiCorp_28LargeGeneralServicePartC,  !- Name
>     ElectricityNet:Facility, !- Output Meter Name
>     kWh,                     !- Conversion Factor Choice
>     ,                        !- Energy Conversion Factor
>     ,                        !- Demand Conversion Factor
>     ,                        !- Time of Use Period Schedule Name
>     ,                        !- Season Schedule Name
>     ,                        !- Month Schedule Name
>     ,                        !- Demand Window Length
>     65.00,                   !- Monthly Charge or Variable Name
>     ,                        !- Minimum Monthly Charge or Variable Name
>     ,                        !- Real Time Pricing Charge Schedule Name
>     ,                        !- Customer Baseline Load Schedule Name
>     Comm Elect;              !- Group Name
> 
> !end  PacifiCorp_28LargeGeneralServicePartC
> UtilityCost:Tariff,
>     PacifiCorp_23GeneralService,  !- Name
>     ElectricityNet:Facility, !- Output Meter Name
>     kWh,                     !- Conversion Factor Choice
>     ,                        !- Energy Conversion Factor
>     ,                        !- Demand Conversion Factor
>     ,                        !- Time of Use Period Schedule Name
>     ,                        !- Season Schedule Name
>     ,                        !- Month Schedule Name
>     ,                        !- Demand Window Length
>     0.0,                     !- Monthly Charge or Variable Name
>     ,                        !- Minimum Monthly Charge or Variable Name
>     ,                        !- Real Time Pricing Charge Schedule Name
>     ,                        !- Customer Baseline Load Schedule Name
>     Comm Elect;              !- Group Name
> 
> !end  PacifiCorp_23GeneralService
> UtilityCost:Tariff,
>     OR_EIAMonthlyRateGas,    !- Name
>     Gas:Facility,            !- Output Meter Name
>     MCF,                     !- Conversion Factor Choice
>     ,                        !- Energy Conversion Factor
>     ,                        !- Demand Conversion Factor
>     ,                        !- Time of Use Period Schedule Name
>     ,                        !- Season Schedule Name
>     ,                        !- Month Schedule Name
>     ,                        !- Demand Window Length
>     0.0,                     !- Monthly Charge or Variable Name
>     ,                        !- Minimum Monthly Charge or Variable Name
>     ,                        !- Real Time Pricing Charge Schedule Name
>     ,                        !- Customer Baseline Load Schedule Name
>     Comm Gas;                !- Group Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: UTILITYCOST:QUALIFY ===========
> 
> UtilityCost:Qualify,
>     MaxDemand4000kW,         !- Name
>     PacifiCorp_48LargeGeneralService,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Maximum,                 !- Qualify Type
>     4000,                    !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     1;                       !- Number of Months
> 
> UtilityCost:Qualify,
>     MinDemand1000kW,         !- Name
>     PacifiCorp_48LargeGeneralService,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Minimum,                 !- Qualify Type
>     1000,                    !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     12;                      !- Number of Months
> 
> UtilityCost:Qualify,
>     MaxDemand1000kW,         !- Name
>     PacifiCorp_30GeneralServicePartC,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Maximum,                 !- Qualify Type
>     1000,                    !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     1;                       !- Number of Months
> 
> UtilityCost:Qualify,
>     MinDemand300kW,          !- Name
>     PacifiCorp_30GeneralServicePartC,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Minimum,                 !- Qualify Type
>     300,                     !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     12;                      !- Number of Months
> 
> UtilityCost:Qualify,
>     MaxDemand300kW,          !- Name
>     PacifiCorp_30GeneralServicePartB,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Maximum,                 !- Qualify Type
>     300,                     !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     1;                       !- Number of Months
> 
> UtilityCost:Qualify,
>     MinDemand200kW,          !- Name
>     PacifiCorp_30GeneralServicePartB,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Minimum,                 !- Qualify Type
>     200,                     !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     12;                      !- Number of Months
> 
> UtilityCost:Qualify,
>     MaxDemand200kW,          !- Name
>     PacifiCorp_30GeneralServicePartA,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Maximum,                 !- Qualify Type
>     200,                     !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     1;                       !- Number of Months
> 
> UtilityCost:Qualify,
>     MinDemand100kW,          !- Name
>     PacifiCorp_30GeneralServicePartA,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Minimum,                 !- Qualify Type
>     100,                     !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     12;                      !- Number of Months
> 
> UtilityCost:Qualify,
>     MaxDemand50kW,           !- Name
>     PacifiCorp_28LargeGeneralServicePartA,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Maximum,                 !- Qualify Type
>     50,                      !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     1;                       !- Number of Months
> 
> UtilityCost:Qualify,
>     MinDemand30kW,           !- Name
>     PacifiCorp_28LargeGeneralServicePartA,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Minimum,                 !- Qualify Type
>     30,                      !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     12;                      !- Number of Months
> 
> UtilityCost:Qualify,
>     MaxDemand100kW,          !- Name
>     PacifiCorp_28LargeGeneralServicePartB,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Maximum,                 !- Qualify Type
>     100,                     !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     1;                       !- Number of Months
> 
> UtilityCost:Qualify,
>     MinDemand50kW,           !- Name
>     PacifiCorp_28LargeGeneralServicePartB,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Minimum,                 !- Qualify Type
