It seems that the 0.175 value should be met.  Is the fan on? (If not, there will be no flow)

 

You might try setting the outdoor air fields in Sizing:Zone

 

The Building Performance Team
James V. Dirkes II, P.E., LEED AP
1631 Acacia Drive NW
Grand Rapids, MI 49504
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of jeannieboef
Sent: Tuesday, September 07, 2010 3:43 AM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Min ODA rate is not being met?

 

 

Min ODA rate is not being met. Resulting airflow is 0.03 m3/s which is smaller than the 0.175 Min ODA rate input in the sizing object.

Any idea why?

!JMM VENTILATION 118204
Sizing:System,
118204 AHU, !- AirLoop Name
Sensible, !- Type of Load to Size On
0.175000, !- Design (minimum) outside air volumetric flow rate {m3/s} !630 m3/hr
1, !- Minimum System Air Flow Ratio
7, !- Preheat design set temperature {C}
0.008, !- Preheat design humidity ratio {kg-H2O/kg-air}
11, !- Precool design temperature {C}
0.008, !- Precool design humidity ratio {kg-H2O/kg-air}
13, !- Central cooling design supply air temperature {C} ! For cooling room setpoint 24°C as per G3.1.2.8 deltaT = 11°C
32, !- Central heating design supply air temperature {C} ! For heating room setpoint 21°C as per G3.1.2.8 deltaT = 11°C
NonCoincident, !- Sizing Option
No, !- 100% Outdoor Air in Cooling
No, !- 100% Outdoor Air in Heating
0.008, !- Central cooling design supply air humidity ratio {kg-H2O/kg-air}
0.008, !- Central heating design supply air humidity ratio {kg-H2O/kg-air}
DesignDay, !- Cooling Design Air Flow Method
0, !- cooling design air flow rate {m3/s}
DesignDay, !- Heating Design Air Flow Method
0; !- heating design air flow rate {m3/s}



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___