[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Airloop Error
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: Airloop Error
- From: "grandocu" <jgrando@xxxxxxxxxxxxx>
- Date: Tue, 28 Sep 2010 12:28:37 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 28 Sep 2010 06:55:47 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=lima; t=1285678546; bh=E9xzgBsTuVNDQ8N/0fDB7avPZu0RknG1xbgOcIc3Etw=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=vE02T1fhHFnfyp+Mkxqn/2vn/GuCfKwNL/EDw357Dke12Meck32rMv8d75C3uD+3vUH+fbW+0PgobpoqtsdsrpvRBiXBpiUlRUu101NnSNo4v4IsF/X7J5y5pzULmm0K
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=lima; d=yahoogroups.com; b=EAk9uqnUfJmmoBoeRfF9qrqRYkrLyQqQRLVUD+t0dLMchZ3lPcm5OBzc+XRGvRrLj+MFjUC+QhybNDR5R9K/EYzwoxBSh8XhMGgJdnI2lniZ6omwdGx8ZtQYWzvuvfVJ;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <00ee01cb5e44$1e1a2c90$5a4e85b0$@com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
I solved the issue. The designer set the air handling unit's minimum outside air to a level much higher than what the zones were requesting. Somehow between the zone:sizing and the specified minimum OA there was an error.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "James V Dirkes II, PE" <jim@...> wrote:
>
> Dear Phylroy,
>
>
>
> The same operating schedule solves the issue if both fans operate
> continuously. An OnOff fan does not, so if the Exhaust fan is running
> during an Off cycle of the zone fan, you get a warning.
>
>
>
> The Building Performance Team
> James V. Dirkes II, P.E., LEED AP
> 1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
>
>
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Phylroy Lopez
> Sent: Monday, September 27, 2010 12:15 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: Re: [EnergyPlus_Support] Airloop Error
>
>
>
>
>
> Wouldn't having the same operating schedule for the supply and exhaust fans
> solve this problem?
>
> Sent from my iPhone
>
>
> On 2010-09-24, at 2:23 PM, Vinay Devanathan <vinay.devanathan@...>
> wrote:
>
>
>
> Mr. Dirkes,
>
> I have been having this problem too and I would like to know if there is any
> way to correct this warning (occurring because of points 2 & 3 as mentioned
> by you).
>
> Thank you.
>
> Regards,
> Vinay
>
> On Fri, Sep 24, 2010 at 1:54 PM, James V Dirkes II, PE
> <jim@...> wrote:
>
>
>
> Here are a couple of things to consider:
>
> . You must have an exhaust fan in the zone. Its airflow rate must
> match the amount of outdoor air introduced to the zone by each air loop.
> Normally that zone outdoor airflow rate is controlled in the
> Controller:OutdoorAir object, but it is also influenced by the outdoor air
> fields in Sizing:Zone. If you have an ERV or other zone object which
> introduces outdoor air, that also affects the balance.
>
> . If your zone fan is not operating at the exact same times as the
> exhaust fan(s), the "unbalanced exhaust" message will occur when the zone
> fan is off (and exhaust is on)
>
> . Finally if your zone fan is the OnOff style, the warning will
> occur during times that the zone fan cycles off and the exhaust fan remains
> on.
>
>
>
>
>
> p.s., Most of this information is from having the same problem and getting
> excellent assistance from Mike Witte
>
>
>
> The Building Performance Team
> James V. Dirkes II, P.E., LEED AP
> 1631 Acacia Drive NW
> Grand Rapids, MI 49504
> 616 450 8653
>
>
>
> From: EnergyPlus_Support@xxxxxxxxxxxxxxx
> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of grandocu
> Sent: Friday, September 24, 2010 10:52 AM
> To: EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: [EnergyPlus_Support] Airloop Error
>
>
>
>
>
> Hello,
>
> I'm getting the following error:
>
> ** Warning ** In AirLoopHVAC AHU-B-5 there is unbalanced exhaust air flow.
> ** ~~~ ** During Warmup, Environment=SUMMERSIZINGDAY, at Simulation
> time=07/20 19:40 - 19:50
> ** ~~~ ** Unless there is balancing infiltration / ventilation air flow,
> this will result in
> ** ~~~ ** load due to induced outdoor air being neglected in the simulation.
>
> I don't see a problem with my connections but I did supply airflow rate
> myself. I am also getting a "maximum iterations" error for this airloop. Has
> anyone ever had this problem before? Thank you.
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/