You are correct, the outdoor air mixer is integral to the PTAC and a HX cannot be included at this time. Yes, in addition to the PTAC, you can include a ZoneHVAC:EnergyRecoveryVentilator to provide outdoor air using energy recovery to the same zone, however, this is not exactly what you intend to model since the inlet conditions to the PTAC coils will not be affected by the heat exchanger. You can model this using an air loop (AirloopHVAC) with the HX in the outside air system. One air loop per zone will be the same as one PTAC per zone, but with the air loop you can include the HX. On 9/15/2010 3:27 AM, Xavier Garcia Casals wrote:
-- Richard A. Raustad Senior Research Engineer Florida Solar Energy Center University of Central Florida 1679 Clearlake Road Cocoa, FL 32922-5703 Phone: (321) 638-1454 Fax: (321) 638-1439 or 1010 Visit our web site at: http://www.fsec.ucf.edu UCF - From Promise to Prominence: Celebrating 40 Years __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.