>     50,                      !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     12;                      !- Number of Months
> 
> UtilityCost:Qualify,
>     MaxDemand200kW,          !- Name
>     PacifiCorp_28LargeGeneralServicePartC,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Maximum,                 !- Qualify Type
>     200,                     !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     1;                       !- Number of Months
> 
> UtilityCost:Qualify,
>     MinDemand100kW,          !- Name
>     PacifiCorp_28LargeGeneralServicePartC,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Minimum,                 !- Qualify Type
>     100,                     !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     12;                      !- Number of Months
> 
> UtilityCost:Qualify,
>     MaxDemand30kW,           !- Name
>     PacifiCorp_23GeneralService,  !- Tariff Name
>     TotalDemand,             !- Variable Name
>     Maximum,                 !- Qualify Type
>     30,                      !- Threshold Value or Variable Name
>     Annual,                  !- Season
>     Count,                   !- Threshold Test
>     1;                       !- Number of Months
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: UTILITYCOST:CHARGE:SIMPLE
> ===========
> 
> UtilityCost:Charge:Simple,
>     SuppleSched200EnergyCharge,  !- Charge Variable Name
>     PacifiCorp_48LargeGeneralService,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     0.0314;                  !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     LoadSizeDemandCharge,    !- Charge Variable Name
>     PacifiCorp_48LargeGeneralService,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     0.50;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DemandCharge,            !- Charge Variable Name
>     PacifiCorp_48LargeGeneralService,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     1.95;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TransmissionAndAncillaryCharge,  !- Charge Variable Name
>     PacifiCorp_48LargeGeneralService,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     1.59;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TaxofTwoPercent,         !- Charge Variable Name
>     PacifiCorp_48LargeGeneralService,  !- Tariff Name
>     SubTotal,                !- Source Variable
>     Annual,                  !- Season
>     Taxes,                   !- Category Variable Name
>     0.02;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TransmissionAndAncillaryCharge,  !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartC,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     1.67;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DemandCharge,            !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartC,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     2.51;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TaxofTwoPercent,         !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartC,  !- Tariff Name
>     SubTotal,                !- Source Variable
>     Annual,                  !- Season
>     Taxes,                   !- Category Variable Name
>     0.02;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TransmissionAndAncillaryCharge,  !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartB,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     1.67;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DemandCharge,            !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartB,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     2.51;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TaxofTwoPercent,         !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartB,  !- Tariff Name
>     SubTotal,                !- Source Variable
>     Annual,                  !- Season
>     Taxes,                   !- Category Variable Name
>     0.02;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TransmissionAndAncillaryCharge,  !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartA,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     1.67;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DemandCharge,            !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartA,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     2.51;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TaxofTwoPercent,         !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartA,  !- Tariff Name
>     SubTotal,                !- Source Variable
>     Annual,                  !- Season
>     Taxes,                   !- Category Variable Name
>     0.02;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DistributionCharge,      !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartA,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     0.0033;                  !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TransmissionAndAncillaryCharge,  !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartA,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     1.74;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DemandCharge,            !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartA,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     2.68;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TaxofTwoPercent,         !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartA,  !- Tariff Name
>     SubTotal,                !- Source Variable
>     Annual,                  !- Season
>     Taxes,                   !- Category Variable Name
>     0.02;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DistributionCharge,      !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartB,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     0.0033;                  !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TransmissionAndAncillaryCharge,  !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartB,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     1.74;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DemandCharge,            !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartB,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     2.68;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TaxofTwoPercent,         !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartB,  !- Tariff Name
>     SubTotal,                !- Source Variable
>     Annual,                  !- Season
>     Taxes,                   !- Category Variable Name
