|
Here are a couple of things to consider: ·
You must have an exhaust fan in the zone. Its airflow rate
must match the amount of outdoor air introduced to the zone by each air loop.
Normally that zone outdoor airflow rate is controlled in the Controller:OutdoorAir
object, but it is also influenced by the outdoor air fields in Sizing:Zone. If
you have an ERV or other zone object which introduces outdoor air, that also
affects the balance. ·
If your zone fan is not operating at the exact same times as the
exhaust fan(s), the “unbalanced exhaust” message will occur when
the zone fan is off (and exhaust is on) ·
Finally if your zone fan is the OnOff style, the warning will
occur during times that the zone fan cycles off and the exhaust fan remains on. p.s., Most of this information is from having the same problem
and getting excellent assistance from Mike Witte The Building Performance Team From: EnergyPlus_Support@xxxxxxxxxxxxxxx
[mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of grandocu Hello, __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |