Yes I am and yes they are set to always available. It only happens on the hour when I go from cycling on any zone at 18 C to running the airloop system at a setpoint at 12.8 C. Coincidentally, there is no OA allowed during night as well so when it starts, the system has a load to deal with and now OA ventilation. Will this lead to a problem? Should I try to modify the OA and warmup schedule to get rid of it or might it be another reason.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>
> The air loop can fail convergence for reasons other than tolerance.
> Are you getting many of these errors?
> Are you using chilled water coils? If so try setting the availability
> schedules for the water coil to always on and see if the message disappears.
>
> On 9/30/2010 8:50 AM, grandocu wrote:
> >
> > Hello everyone,
> >
> > I have a warning that keeps popping up saying "Maximum iterations (20)
> > exceeded" and the message below says the airloop failed, but all
> > tolerance values below are 0. Does anyone know why this message is
> > showing up if all the tolerance values are 0?
> >
> > ** Warning ** SimHVAC: Maximum iterations (20) exceeded for all HVAC
> > loops, at ANNSIM, 01/02 05:10 - 05:11
> > ** ~~~ ** SimFlags=[TFFFFFFF]
> > AirLoops[T],ZoneEq[F],NonZoneEq[F],PlantLoops[F],CondLoops[F],ElecCircuits[F],PlantDemandLoops[F],CondDemandLoops[F]..F=ok,T=fail
> > ** ~~~ ** HVAC Tolerance Flags=[0000000]
> > Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0]..0=ok,1=fail
> > ** ~~~ ** HVAC Tolerance Values, Most Recent listed first
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[724 - AHU-B-6 RETURN AIR OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[723 - AHU-B-3 RETURN AIR OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[720 - AHU-B-5 RETURN AIR OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[719 - AHU-B-4 RETURN AIR OUTLET]
> > ** ~~~ ** HVAC EnthalpyTol=0.000, MassFlowTol=0.000, HumRatTol=0.0000,
> > PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** HVAC side outlet node=[722 - CB AHU-B-2 RETURN AIR OUTLET]
> > ** ~~~ ** Plant Tolerance Flags=[00000000]
> > Enthalpy[0],MassFlow[0],HumRat[0],Pressure[0],FlowQual[0],Energy[0],Temp[0],PlantFlowMassFlow[0]..0=ok,1=fail
> > ** ~~~ ** Plant Tolerance Values, Most Recent listed first
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[390 - CB CONDENSER DEMAND OUTLET NODE]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[347 - CHW_LOOP CNDW DEMAND OUTLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[383 - CB CONDENSER DEMAND INLET NODE]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[342 - CHW_LOOP CNDW DEMAND INLET]
> > ** ~~~ ** Plant EnthalpyTol=0.000, MassFlowTol=0.000,
> > HumRatTol=0.0000, PressureTol=0
> > ** ~~~ ** FlowQualTol=0.00, EnergyTol=0.000, TempTol=0.00
> > ** ~~~ ** Plant side outlet node=[314 - HW_LOOP HW DEMAND OUTLET]
> > ** ~~~ ** Plant Flow Tolerance Values, Most Recent listed first
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> > ** ~~~ ** PlantFlowFlowTol=0.000
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/