>     0.02;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DistributionCharge,      !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartC,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     0.0033;                  !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TransmissionAndAncillaryCharge,  !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartC,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     1.74;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DemandCharge,            !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartC,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     2.68;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TaxofTwoPercent,         !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartC,  !- Tariff Name
>     SubTotal,                !- Source Variable
>     Annual,                  !- Season
>     Taxes,                   !- Category Variable Name
>     0.02;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TransmissionAndAncilaryCharge,  !- Charge Variable Name
>     PacifiCorp_23GeneralService,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     0.0051;                  !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     DistributionCharge,      !- Charge Variable Name
>     PacifiCorp_23GeneralService,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     0.0142;                  !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TaxofTwoPercent,         !- Charge Variable Name
>     PacifiCorp_23GeneralService,  !- Tariff Name
>     SubTotal,                !- Source Variable
>     Annual,                  !- Season
>     Taxes,                   !- Category Variable Name
>     0.02;                    !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     MonthlyRateGasCharge,    !- Charge Variable Name
>     OR_EIAMonthlyRateGas,    !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     OR_MonthlyGasRates;      !- Cost per Unit Value or Variable Name
> 
> UtilityCost:Charge:Simple,
>     TaxofTwoPercent,         !- Charge Variable Name
>     OR_EIAMonthlyRateGas,    !- Tariff Name
>     SubTotal,                !- Source Variable
>     Annual,                  !- Season
>     Taxes,                   !- Category Variable Name
>     0.02;                    !- Cost per Unit Value or Variable Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: UTILITYCOST:CHARGE:BLOCK
> ===========
> 
> UtilityCost:Charge:Block,
>     SupplyServiceSchedule200,!- Charge Variable Name
>     PacifiCorp_30GeneralServicePartC,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     20000,                   !- Block Size 1 Value or Variable Name
>     0.0335,                  !- Block 1 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 2 Value or Variable Name
>     0.0334;                  !- Block 2 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     LoadSizeCharge,          !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartC,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     200,                     !- Block Size 1 Value or Variable Name
>     0.0,                     !- Block 1 Cost per Unit Value or Variable
>     Name
>     100,                     !- Block Size 2 Value or Variable Name
>     1.1,                     !- Block 2 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 3 Value or Variable Name
>     0.55;                    !- Block 3 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     SupplyServiceSchedule200,!- Charge Variable Name
>     PacifiCorp_30GeneralServicePartB,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     20000,                   !- Block Size 1 Value or Variable Name
>     0.0335,                  !- Block 1 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 2 Value or Variable Name
>     0.0334;                  !- Block 2 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     LoadSizeCharge,          !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartB,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     200,                     !- Block Size 1 Value or Variable Name
>     0.0,                     !- Block 1 Cost per Unit Value or Variable
>     Name
>     100,                     !- Block Size 2 Value or Variable Name
>     1.1,                     !- Block 2 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 3 Value or Variable Name
>     0.55;                    !- Block 3 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     SupplyServiceSchedule200,!- Charge Variable Name
>     PacifiCorp_30GeneralServicePartA,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     20000,                   !- Block Size 1 Value or Variable Name
>     0.0335,                  !- Block 1 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 2 Value or Variable Name
>     0.0334;                  !- Block 2 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     LoadSizeCharge,          !- Charge Variable Name
>     PacifiCorp_30GeneralServicePartA,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     200,                     !- Block Size 1 Value or Variable Name
>     0.0,                     !- Block 1 Cost per Unit Value or Variable
>     Name
>     100,                     !- Block Size 2 Value or Variable Name
>     1.1,                     !- Block 2 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 3 Value or Variable Name
>     0.55;                    !- Block 3 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     SupplyServiceSchedule200,!- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartA,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     20000,                   !- Block Size 1 Value or Variable Name
>     0.0341,                  !- Block 1 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 2 Value or Variable Name
>     0.0339;                  !- Block 2 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     LoadSizeCharge,          !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartA,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     50,                      !- Block Size 1 Value or Variable Name
>     0.94,                    !- Block 1 Cost per Unit Value or Variable
>     Name
>     100,                     !- Block Size 2 Value or Variable Name
>     0.77,                    !- Block 2 Cost per Unit Value or Variable
>     Name
>     300,                     !- Block Size 3 Value or Variable Name
>     0.41,                    !- Block 3 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 4 Value or Variable Name
>     0.31;                    !- Block 4 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     SupplyServiceSchedule200,!- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartB,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     20000,                   !- Block Size 1 Value or Variable Name
