Yes I am and yes they are set to always available. It
only happens on the hour when I go from cycling on any
zone at 18 C to running the airloop system at a setpoint
at 12.8 C. Coincidentally, there is no OA allowed during
night as well so when it starts, the system has a load to
deal with and now OA ventilation. Will this lead to a
problem? Should I try to modify the OA and warmup schedule
to get rid of it or might it be another reason.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx,
Richard Raustad <RRaustad@...> wrote:
>
> The air loop can fail convergence for reasons other
than tolerance.
> Are you getting many of these errors?
> Are you using chilled water coils? If so try setting
the availability
> schedules for the water coil to always on and see if
the message disappears.
>
> On 9/30/2010 8:50 AM, grandocu wrote:
> >
> > Hello everyone,
> >
> > I have a warning that keeps popping up saying
"Maximum iterations (20)
> > exceeded" and the message below says the airloop
failed, but all
> > tolerance values below are 0. Does anyone know
why this message is
> > showing up if all the tolerance values are 0?
> >
> > ** Warning ** SimHVAC: Maximum iterations (20)
exceeded for all HVAC
> > loops, at ANNSIM, 01/02 05:10 - 05:11
> > ** ~~~ ** SimFlags=[TFFFFFFF]
> >
AirLoops[T],ZoneEq[F],NonZoneEq[F],PlantLoops[F],CondLoops[F],ElecCircuits[F],PlantDemandLoops[F],CondDemandLoops[F]..F=ok,T=fail
> > ** ~~~ ** HVAC Tolerance Flags=[0000000]
> >
Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0]..0=ok,1=fail
> > ** ~~~ ** HVAC Tolerance Values, Most Recent
listed first
> > ** ~~~ ** HVAC EnthalpyTol=0.000,
MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[724 - AHU-B-6
RETURN AIR OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000,
MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[723 - AHU-B-3
RETURN AIR OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000,
MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[720 - AHU-B-5
RETURN AIR OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000,
MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[719 - AHU-B-4
RETURN AIR OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000,
MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[722 - CB
AHU-B-2 RETURN AIR OUTLET]
> > ** ~~~ ** Plant Tolerance Flags=[00000000]
> >
Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0],PlantFlowMassFlow[0]..0=ok,1=fail
> > ** ~~~ ** Plant Tolerance Values, Most Recent
listed first
> > ** ~~~ ** Plant EnthalpyTol=0.000,
MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[390 - CB
CONDENSER DEMAND OUTLET NODE]
> > ** ~~~ ** Plant EnthalpyTol=0.000,
MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[347 - CHW_LOOP
CNDW DEMAND OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000,
MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[383 - CB
CONDENSER DEMAND INLET NODE]
> > ** ~~~ ** Plant EnthalpyTol=0.000,
MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[342 - CHW_LOOP
CNDW DEMAND INLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000,
MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000,
TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[314 - HW_LOOP
HW DEMAND OUTLET]
> > ** ~~~ ** Plant Flow Tolerance Values, Most
Recent listed first
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer