Thanks Mr. Dirkes,

I didn't express myself properly. Min ODA rates are not auto-sized. These I have properly calculated with a very large table containing room types as per 62.1. The heating and cooling ventilation rates are autosized. 

I run a cooling design day calc with Sizing:Parameters set at 1.15 and a heating design day calc with Sizing:Parameters set at 1.25.