>     0.0341,                  !- Block 1 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 2 Value or Variable Name
>     0.0339;                  !- Block 2 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     LoadSizeCharge,          !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartB,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     50,                      !- Block Size 1 Value or Variable Name
>     0.94,                    !- Block 1 Cost per Unit Value or Variable
>     Name
>     100,                     !- Block Size 2 Value or Variable Name
>     0.77,                    !- Block 2 Cost per Unit Value or Variable
>     Name
>     300,                     !- Block Size 3 Value or Variable Name
>     0.41,                    !- Block 3 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 4 Value or Variable Name
>     0.31;                    !- Block 4 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     SupplyServiceSchedule200,!- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartC,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     20000,                   !- Block Size 1 Value or Variable Name
>     0.0341,                  !- Block 1 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 2 Value or Variable Name
>     0.0339;                  !- Block 2 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     LoadSizeCharge,          !- Charge Variable Name
>     PacifiCorp_28LargeGeneralServicePartC,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     50,                      !- Block Size 1 Value or Variable Name
>     0.94,                    !- Block 1 Cost per Unit Value or Variable
>     Name
>     100,                     !- Block Size 2 Value or Variable Name
>     0.77,                    !- Block 2 Cost per Unit Value or Variable
>     Name
>     300,                     !- Block Size 3 Value or Variable Name
>     0.41,                    !- Block 3 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 4 Value or Variable Name
>     0.31;                    !- Block 4 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     SupplyServiceSchedule200,!- Charge Variable Name
>     PacifiCorp_23GeneralService,  !- Tariff Name
>     totalEnergy,             !- Source Variable
>     Annual,                  !- Season
>     EnergyCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     3000,                    !- Block Size 1 Value or Variable Name
>     0.0407,                  !- Block 1 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 2 Value or Variable Name
>     0.0294;                  !- Block 2 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     DemandCharge,            !- Charge Variable Name
>     PacifiCorp_23GeneralService,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     15,                      !- Block Size 1 Value or Variable Name
>     0.0,                     !- Block 1 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 2 Value or Variable Name
>     2.38;                    !- Block 2 Cost per Unit Value or Variable
>     Name
> 
> UtilityCost:Charge:Block,
>     LoadSizeCharge,          !- Charge Variable Name
>     PacifiCorp_23GeneralService,  !- Tariff Name
>     totalDemand,             !- Source Variable
>     Annual,                  !- Season
>     DemandCharges,           !- Category Variable Name
>     ,                        !- Remaining Into Variable
>     ,                        !- Block Size Multiplier Value or Variable
>     Name
>     15,                      !- Block Size 1 Value or Variable Name
>     0.0,                     !- Block 1 Cost per Unit Value or Variable
>     Name
>     remaining,               !- Block Size 2 Value or Variable Name
>     0.7;                     !- Block 2 Cost per Unit Value or Variable
>     Name
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: UTILITYCOST:VARIABLE ===========
> 
> UtilityCost:Variable,
>     OR_MonthlyGasRates,      !- Name
>     OR_EIAMonthlyRateGas,    !- Tariff Name
>     8.32,                    !- Variable Type
>     8.52,                    !- January Value
>     8.69,                    !- February Value
>     9.12,                    !- March Value
>     8.08,                    !- April Value
>     8.55,                    !- May Value
>     8.67,                    !- June Value
>     8.83,                    !- July Value
>     8.98,                    !- August Value
>     9.71,                    !- September Value
>     8.47,                    !- October Value
>     8.45;                    !- November Value
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTPUT:VARIABLEDICTIONARY
> ===========
> 
> Output:VariableDictionary,
>     IDF,                     !- Key Field
>     Unsorted;                !- Sort Option
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTPUTCONTROL:TABLE:STYLE
> ===========
> 
> OutputControl:Table:Style,
>     HTML;                    !- Column Separator
> 
> 
> !-   ===========  ALL OBJECTS IN CLASS: OUTPUT:VARIABLE ===========
> 
> Output:Variable,
>     *,                       !- Key Value
>     Surface Ext Convection Coeff,  !- Variable Name
>     Hourly;                  !- Reporting Frequency
> 
> Output:Variable,
>     *,                       !- Key Value
>     Outdoor Dry Bulb,        !- Variable Name
>     Hourly;                  !- Reporting Frequency
> 
> Output:Variable,
>     *,                       !- Key Value
>     Wind Speed,              !- Variable Name
>     Hourly;                  !- Reporting Frequency
> 
> Output:Variable,
>     *,                       !- Key Value
>     Direct Solar,            !- Variable Name
>     Hourly;                  !- Reporting Frequency
> 
> Output:Variable,
>     *,                       !- Key Value
>     Surface Outside Temperature,  !- Variable Name
>     Hourly;                  !- Reporting Frequency
> 
> 
> 
> 
> 
> 
> 
> 
> 
> ------------------------------------
> 
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to
> energyplus-support@xxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
> 
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are currently allowed but be mindful that not everyone has a
> high speed connection.  Limit attachments to small files.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under
the
> Documentation link and press the "search" button.
> Yahoo! Groups Links
> 
> 
> 


------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/